radiant floor

18 years ago

We just installed a radiant floor in a concrete slab (no floor covering) in a one story extension. The room is very comfortable but there are definite hot and cold patches in the floor, should the floor feel even? Our plumber has been problematic and uncommunicative so I want as much information as possible before confronting him

Comments (8)

  • 18 years ago

    Depending on the insulation and span between pipes. Normally pipes are 6-16 inches apart and seem to be satisfactory.

  • 18 years ago

    The closer the tubing is spaced, the more even the floor, but eventually the heat should bridge the gaps if the circulation is for longer periods of time.

  • 18 years ago

    There really isn't a lot you can do about it now. You really need to look at how it was installed as stated by others here.
    What was the spacing, how hot is the water, how thick is the concrete over the pex tubing?
    I have a 900 sq ft slab that's also radiant but I'm 6" spacing and not sure if I have cold spots, but one would think that the heat would transfer evenly through the mass of concrete. It may be less noticable when you put down your finish floor.
    Frankly I can understand why the plumber doesn't want to get involved. There really is not much you can do to tweek the system except to check the water output temp and to make sure the loops are all supplying the same water flow.
    There may also be heat up time differences on the slab where some of the tubing is at a different depth in the concrete. Those are things you'll never be able to check.

  • 18 years ago

    We installed ours last year and the hotter it gets the colder it feels in those spots. Mine is spaced correctly it's cold where you are on the return side of each loop. The numbers say 4 loops @ 350' is enough for our floor but if I was to do it all over again I would go with 5 loops at 300'. Nothing can be done to fix it, the best you can do is have your pump on high and try to extend the hot water as far as you can through the loops.

  • 18 years ago

    pirondelle,

    Can you elaborate on your problem more. Is it so hot, thats it's not tolerable to stand on? So cold that it is not tolerable? What type of flooring do you plan on installing?

    Placement of the tubing is critical, horizontally and vertically. If the tubing is too close to the top of the concrete, you will get hot spots, if it's too low you can can cold spots. Similar with horizontal spacing. A problem with spacing can only be resolved by tearing out (Jack hammer) the concrete slab & piping and redoing the entire job.

    Heres a horror story. The State of Minnesota hired a contractor to install an electric snow melting system for the sidewalk leading to the Capitol. (This system is similar to infloor heating systems) After the installation, the first winter, the State had patches of ice and patches where the system worked well. They hired a company to make a video image of the sidewalk and used infrared technology to view the sidewalk in a thermal image. You can actually see the cable in the slab, where it is working and where it is not. They gave me the video and I made an isometric drawing of the cable placement in the slab. The contractor had failed to install the heating cable properly. The cable was not tied to the reinforcing mesh as required by the manufacturer, so the cable rose higher in the slab at some places. The mesh was not supported when the slab was poured, so the cable was lower in some spots causing icing on the sidewalk. The day of the trial, the drawing was presented to the contractor prior to the start. The contractor did not argue his point and agreed to tearout and replace the sidewalk & heating cable at his own expense $30,000.00.

    Hope that helps,

    Dan Martyn

  • 18 years ago

    One other option if it wasnt done is to use an injection pump system or a 3 or 4-way valve, either in conjuction with an outdoor controller to modulate the water temp directed to the floor based on outdoor temp. The theory is to closer match the floor temp with the heat loss, or room heat requirement. This also allows the circulation to stay on longer thus, less noticible hot spots.

  • 18 years ago

    thanks for all the responses
    this is a studio, so there is no floor covering, just a cement floor.
    as i mentioned the room itself is comfortable but there are definite warm and cold spots, nothing is burning hot or super cold.
    having never been exposed to a radiant floor i wanted a better understanding of what is "normal" and if the hot/cold spots might have to do with trapped air
    since the main objective (even air temperature) is being met, i am not about to rip up the floor
    but if i can improve the circulation in some way, i would like to know
    also, if there has been a flawed installation, it would be helpful to know that since not all the radiators in the rest of the house have been installed and it will give me some leverage with the final bill.
    (we have had the hot water pump fail 3 times on a brand new installation so there are other "issues" and concerns vis a vis workmanship)

  • 18 years ago

    Circulator should go 10-15 years +.

    3 "pumps"? you have a design/install problem