Clueless about ducting

16 years ago

I am installing a Bryant Evolution with matching air handler next week. We are completely replacing the current duct system with round supply to flex out to the ceiling supply vents. We are removing the air handler from its current location and moving it into a conditioned closet since the attic is a unconditioned area. I am also having a 4 inch media cabinet filter system installed. I am going to put a louvered door on the closet for return air flow. I am confused as to where the media cabinet filter would be on the air handler and whether it will be enough return air, and to protect the system at the same time. The house is a 1300 square foot ranch with the air handler closet located in the hall furtherest away form our main living area and master bedroom. The unit is 3 ton.

Comments (12)

  • 16 years ago

    If you're pulling return air from the louvered paneling (and I think this is a two ton system), then almost undoubtedly the return will come from the bottom and it will be an upflow system (wrong?). If it's downflow, then I'd assume the louvered paneling to be at the top of the door. Either way, the media air cleaner can still be used. Your contractor will want to leave a sufficient space between the floor and air handler for return air entering (probably around 16" or so).

  • 16 years ago

    Thanks Ryan.Will that be enough return air. The Louvered door has louvered panels on top and bottom. The system is 3 ton.

  • 16 years ago

    The closet should sheetrocked and sealed to keep
    attic air from entering.
    The top of the closet should also be air sealed,
    meaning no gap around plenum, sealed not stuffed with insulation.
    the platform between unit and R/A should be
    caulked to walls.
    Foam strip installed at platform
    to door to seperate return from mechanical portion of
    closet. i wouldn't use a louvered door.

    what happens is that the closet is open to the attic
    allowing attic temps to enter the house. unit condensates
    insulation particles enter the house..hot near closet
    in summer..cold in winter.
    when the walls are not sheetrocked they suck attic
    air into the closet. sheetrock is cheap and installs
    fairly easily (I use ductboard to seal existing chases
    and R/A)
    if the return is not sealed and seperated from the rest of the closet you will have air that bypasses the filter
    and gathers on the coil.
    the door should also seal well, and have a seal at the
    bottom of the door to the floor.

    also make sure your ducts and supply boxes are mastic sealed,

    best of luck.

  • 16 years ago

    Energy...i am not sure what you mean when you say "The top of the closet should also be air sealed,
    meaning no gap around plenum, sealed not stuffed with insulation.
    the platform between unit and R/A should be
    caulked to walls. Could you please explain?

    The closet is completely sheet rocked and finished and is a inside wall. If everything is sealed right why would I not want to use a louvered door. My neighbor has his air handler in a closet with a small return vent built into the door. He has to open up the door on extreme cooling days to get optimum airflow. That was why I though a louvered door would be a good solution. I also want to be sure I have adequate return air flow.

  • 16 years ago

    sorry hope this will be better!

    when you open the closet door and look up at the top
    of the closet..what do you see?

    in most cases the plenum is attached to the ahu
    and penetrates the top of the closet to the attic
    where ducts are attached.

    if the sheetrock ceiling of the closet is tight to the plenum, and caulked then you have a tight air seal to the attic.
    if you have a gap around the plenum..(often stuffed
    with insulation batts)..then you have air entering
    from this gap. attic air is hot adds humidity,and insulation
    particles to your living space.

    I find gaps around the plenum from inside the attic, but you
    can check from inside the closet. if you see a gap
    take a look topside from the attic,
    small gaps can be caulked, but larger gaps will need
    more sealing methods. Last week I sealed around a plenum that had small gaps on 2 sides, but gaps that I could fit
    my whole hand into on the other 2 sides. I used ductboard
    (foil facing into heating closet) nailed in place and caulked to seal.

    your neighbor prolly has an undersized return.
    make sure that the platform is high enough to give
    you a properly sized return. better more r/a than
    not enough.
    congrats on your sheetrocked closet..there are many
    homes with exposed studs and walls that open into attic.

    keep in mind that stuffing insulation into holes does
    not work. insulation filters air but does not stop it.
    this is why the insulation stuffed into these gaps
    is so dirty..it filters the dirty attic air being sucked
    through it.

