Air pressure test for PVC?

19 years ago

Where can one purchase one of the air gauge things you hook up to your pipes and pump the pipes full of air to test for leaks? Are these generally available at the big boxes, or are they more specialized? Not even sure what they are called to be able to ask around.

I ran a pvc line for an ice maker supply and would like to test before turning on the water. I assume the air pressure test is the best way. Any other methods that would be better?

Hmm, just noticed this at http://www.ppfahome.org/pvc/index.html: "PVC piping systems should not be tested with compressed air or other gases either." So...how does one test for leaks?

Thanks.

Comments (11)

  • 19 years ago

    The Plumbing codes prohibit the use of PVC piping for water lines within a structure.

  • 19 years ago

    Oops. What is the reason for that prohibition?

  • 19 years ago

    Look at the writing on the pipe wall..PVC has a maximum allowable working temperature of 73degF. Not all residences have air conditioning and even with air conditioning the actual location where the pipes are run may exceed that temperature such as in an attic space or inside an outside wall on a hot summer day. For that reason PVC is approved for Supply lines, which are the buried lines from a well or municipal main but it may not be used for Distribution lines within a structure.

  • 19 years ago

    Are you sure about that? I found this online:

    "The maximum use temperature for PVC pressure pipe is 140 degrees F."

    And also this:

    "From 1/2" to 2", it is rated at no less than 140 psi at 73°F."

    So it seems like maybe the 73 deg number is the basis for pressure testing and not necessarily a max temperature? No idea. I'll look at the markings on the pipe and see what else I can find out.

  • 19 years ago

    cstrombe,

    Just for clarity, are you talking about pvc or cpvc?
    CPVC can be used for hot or cold if codes allow it.

    Run your line in CPVC. Use primer and glue that is suitable for CPVC and otherwise do a good job on the joints and then turn on the water (after 24 hours). You will be fine. Forget the tester.

  • 19 years ago

    California just this year changed the code to allow pvc for cold water and cpvc for hot or cold. Finally! I thought we were the last state to make that change, but I could be wrong.

    Here's how to test your work: have second person stand by the new work while you turn the water back on. If no screaming or hollering is detected, your test is satisfactory.....(-;

  • 19 years ago

    Quote--"California just this year changed the code to allow pvc for cold water and cpvc for hot or cold. Finally! I thought we were the last state to make that change, but I could be wrong."

    California must be working backwards..When PVC first became available it was approved by the IRC & UPC for both Supply & Distribution Piping. Later when CPVC became available they ammended the codes to permit PVC for Supply & Cold Water Distribution but required CPVC for Hot water Distribution. In the late 1980's the IRC & PVC prohibited the use of PVC for any distribution within a structure.

    Per the IRC Table 2904.4.1 the approved choices for distribution within the structure are:

    Brass Pipe
    Copper pipe types K,L&M
    CPVC
    Galvanized Iron Pipe (not under a slab)
    Polybutelene Pipe
    PEX plastic Tubing
    PEX-AL-PEX pipe

    Under the Uniform Plumbing Code per table UPC-604.1 you may use:
    Brass Pipe
    Copper types K,L & M (type M only above ground)
    Ductile Iron-(under a slab it must be machine wrapped and all joints field wrapped to equivalent protection)
    Galvanized Steel Pipe-(under a slab it must be machine wrapped and all joints field wrapped to equivalent protection)
    PEX plstic tubing

    On the PPFA (Plastic Pipe & Fittings Association) website you can find complete installation manuals for PVC, CPVC, & PEX as well as a number of other manuals in PDF format for free download.

    PPFA free publications---in PDF format for download
    http://www.ppfahome.org/publications.html

    Here is the CPVC installation manual. It is an easy read 8 page manual in PDF format for easy download.

    CPVC INSTALLATION MANUAL
    http://www.ppfahome.org/pdf/PPFA_CPVC_Installation_Manual_2006.pdf

  • 19 years ago

    What's their problem with pvc (other than that unions don't like it)?

    Personally, I'll take pvc over galvy any day. Every iron or steel pipe we take out is rusted, and often clogged entirely. Copper is great, but have you priced out a copper job lately? Yow! Haven't used pex yet, but it sure seems to have advantages. I've never seen brass pipe used for water supply out here.

    Until this year we always used copper, but when the price tripled, we switched to pvc. It's definitely the value leader. But I'm wondering why the IRC and UPC don't allow it.

    And yes, California is about 50 years behind the times when it comes to building codes. Too often, our definition of "progressive" seems to be to regulate things into the ground, and never change it. We miss out on a lot of great technology because of it.

  • 19 years ago

    Jake, I'm talking about PVC not CPVC.
    Jason, the PPFA site that lazypup mentioned is where I found the PVC temp rating info, on this page: http://www.ppfahome.org/pvc/index.html

  • 19 years ago

    I am seeing information on that site that PVC decreases in pressure rating and stiffness as the temperature increases. (at 120 degrees F pressure and stiffness ratings decrease by half). I suspect this may be the issue the codes have with it.