17 years ago

We have a 2nd story MBA with a vanity containing two sinks. Both sinks have separate drains that join in 1 1/2 pipe. Is 1 1/2 large enough for code puposes? There's nothing else besides the sinks on this portion of the branch. We are located in Norfolk, VA and I believe we are governed by IBC.

Comments (5)

  • 17 years ago

    2 sinks are not allowed by code to drain into a 1 1/2 pvc pipe..what is common by code is inside the wall..there is a
    2 x 2x 1 1/2 cross the sinks drain inti the cross
    via the 1 1/2 on each side, of the fitting
    so that..where the 2 drains meet, is 2"..
    drains are sized by what is called a fixture unit
    each fixture is assigned a unit number..a lav in a residential bldg is given the number 1
    and a 1 1/2 pipe can only carry the waste from 1 fixture unit. but 2" can handle them booth

  • 17 years ago

    Just as a quick follow up, and not to answer my own question, but.... per my research, a horizontal 1 1/2 pipe carries up to 3 DFUs. Assuming a sink = 1 dfu (and thus 2 sinks = 2 DFUs), just curious why the 2 inch pipe requirement? Just want to understand the reasoning here. Thanks!

  • 17 years ago

    for a couple of reasons,
    each fixture has to have its owh vent
    unless you use a common vent, by using a cross fitting
    but..if you use a cross, then the barrell of the fitting must be 2x the diameter of the trap it serves
    which a lavs trap is actually 1 1/4 x 2 is 2 1/2 inch
    here we cheat a little and use the od of 2" pipe
    calling it 2"
    AND...a gotta drag out the book..will get back with verbattem

  • 17 years ago

    Sorry... should have been more detailed in my explanation. I am NOT planning on connecting the drains via a cross fitting. Each sink has it's own trap. Connection to the horizontal run (1 1/2 pipe) is accomplished via a sweep elbow for one sink and a combination wye fitting for other.

    All my research has lead me to lav. sink = 1 DFU and 1 1/2 horizontal can carry 3 dfu's, but wanted to double check and make certain I'm not missing something here. Still learning.....

  • 6 years ago

    I know that this reply is 11 years too late, but the answer to your question is yes, 1 1/2 inch branch drain pipe is sufficient to drain 2 master bath sinks in your situation. Per International Residential Code 2015, P3005.4.1 Branch and Stack Sizing (which references Table P3005.4.1), a 1 1/2 inch drain pipe can handle up to 3 drain fixture units in a horizontal direction; and 4 drain fixture units in a vertical direction (as long as the source is not a water closet). A single bathroom sink/lavatory drain is 1 drain fixture unit; therefore a 1 1/2 inch drain will accommodate a double bathroom sink vanity. Make sure you follow P3005.1 Drainage Fittings and Connections (and the reference Table P3005.1) which specifies the proper pipe connections/fittings to use to connect it all together.