Sorry for the long post.
I have had an issue this summer with low pressure in my G/T loop system. I have a 12 ton system with a horizontal slinky loop. My loop does not have an expansion tank, auto-fill, or air separator installed. The loop system capacity is 300 gallons. I am located in the mid Atlantic region, at 1200 ft elevation.
After 2 years of operation, the loop system developed some air bubbles and had to be purged. We did that this past March and after purging, the loop system pressure was 50psi when the pump was running. About a month ago, I heard what sounded like an air bubble clunking at the top of the second floor (I have a GT heat pump up there) when the loop pump turned on similar to sounds we had before purging. I checked the system pressure  down to 20 psi.
I called the designer of my system (retired, company is now out of business) and he explained that the thermal expansion of the loop pipe is the reason for the reduced pressure. He claimed that the excessive heat this year has caused more thermal expansion then normal. After checking this out on line it appears that this is normal especially for a slinky loop system. He suggested that I juice the system which I did and I got the pressure back up to 40 psi. The delta P at the units is within spec when the pressure is at 40 psi.
I have a concern that when the ground starts to get cold and the loop pipe tightens up that the pressure in the system will grow too high  or higher than it needs to be. I asked the designer about this and he said the pipes would handle the increased pressure. He suspected the pressure could go up to 90 psi in the winter.
I have been thinking about this and was wondering about such a large pressure swing. If the system works within spec with a loop pressure of 40 psi, why let the pressure go up to 90 or more? After doing some research it appears that others have addressed this same issue with an expansion tank I am thinking about adding one to my system. Can anyone answer the following questions?
1) How large of a tank do I need?
I found this link (http://geoheat.oit.edu/otl/otl01-03.pdf) , see page 2. They calculate for an example system an 8 gallon expansion tank volume. I used the equation for my system, with a min temp of 30 and a max temp of 75, min pressure of 40 psi and max of 60 psi  and it says I would need a 6 gallon expansion tank. Does that make sense? I havenÂt added 6 gallons to the system when I juiced it, maybe 1-2 gallons max.
2) What type of tank should I use? I can get a Flexcon SXHT40 (http://www.flexconind.com/pdf/htx_install.pdf) will this tank work? I read that when putting an expansion tank into a G.T loop to use one designed for potable water systems due to the rubber membrane which keeps water (or in this case methanol & water) from touching anything metal and casuing corrosion. The install manual on the SXHT40 says not to use with potable water systems but it looks like it has the rubber membrane and would be just fine for my needs.
3) Where should the tank be installed?
I read somewhere that I should put the tank such that I pump away from the expansion tank - that would be on the supply side of my system. Is that correct? I have two 1" pipes with shutoff valves that are used when my system is purged (one on supply side, one on return side of the loop pump). I could easily add the expansion tank off one of these ports with a T Â still allowing a purge cart access but also allowing for extension of the loop to accommodate the tank. If I can do it this way, no cutting into the existing loop system is required.
4) Do I also need an air separator? If so, where should that be installed?
I read that I should put this device at the highest point in the system which would be somewhere on my second floor unit. I would rather install it in the basement near the loop manifold and expansion tank. Can I do that and will the air separator work OK not being at the highest point in the system?
5) If I should use an air separator, should I also attach a water supply line so that when air is burped out, the evacuated volume is replaced with water?
I read that GT manufacturers now make an integrated air vent with auto fill input. It looks like these units have a water hookup similar to my humidifier with a small (3/8 or 1/4) inch supply tube. I donÂt want to put an integrated unit in because I would have to cut into my existing loop system. But I can make one by using one of my PeteÂs ports and a backflow preventer for the water supply, and then adding the air vent somewhere in the system.
Thanks for the help.
refrigman1
sniffdogOriginal Author
Related Professionals
Jackson General Contractors · Miami General Contractors · Jacksonville Home Remodeling · Aberdeen Home Remodeling · Southaven Home Remodeling · Winston-Salem Home Remodeling · McAlester Home Remodeling · Johnson City Home Remodeling · Augusta Home Remodeling · Bennington Home Remodeling · Hobbs Home Remodeling · Salt Lake City Home Remodeling · Sarasota Bathroom Remodelers · Frisco Bathroom Remodelers · Seattle Bathroom Remodelersfsq4cw
sniffdogOriginal Author
fsq4cw
sniffdogOriginal Author
fsq4cw