Contractor says geo needs back up?

18 years ago

He was here doing a load calc this week. We're looking at Waterfurnace, and he's stating that we need a split system with either electric or oil backup.

Help me understand this. I see how an air-source HP needs backup at lower outdoor temps, but why would geo need backup since the whole premise is that underground temps are stable and warmer than air?

We're in VA, so it's not as though we're in an extreme climate, either.

Comments (5)

  • 18 years ago

    Probably only need backup for when or if the sucker breaks down.

  • 18 years ago

    I don't understand either. Ask for an explanation as to why you'd need backup.

  • 18 years ago

    Your heat loss is higher than your heat gain. If you installed one big enough for the heat requirements, it would be to big for the cooling load.
    Thats usually the reason.

    For instance, in the north it is common in commercial buildings with GSWHP's to have hot water reheat coils off a boiler to boost the heat output around the perimeters. As you head farthur south and the loads equalize or the cooling loads become higher than heat requirements,and HP's are more common, most southereners have a tough time understanding that till it's pointed out.

    I chuckle everytime a northerener doesnt understand why a house will need 5 tons and be only 2900 sq ft. Well because it is hot down here.

    Hows this; in NY I had a 60,000 furnace and 2.5 tons
    In TX I have 8 tons and only 80,000

  • 18 years ago

    zl700, that actually makes lot of sense. If I'm recalling correctly, the load calc showed a heat loss that was twice as much as the heat gain.

  • 18 years ago

    beth

    I live in VA too and have a 12 ton GT system. All 3 of the heat pumps have electric heater packs (I call them my toasters) that come on when there is a problem with the system or when it is really cold outside and the heat pump needs a little boost.

    During our first winter this past year, the toasters on my 6 ton unit came on quite a bit. The first time we had a compressor go bad due to a power surge and it took 10 days to get a new one. The second time we discovered that the guys who installed our system had the wrong mixture of anit-freeze and they forgot to load balance the loop field - so my 6 ton unit kept calling for the emergency heat because the two 3 ton units were pulling too much flow from the loop field.

    Once we got those bugs worked out, the emergency heat never came on - even when it was in the teens outside. I am glad I have the backup heat, but I hate to see the Aux light go on. That just means I am burning up dollar bills by the minute.

    This winter I plan to augment the GT heat with my wood burning fireplace insert which can give me an extra 40,000 BTU's if I crank it all the way up. If I use that during the extremely cold days, I hope to never see the dreaded red light (toaster ON) again.

    One thing you need to think about is what happens if the power goes out - since that will knock out your GT system. If you have oil or gas as backup, you could install a small power generator to power the controls for the gas/oil burners and the HVAC fans - but they need to wire it properly so you can easily do this (put in a seperate sub-panel for the power generator circuits, and run the backup heat controls and HVAC fans off circuits in the the sub-panel).

    You could try to backup the entire GT system, but the power generator would need to be quite large to handle the compressor start up loads. My 6 ton unit would require a 50 amp (240 volt) power gen just to start the compressor. II tried to backup all 3 units, I was looking at 110 amp power generator at 240 volts (that's a 26 kW generator!!) just for the heat pumps.

    I decided to use my fireplaces as my backup heat. I have 2 gas inserts and one wood burning insert - all rated as heaters. I put in a 12 kW power generator which will power the controls for the fireplaces, the small blower fans, outlets, refrig's, and other necessities. I plan to use 2 large pedestal fans to circulate the heat generated from these 3 fireplaces around the house.

    I love the GT system, but it stinks when the power goes out. We had one 26 hour outage and the temps outside got down to below 20. The inside temp got down to the low 50's. At that time I did not have my power gen so only the wood burner worked - but no blower fan. We made it through but it sucked..