  • 16 years ago

    Energy....My current air handler is in the unconditioned attic. I am going to bring it down in the into the closet when i replace the system. I appreciate the headsup. I will be sure it is sealed.

  • 16 years ago

    Bizarre, energy_rater_la here we are required to place two
    ducts, one 12" from the ceiling of the furnace closet and a second 12" from the floor for combustion air. Not legal to
    seal it in any case.

  • 16 years ago

    in a closet for a heat pump you are required to
    introduce fresh air? thats odd.

    I'm not aware of any code issues with sealing
    heating closets, although with gas units fresh air is
    required.

  • 16 years ago

    Yes, for gas combustion but I don't believe the code excepts Heat Pumps.

  • 16 years ago

    Saltcedar..make me worry all day!

    irc 2006
    in chapter 17 section m1702.2 under combustion air
    it reads:
    Confined Space. Where the space in which the appliance
    is located does not meet the criterion specified in m1702.1
    two permanent openings to adjacent spaces shall be provided
    so that the combined volume of all spaces meets the criterion. One opening shall be within 12" of the bottom space (as illustrated..) Each opening shall have a free area
    equal to a minimum of 1 sq inch per 1,000 btu/h input raing of all appliances within the space, but not less than 100 sq inches.

    I believe this is what you are refering to.

    I'm no code inspector, but do try to check out any
    issues that may arise with the work I do.
    Sometimes I miss things..but I try to stay current
    to changes that affect my clients.
    As any code inspector will tell you the codes are subject
    to the interpertation of the code official.
    My understanding and the understanding of the code officials I have spoken with before undertaking this type of work is this.
    No mention of air sealing of the mechanical closet.
    combustion air is a different matter as backed up by above
    section. However..and this is based on the interpertation
    of the code here in La..in my area..
    dedicated combustion air for gas appliances within a mechanical closet....not a question.
    however once these dedicated permanemt pathways are installed, there is not a problem with sealing the top of the mechanical closet for gas units.
    heatpumps in a mechanical closet do not require combustion air.

    The energy code deals with the efficiency side, and it
    is about air sealing for a continuous air barrier between attic/crawlspaces and conditioned spaces. Thermal barriers
    (insulation) are to be installed once air barrier is completed..as insulation filters air.
    Building Sciences and better building practices reinforce this.
    There is always the issue of is the house too tight..
    (well not always..but it seems to be an excuse for leaky
    building systems) ASHRAE 62.2 deals with this.
    IMO its should always be 'build it tight and ventilate right'
    But then I test buildings and duct systems to know what tightness I am dealing with on each project. SO my pov
    is different than most.

    I'm not trying to be combatitive, and would like to hear
    what you think.

    (sorry to hijack your thread OP)

    have a good weekend all.

  • 16 years ago

    DonnWarry Behappy :-) I agree no need for air in a heat pump
    but I've never seen a (code compliant) furnace closet with out the vents.

  • 16 years ago

    here in La we just recently started enforcing the IRC
    many parishes (counties) don't have code officials at
    all.
    as a result of this...lack of minimal safety inspection..most heating closets for
    gas units are just left open to attic at the top of
    the closet, with all combustion air comming from attic
    around the top of the closet.

    units mold, if plenum and ducts are not well sealed
    (mastic) they mold. inside of heating closet molds.
    hot near closet in summer/cold in winter.
    gotta love hot humid climates..right?

    La adopted the code then got a one year delay due
    to hurricanes..so enforcement is slowly catching up.
    Not soon enough,,but better late than never!!

    unfortunately closets with dedicated combustion air is the
    exception not the norm.

    Texas is miles ahead of us..and Austin..I read good
    things about the energy efficiency there.