Do these settings look OK for GT?

17 years ago

OK, didn't pull the cover off to check DIPs, or how 15kW aux heat is staged, but Honeywell IAQ t-stat settings are:

0172 (system type) - 2E (HP with Auto Discover)

0174 (cooling compressor stages) - 2E (2 stages, AD?)

0176 (heating compressor stages) - 1E (1 stage, AD?)

0190 (changeover valve) - 0 (O/B terminal controls valve in cooling - what's that?

0200 (backup heat) - 0E (electric, AD)

0220 (stage 1 compressor cycle rate) - 3E (3 CPH, AD?)

0230 (stage 2 compressor cycle rate) - 3E (3 CPH, AD?)

0240 (Stage 1 heat cycle rate) - 5E (5 CPH, AD?)

0300 (auto/manual changeover) - 0 (manual - should I change this?)

0342 (outdoor sensor) - 1 (remote) - not sure why this doesn't say E as well, since the other functions with AD do.

0350 (HP compressor lockout) - 0 (none - good? Manual says if we have remote sensor, should select lockout)

0360 (HP Aux lockout) - 0 (none - I think we should set this, so if outside temp is above certain point, only HP runs? But what's reasonable?)

0365 (discharge sensor) - 1 (yes)

0370 (Indoor humidity sensor) - 0E (disabled, but should autodiscover? - Honeywell told me there was one)

0400 (ventilation control) - 0 (none)

0530 (Adaptive Recovery) - 1 (on)

0580 (compressor off time) - 5 (minutes)

0600 (heat range temp stop) - was 90, I changed to 75

0610 (cool range temp stop) - was 60, I changed to 65

0650 (extended fan time heat) - 0 (off)

0660 (extended fan time cool) - 0 (off)

0680 (heat temp control) - 2 (factory setting)

0690 (cool temp control) - 2 (factory setting)

Do these look reasonable for cold New England? Coldest month last year we used 74 kWh/day, this year 77 kWh/day and we're looking to reduce. Shut breaker for Aux Heat off a few weeks ago but we'll turn it back on around Tgiving and we'd like not to have huge electric bill next winter.

Comments (5)

  • 17 years ago

    0300 (auto/manual changeover) - 0 (manual - should I change this?) - You can change this so you will at least have the option of using autochangeover in the spring and fall

    0350 (HP compressor lockout) - 0 (none - good? Manual says if we have remote sensor, should select lockout) - since you have geothermal you don't want compressor lockout

    0360 (HP Aux lockout) - 0 (none - I think we should set this, so if outside temp is above certain point, only HP runs? But what's reasonable?) - This should be changed. You can start somewhere (maybe 20) and adjust it to works best with your house

  • 17 years ago

    FYI, the link to the earlier thread on this is below.

    funnycide's suggestion on the HP Aux lockout is a good one. The other thing I think I'm seeing is that your Aux heat is set up as one 15kW stage. For a HP, I think 0176 is going to be the number of stages of Aux heat (1 in your settings). If you look at the wiring, I think you'll find that there's only a W1 wire from the IAQ box to the heater. Changing this to multiple stages may help optimize the electric heater use somewhat.

    At some level, though, if the house needs the heat, well, it needs the heat. If your GSHP hasn't been keeping up this winter, there's some chance that other stuff is going on. I know we're getting a last cold snap down South today/tomorrow. If it's going to be even colder up there, then you might make the change to the Aux lockout and see if it keeps up.

    The adaptive recovery won't learn that quickly, but if the Aux is locked out, it won't make much difference.

    If you're having problems keeping the place warm, then I'd go back to your detailing on air sealing, insulation, etc. And I guess there's always the possibility that the HP is undersized.

    Here is a link that might be useful: RE forum thread

  • 17 years ago

    Since 0176 says "compressor" stages, I figured that's the HP not the Aux HEat but I'll check wiring. Didn't think installer would have changed Climatesmaster factory defaults (5 kW 1st stage). I do think it's a good idea to pick Aux Heat lockout - but what temp makes sense? 30-32 F or lower than freezing?

    No trouble keeping the place 68, but the electric bills in Dec - Feb are awful. Do you think 4 tons is too small for 2656 sf house in NW CT? Bear in mind that *highs* for a few weeks each Feb since we built have been in high singles - low teens, has gone below zero for lows those weeks too.

    Oh,k and should we keep it set steady on mid-high 60's as installer said, or drop the temp at night, try to bring it up 1*/hr in AM?

  • 17 years ago

    The IAQ manual says 0176 is "Heat or Heat Pump Aux Stages." Since 0172 is set as heat pump, 0176 is going to be number of Aux stages. The only way you're going to be able to tell how the heater is wired is to kill the power, open the cover and look.

    The heater jumpers may be factory, but if I'm reading this correctly, you'll either only get 5kW (doesn't make sense) or it's wired together at the heater to only turn on at full power. The way your stat is set up, aux heat is only "off" or "on" with no staging.

    As funnycide mentioned, the GSHP isn't affected by outdoor temp. You could try setting the Aux lockout to 20F and set up daytime setbacks for periods when you aren't there. If it's above 20F and the stat's only option for heating is the HP, based on the stat's settings, then that's what it'll run. And it'll cost less than the Aux heat. Give it a shot, it isn't going to hurt anything.

    I have no idea whether your system is sized correctly. FWIW, our dual fuel system has been running ~50kW a day, plus gas use below 30F (probably equivalent to electrical use). That's in GA with 2,200 sq ft, part of which has no insulation in the walls. My feeling is that 70kW/day in CT in winter isn't that bad.

    Maybe you need a woodstove? ;-)

  • 17 years ago

    I know GSHP isn't affected by air temp - just was wondering if we were trying to maintain 60* difference b/t inside and outside air temp, given R-22 walls and some air infiltration (working on that), whether it was reasonable to expect HP to keep up with that demand, or if 50* delta was the best we could hope for. I am home during the day (though maybe I can find a job in 2011 when DD starts 1st grade) so no setback except at night we'd like to set downstairs lower, upstairs is lower during the day but not too low since heat will just rise up stairwell from Zone 1 anyway.

    No chimney so no woodstove. I had planned for on in FR, but missed the fact that upstairs window would interfere. Plus now that we have furniture I think even a small one would be too tight. My mom also says we don't want the mess. We had one in old house, but the carpet was already burned so I didn't worry. She's right, though, not much room for wood in FR so I'd have to run to basement all the time. DH wants one in basement but I don't know how we could get one in at this point, esp. given where septic outlet is.

    Installer won't answer my ? as to whether t-stat is set correctly, just says tech can change it when we service this summer/fall. I guess I'll just have to ask the guy who comes out lots of ?s and make sure he checks the jumpers/wiring. I don't want to do anything with it b/c I don't want them to say I messed it up and void my warranty. Just the same way I told electrician his apprentice used wrong neutral for my LR circuit but didn't touch anything myself - had him come out and do it (I was EE in former life - until DD was 1 yr old).