Sizing heatpump based on heat loss analysis

19 years ago

I plan on building another house in 2008. I currently have a closed loop geothermal system and love it, so I plan on installing one again. However, I don't want to make the same mistake in oversizing my equipment this time.

So looking back, what would have been the proper size for my current house?

3160 SqFt, 2 floors

Stonington, CT

Heat Loss 34.9 kBtu/hr

Recommended output Required 40.1 kBtu/hr

I have two 3-ton GSHPs (72,000 BTUs?), one in the basement for the main level, and another with a air handler in the attic for the upstairs.

Comments (7)

  • 19 years ago

    Come on, fsq4cw (Steve). This question has your name written all over it.

  • 19 years ago

    Let me ask this. Would you go with a 4-ton unit for 48,000 BTUs? Or, would a 3-ton (36,000 BTU) be the smarter choice since you can count on the heatstrips to kick in on the most demanding days. Hmmm?

  • 19 years ago

    Razl:

    I can't comment on geothermal units.

    I have a 3-ton heat pump in my 1700 square-foot home in Baltimore. I replaced a 21 year-old Trane with a same sized Goodman (no Manual J calc done). I may be a bit oversized, but I need all the available btus for heating to stay off of the back-up strips. If I want more humidity removal in the summer, I drop the temperature down a degree or two - no big deal. In August we had a 105 degree record-setting day. I could have frozen meat in my family room on that day if I wanted to. I'd rather have it that way than have the unit running non-stop and can't keep up. Plus, the unit is new and will only lose capacity as it ages.

    Not sure how this applies to geo.

    Take care.

  • 19 years ago

    I did not comment on this because despite it sounding like a simple question, it isnÂt. It sounds to me deceivingly simple (which is why I didnÂt post) and as such can only be answered on this forum using Ârules of thumb  and thatÂs how we get into trouble! (Gary, you WANT to get me in trouble, donÂt you?)

    IÂm not going to take the bait, but IÂll nibble a bit with some things that cross my mind.

    IÂm more interested in heat gain than heat loss (for the purpose of this discussion). Under sizing for heating mode can be made up for with a plenum heater. Mess up the A/C side of things and guess what? YouÂve got even bigger problems.

    Since you Âlove your installation, use the same installer; discuss your issues with him. Perhaps 2-3ton systems are what are required. I would recommend units with 2-speed compressors and ECM blowers if it were all forced air. This still leaves open the question of whether this is more capacity than needed and the economy (or lack of it) of a larger ground loop. Again, consult your installer! (Do the Manual J calcs!)

    The other thing I would do is design the installation with both units in the same basement mechanical room.

    IMO

    SR (Steve)

  • 19 years ago

    I didn't mean this to be a trap. I guess it's more complex than I thought. The installer did do a manual J but this was the first time he worked with my builder so he could account for air infiltration which as I understand it, plays huge roll in estimating equipment size.

    As I recall, he came up with 4-tons total for a tight build but said he felt safer with 5-tons. Because I did not have an easy "chase", we agreed to do a split system, so an air handler went in the attic. I had to go with 6-tons becuaseit was either two 2-tons or two 3-tons, so he rounded up. I guess hindsight, dual 2-tons would have been just as good.

    Last question, does a HPs tonnage take into account the backup heat strips or is that additional BTU output?

  • 19 years ago

    "Last question, does a HPs tonnage take into account the backup heat strips or is that additional BTU output?"

    - I believe that an air source heat pump is supposed to be sized for cooling. Additional heating btus required are supplied by the electric strips. Not sure about geo heat pumps. Note that I am just a lowly homeowner and not a pro.

  • 19 years ago

    Re: razl

    I didnÂt think you were setting a trap. Sometimes itÂs wiser to keep oneÂs (my) trap shut than to sound like a fool. Your last post confirms that design is a complex mix of many factors.

    Most heat pumps list their size by cooling capacity. A nominal 5-ton HP usually means 60,000BTU. Heating capacity of this same unit may only be 48,000BTU or 4-tonnes (or less) Â but still requiring a properly designed 5-ton ground heat exchanger. Back-up heat strip BTUs are in addition to HP BTUs. Remember, unlike air-source HPs, GSHPs back-up works in tandem, not instead of, so a geo system may require less plenum back-up heat than a comparably sized air-sourced HP system.

    Geothermal has to be properly designed from the ground up. No 2 systems will likely be exactly the same. ItÂs a custom design every time  particularly with regard to the ground heat exchanger. This is why a good designer/installer is worth his price. You donÂt want to get this wrong; it MUST be designed and installed right!

    SR