New HVAC system

16 years ago

I live in Massachusetts in a 1400 sq ft ranch. Looking to replace ancient system. I was given the following estimate:

TUH2C100A9V4VA with a 3-ton XR15 Seer Trane A/C system

4TTR5036E1000A for the first floor.

A/C coil M#4TXCC037BC3HCA

AprilAire energy star thermostat

I would like to know if the A/C coil is correctly matched to the system and what thermostat would be recommended for this 2 stage furnace. I am also replacing all duct work - is there anything I should be aware of with regards to the duct work?

Thanks for the help.

Comments (7)

  • 16 years ago

    wheelchairlady

    excellent equipment. wrong thermostat. the correct thermostat would be Trane's 803 or the identical equivalent from Honeywell.

    and I question the sizing of both the furnace and the AC condenser.

    what size furnace and AC are you replacing?

    post back.

    IMO

  • 16 years ago

    100,000 btu furnace from 1987
    Currently no AC

    Old ranch from 1959. Only 1/2 house has R-13 fiberglass insulation and new windows. Rest of house has old windows no insulation.

    Hope this helps.

  • 16 years ago

    wheelchairlady

    you need a load calculation both cooling and heating.

    at the best, your current furnace would be 80% eff, possibly less efficient. I suspect that the 80 KBTU XV95 furnace would be more than adequate for your home. only a properly performed load calc would confirm the correct size.

    please request this from your dealer.

    I would also want a new refrigerant lineset and a 4-5" pleated filter media cabinet.

    IMO
    Good Luck!

  • 16 years ago

    >>properly performed load calc
    When I asked for a load calculation this is what I am told:
    "I've been doing this for 30 years. This size ranch in this town needs a **** furnace and *** ac unit." Then I get a "load calculation" sheet with all kinds of numbers with the bottom line being exactly what he said it was.

    I got 3 such calculations.
    80k furnace 3 ton ac
    80k furnace 2.5 ton ac
    100k furnace 3 ton ac

    I like the company who quoted me 100k since he said I might need the extra btu's if I decide to heat the full basement when I finish it in a few years - "You can always use more heat". Don't know if he was right which is why I asked in this forum.

    The bigger question to me is if the ac is sized correctly. All of the HVAC guys said it was between a 2.5 ton and a 3 ton. My brother had gone with a bigger unit and is miserable as the unit turns on for 15 minutes then shuts off. He keeps telling me not to oversize the ac. Your opinion?

  • 16 years ago

    1400 sq. ft. ranch doesn't need 100k btu furnace.
    80K btu is fine if its 2-stage. 2.5 ton A/C is the correct size. I wouldn't get 3 ton. Seriously - oversize really is not the way to go.

  • 16 years ago

    Can you tell me if this is a matched system?
    TUH2B080 with a 4TTR5030 a/c unit with a TXCB032BC3 coil

    Thanks for your help!

  • 16 years ago

    wheelchairlady

    according to AHRI that is not a match. you would need a different evap coil.

    here is a suggestion.

    3554442 Active Systems XR15 TRANE 4TTR5030E1 4TXCB004CC3 *UH2B080A9V3 29000 13.00 15.25 1

    I would recommend the 803 Trane stat or identical HW equivalent.

    you should also consider a wholehouse 4-5" pleated filter media cabinet like the Honeywell 200 or Trane Perfect Fit(would be more expensive).

    IMO