Data of AC Operation

19 years ago

I am trying to determine where the fault lies for lack of moisture removal of my central air system. Below is data that is transmitted to my thermostat in the cooling stage:

Cool Stage..........Low Speed.

Airflow CFM.........430.

Coil Temp...........86 Degrees.

Blower RPM..........494.

Static Press........0.15.

The room temperature was 76 degrees with 58% Rh.

The temperature differance of the incoming air vs the outgoing air is 14 degrees. There is no condensate in the drain pipe.

Does anyone see anything wrong with these numbers?

Comments (3)

  • 19 years ago

    Coil Temp 86 Degrees?? Where is the tstat getting that information from? Impossible! More info is needed then what you supplied here. You didn't say what the setpoint was. Or the size of the unit. 430 CFM is nothing and your static pressure is practically non existant. With those readings one would tend to think your coil would be icing up but with that delta T it doesn't appear to be. By any chance is this a heat pump and has anyone ever slapped a set of guages on this system lately?

  • 19 years ago

    The setpoint was 78. there will be a 2 degree drop when the humidity is set for 46 Rh. its a 2 ton AC and a technician put guages on the lines recently and check ok, he said. Its a "Bryant system consisting of model 315AA varible speed Plus 80V furnace, Model 598BNX two speed Puron Plus air conditioner and a Evolution thermostat model SYSTX and a Coil model CD5AXA.

    If there is something wrong with the numbers, then the control board circuitry which communicates with the thermostat is either receiving the wrong signals or is sending out the wrong signals.
    I have had 3 visits on my complaints about little or no moisture removal and the techs do nothing more then hook up guages and ammeters instead of troubleshooting the circuit boards between thermostat, furnace and the condensor.
    I have already spoken to a field manager about the lack of a complete check on my system and he and the installing dealer are going to make an appointment to check my system again. From what I learned is that on my two speed system, its should be the low speed that removes moisture, but I find thats not the case because the air temperature before and after the A coil is 72 and 58 degrees respectively; a 14 degree differance. I do not see any moisture removal. But if I force it into high speed by dropping the setpoint 5 degrees lower, then within say 10 minutes, I see a lot of water coming from the evaporator and the temperature differance is now 20 to 24 degrees. When my system was new, It work great for about 7 weeks. In the past, the dealer told me that my system does develop a history that can affect the operation. I think thats stretching the truth a bit. If it were true, then I wonder how can I change my basic and advanced settings, turn the thermostat up or down or shut it off, without leaving a history to affect the operation. There's also a programable option called "High Speed Latch" which does not work. In the default mode, the compressor should operate in low speed most of the time and if rising outdoor temperatures such as in the ninetys, then it should go into high speed. The other user choices are settings of 80 through 110 degrees that only the high speed will operate. None of these work.

  • 19 years ago

    Here is a clearification of the numbers I previously presented:

    Airflow CFM equals Indoor cfm measurement.
    Blower RPM equals rpm feedback from indoor motor.
    Coil Temp. equals temperature of the outdoor unit coil (only available on communicating outdoor units).
    The stage and static pressure are self explanatory.

    This is not a heat pump but a two stage air conditioning.