new system not sufficiently cool

16 years ago

About a month ago, I had a new Lennox system installed. The crew seemed competent and the installation seemed to go well, but the system is struggling to keep the house cool. On hot days (95+), with the thermostat set to 74, it will cool to only 77-78 degrees and that's running essentially non-stop. I'd appreciate any suggestions on where things went wrong and what I can do about it.

Here are the details on the system:

AC: XC-14-36

F: G-61mpv 36-71

Coil: C-33-36

T-stat: ComfortSense 7000

Merv 16 air purifier

White-Rodgers humidifier

I live in Oklahoma and the house is just shy of 1700 square feet. The installation company has been out three or four times and each time tweaks something new (blower speed, humidity setting on the t-stat, etc.). They're coming out again Monday to take more readings. It seems to me that if we've established that there were no problems with the installation, then it must be that either the system is defective or it is undersized. Any thoughts?

Comments (9)

  • 16 years ago

    One other bit of information. The tech measured the temperature differential, in the ductwork coming in and going out of the system (as opposed to the return and vents), and it was 15. I thought it was supposed to be closer to 20?

  • 16 years ago

    carlosok

    fifteen is on the low acceptable side.

    what have the outdoor temps been in your location?

    take a measurement of your inside supply temp at different registers using a digital thermometer. note time, location, and outdoor temp. morning, afternoon, and evening reading.

    old system was three ton? if so, how did it perform?

    has system been running continuously?

    post back.

    IMO

  • 16 years ago

    Thanks Tiger. I'll post back with measurements tomorrow.

    Outdoor temps over the past month have been consistently hot, above 90 most days and above 100 on several days. Just yesterday and today, we've had cooler temperatures of around 75. (As a result of the break in the weather, the tech did not return yesterday as planned).

    From what I can tell, the new system runs continuously during the day any time it's 95 or above. I'm not as sure how much it's running at 90-95, but it still seems to be fairly continuously. I don't have the full picture because I work during the day -- but that's what I've observed after work and on the weekends.

    The old system was a three ton package unit by Goodman from 1991. It burned lots of energy, but got the job done at three tons, even in the same type of hot (100+) weather. It's disappointing to get a new system and end up a step back as far as keeping the house cool.

  • 16 years ago

    carlosok

    I researched the performance/eff numbers on your system. not surprised what I found. While Lennox calls the XC14-036 a three ton AC condenser, in fact your particular system as configured only has a 33 KBTU output.

    see below from the AHRI Directory.
    3130740 Active Systems XC14 SERIES LENNOX INDUSTRIES, INC. XC14-036-230-03 C33-36+TDR+TXV G61MPV-36B-071* 33000 12.20 14.50

    This is really typical of Lennox more than they would care to admit. Full three ton BTUs would be 36 KBTUs. So in fact you are short by 10%. In your case this could make a significant difference especially on very hot days.

    a major reason why I don't like Lennox. all the evap coil/furnace combinations on the XC14/G61MPV-36B-071 yielded short BTUs on cooling.

    I think Lennox and the industry needs to clean up their act and be more transparent on performance/efficiency numbers.

    while you may have equipment/install issues, this has to be large part of the problem you are experiencing.

    sorry for your trouble.

    IMO

  • 16 years ago

    Well that's disappointing.

    I suppose the next questions are (1) what is the fix, and (2) am I responsible or is the installer?

    On (1), if I understand correctly, what's needed is a larger condenser, presumably 3.5 tons. As opposed to changing the coil or the blower (can you just change the fan or would that require changing the entire furnace?). If you change the condenser to 3.5 tons, would you also need to increase the fan/furnace to 3.5 tons?

    On (2), am I out of line in insisting that the installer replace the current unit with a higher size (assuming that's what we need to do)? Or am I on the hook? Would it be reasonable to say that I'll pay the difference in the price of equipment but the installer puts it in at his cost?

  • 16 years ago

    carlosok

    there is no easy fix such as changing a setting.

    I think you are in an uphill climb. what may be reasonable to you may be unreasonable to your installing dealer.

    I did check the directory and it does state that your furnace can accept a 3 1/2 ton AC condenser. of course, you would need the best evap coil for this application.
    and if you do go a larger condenser, this probably means some type of modification to your ductwork system both supply and return. That would definitely be at your expense.

    my suggestion is a sitdown face to face with dealer/owner not a sales guy. do not make a proposal-let them do that. also you should watch system's performance when weather moderates.

    I am sorry for your situation. BTW, was a load calculation even performed prior to install? if so, at what outside/inside design temps. if you did any research before your purchase, you would see from this forum and others that a load calc is always recommended. any chance for insulation upgrade that might help?

    IMO

  • 16 years ago

    I'll plan on talking with the owner. I don't want to cause trouble, but I do expect a brand new system to do the job.

    No full load calc, which is my mistake. I got 5 bids and all of the companies specified a three ton system. Some guys did more calculations than the others, but no one did a full Manual J calculation. My guess is that three tons would have worked -- if Lennox was a full three tons. It's that last bit of performance that's missing.

    The weather has remained cool today, around 80-85. The system seemed to be working fine this morning, cycling on and off. Temperature at a register close to the supply was 54.4; at the end of a line it was 56.3. The outside temp was 81 at the time. I'll check when it gets hot again.

    I'd like to improve the insulation, if there's a way to do it. The house was built in 1938. My guess is that there is no insulation in the walls, and with a brick exterior it would be difficult to add any. Lots of old windows, although I do have storm windows. Underneath, there is a three-foot ventilated crawl space, with no insulation on the floor joists. The vents can be closed off in the winter. Above, there is a large attic with batt insulation that is maybe 15 years old.

    Thanks again for all the help. You've been great. -C

  • 16 years ago

    carlosok

    there is nothing wrong with those supply temps. you might call an insulation contractor for some ideas/estimates to improve overhead and underneath(I would concentrate on overhead first). there are alot of claims regarding new DP replacement windows. I have found that while they are nice/look good over sgl pane/storm windows, the reduced cost of AC cooling/winter heating are greatly exaggerrated. certainly any payback is way out in the future.

    I think at the very least your dealer should perform a thorough load calculation both cooling and heating at design temps both of you agree to. I doubt if we would be talking about this situation if you were truly getting 36 KBTUs of cooling.

    I would appreciate letting me know of your progress.

    Good Luck!
    IMO

  • 16 years ago

    In this stage of the game the sealing/insulating might be your best bet if the owner doesn't make things right. If you sealed things up better and got some more insulation the system might maintain better.

    I have to say this is another that a energy audit with infrared temp camera and blower door test would be extremely beneficial. This will help show where you can put your money that will matter most.

    I would attempt to argue that you were told '3 tons' of cooling were called for in multiple other bids other than this one and the system as quoted and installed falls short of what is really considered 3 tons of cooling.

    I do think that if you are stuck with it I would research the sealing and insulating and see how much effort is needed to make the home fit the system. It might not take a whole lot of work or money to make it happen either.

    Best of luck to you and please report the outcome.