Hey guys

I am hoping to get some answers on Combustion air.

Ok first off I have two mechanical rooms in this building, both have ducts for combustion air.

first one

one 200,000 BTU natural draft

one 112,000 BTU forced draft

one 40,000 BTU Water heater natural draft

room size approx 225 sq ft with a 9'celing

duct from outside measures 8"x16"

2nd one

3 furnaces all the same 100,000 BTU forced draft ea

room size approx 350 sq ft 9' ceiling

duct from out side 8"x39"

I am in michigan and the cold air just poor in the vent

ducts.

I was thinking of a damper that would open and close with furnace operation (stat controlled)or is there better way to do it?

What would be really nice would be a damper that would open part way or full depending on the # of furnaces running, but I would image that would be much harder to make happen.

Any comments welcome and or questions

Thank you

Comments (8)

  • 15 years ago

    I don't know Michigan regulations, but in PA, Labor and Industry allows a louvered vent for combustion air inlet. Nothing fancy. If a negative pressure develops in the room, the vent swings open on its own.

  • 15 years ago

    I wondered about this, what would you call that style of damper or vent?

    Thank you

  • 15 years ago

    Look under Grainger.com under vents. Either wall or supply vents. My computer won't load the pages.

  • 15 years ago

    Ok I see the type you are talking about, I guess my only concern is the wind being able to blow it open.

    Thanks for your input

  • 15 years ago

    Anyone else want to chime in?

  • 15 years ago

    Our vent was on the north side of the building and I never noticed that wind was an issue.

  • 15 years ago

    There are motorized dampers that can be interlocked with the combustion appliances. They only allow operation of the combustion device if the door is in the open position.

    I have only looked at the ones scaled for residential applications, but I can't imagine that they would not be available larger. YOu can install more than one to scale the amount of air need, but it might be a lot more expensive. Google will find them.

  • 15 years ago

    I used to maintain a pair of furnaces that used a mechanized damper. The original furnaces had been installed in the mechanical room with no outside air and there were constant problems with soot. After the damper was installed problems went away. There is an interlock so the damper opens before either burner can fire. I don't know where the damper came from, too long ago but it's been very reliable and because the room is fairly airtight due to fire code, there's no problem with cold air in the adjoining room.