Air flow/hall thermostat problem

11 years ago

We recently bought a 1960's ranch house, built on a slab in a southern community. The Hvac is a heat pump that works well except for one poblem. The thermostat is in a hall which has no heat vents but two large return vents. If all the doors off the hall are clsoed, it becomes a closed room with no heat vents so the system runs a long ti e to reach the set temp so that the rooms of the house are either too hot (if heater is running) or too cold (if a/c is running). We can get around this by playing with leaving a door open or patially open which lets some heat get to the thermostat so it gets to temp soon after the rooms are warm. Sometimes however, when it turns on and sucks air through the return vents in the hall, the open door will slam shut.

We are thinking there must be some kind of adjustable door vent we could place in one of the doors to regulate this a little more precisely and to avoid the door slamming.

Anyone have the right product or solution? Thanks.

Comments (8)

  • 11 years ago

    Relocate the thermostat. It's not that difficult.

  • 11 years ago

    You have one air handler/heat pump that is served with two returns in the same hallway?

    It seems like your base problem is that you have inadequate return air flow. With supplies elsewhere and the returns in the hall, you need to have air flow from ALL the rooms into the hallway where the returns are. The typical low cost way too do this is undercutting the doors. Alternative methods are to install jump ducts (transfer grilles, transfer grills, transfer grates,...) in the walls or through the attic space. Ideally, you have a return in each room, but that is costly. The door undercutting is often subverted by later carpet or flooring installation.

    If you have pressure differentials like you describe, opening one door is not going to work very well. You pressurize the rooms with the doors closed and depressurize the hallway or what ever room the returns are in. What happens then? Air blows right out of your house from the pressurized rooms, into the attic, past leaks around the windows and wherever there is a little crack or hole. In the room where there is negative pressure, outside air gets sucked in, from the attic,.... The sucking air in from a hot/humid outdoors sometimes results in condensation and wood rot.

    For now, leave all your doors open. Maybe later undercut them to an area equal to the supply grill size in that room or install grills, jump ducts or transfer ducts.

  • 11 years ago

    Thanks for the explanation, ionized.

  • 11 years ago

    Thanks geoffrey, we considered moving the thermostat but i think ionized has pinpointed the issue.

    Btw, i think somewhat recent carpet in the bedrooms may have caused or exacerbated the problem.

  • 11 years ago

    good post Ionized!

    the rooms off the hallway need return air pathways.
    doors undercut up to 1" will allow air from
    one supply to return.
    but if you've just carpeted, then the carpet
    blocks the air flow.

    in a year or two you'll see ghosting under
    the doors where the dirt filters through
    the carpet on its way to the hallway return.

    you could add transfer grills in the walls
    above the doors, or to the side of the doors.
    don't line them up though, make one higher
    and one lower. this will eliminate light transfer
    and help with noise transfer. if you put
    them back to back, you'll have both noise & light
    issues.

    or you could do a jump duct from each room
    into the hall.
    supply boxes, duct, supply grills. the duct
    "jumps" the air from bedroom to hall.
    this would be an attic install, and the least
    intrusive solution.

    best of luck.

  • 11 years ago

    Energy, with transfer through the walls, do you recommend duct between the grills or do you just use the stud space?

  • 11 years ago

    Best and cheapest option would be to re-locate room stat/thermostat. You can get it wireless option and easily control the temperature with your smart phone or ipad

    Here is a link that might be useful: London Plumber

  • 11 years ago

    just use the stud space.

    if you have space you could locate
    the grills over the door.

    if you have more than one supply grill
    in the master suite, you may need to
    increase size or add two sets of transfer grills

    see if solving the return air problem
    makes the tstat issues better.

    best of luck.