Replacing system: opinions on quotes

16 years ago

Here is where we are at:

Company A : only company to do Manual J calc; Trane; prices include repairing and sealing existing metal duct work; adding 3 supplies and 3 returns; reinsulating all ductwork to R6;

XB14 4TWB4042E / 4TEE3F65B 8,300

XR15 4TWR5042E / 4TEE3F65B 8,730

XL15I 4TWX5042A /4TEE3F65B 9,490

add $170 for IAQ upgrade

is it worth $170 for the thermostat upgrade?

Company B: American Standard; completely replace ducts with flex and add 2 supplies; no additional returns;

4A6H5042E1000A / 4TEE3F65B1000A 10,062

Company C: Carrier; completely replace ducts with flex and add 3 supplies; no additional returns;

2HCB348A003 / FV4CNF005T00 10,055

25HPA648A003 / FE4ANF005T00 11,845

All quotes include new copper, drain. etc. Anny advice or comments would be greatly appreciated. Thanks. johnnymac

Comments (3)

  • 16 years ago

    johnny

    what is your location?

    insulation is relatively cheap and has good payback. go with R8 over R6.

    I find the pricing on high side. Ductwork changes/modificationa are not too expensive as long as good accessibility.

    I like the XR15.

    Backup heat strip should be staged. what size was quoted?

    The Carrier quotes are 4 ton, while the Trane and AS are 3 1/2 ton systems.

    these are my minimum specs for a new HP system. both outside and inside units should be replaced to have a properly matched system.

    15 SEER, 12.5+ EER, 9 HSPF
    best matching VS air handler
    full BTUs in both cooling and heating for your rated size
    R-410a refrigerant(same as Puron)
    scroll compressor preferred
    electronic demand defrost preferred
    thermostat with "dehumidify on demand" feature
    staged backup heat strips
    new and correctly sized refrigerant lineset

    you want a thorough inspection of your ductwork system. size, overall condition, supply and return lines, insulation qualities, leak test, etc.

    any hot/cold spot issues in your home should be addressed.

    I would only use authorized dealers for the various brands that provide quotes. see mfg websites.

    I would look at Trane/AmStd,Rheem,Carrier/Bryant.

    IMO
    Good Luck!

  • 16 years ago

    Tiger,
    We are on the west coast of Florida across the bay from Tampa. Accessability to the ductwork is bad. Very tight up in the attc. 3/12 pitch, about 3' tall at the peak. Duct work takes up most of the room. I am definitely leaning towards company A and the XR15. They are a Trane dealer, the only company who did a Manual J calc to size the unit and they have been very responsive to any questions. Not sure what size heat strip. Maybe 7.5kW? What is a staged heat strip? Also, is it worth the $170 for the upgraded IAQ T-stat? I will ask if they can upgrade insulation to R8 instead of R6. Thank you so much for sharing your expertise. johnnymac

  • 16 years ago

    johnny

    R6 insulation will be fine for Tampa area location.

    7.5KW heat strip would be fine.

    I would go with HW VP IAQ stat for its DOD feature-dehumidify on demand.

    IMO
    Good Luck!