Radiant floor heat design

11 years ago

So I know this is a job best left to the pros, but I am on a very tight budget. I am an extreme handy man, I do everything, and most of the time I do it better than the specialist, albeit a bit slower. I have never messed with HVAC other than minor repairs. So I'm about to remodel a small 850 sq ft house I just bought, so I can accommodate my family of 5. It will then be 1280 sq ft. Right now it has 2 propane floor furnaces, but I have a toddler and using these will be a pain and safety hazard.

So I think I have decided on hydronic floor heat via propane tankless hwh. I have countless hours into research, but mostly I have found lots of conflicting info. It seems this is not an exact science yet. I do know that I just want it on one zone( I think), but it will have multiple loops. I'm planning on 8 inch pipe spacing, I think with four equal size loops about 450 feet each. But I may need more as some sites say you shouldn't exceed 300 feet per loop, but others have said you can go to 6 or 700. The only real difference in any of the rooms is the bedrooms will be carpet, living room wood, and baths tile. There is no real difference in heat loss for the rooms. I know that the r-value of the carpet will be about twice that of the wood. And I don't mind at all the bedrooms being a few degrees cooler.

The house is pretty well built and insulated now, and I will be making improvements as well, and have calculated my projected heat loss at around 22,500btu. At least thats what the one, very complex calculator I used told me. So that puts me at 17.5 btu/sq ft. From here I've followed directions on a few different sites, and got different results on what I would need. Some even suggest not counting or heating under cabinets, tubs etc. Theres just lots of conflicting info out there, so I'm just looking for some info that might better help me design this myself.

Also any suggestions on what kind of pipe works best. I'm thinking it may depend on loop length as a thicker wall pipe may help spread the heat farther, but it may not matter. I was planning on using some sort of reflective barrier on or around the pipe, but not sure what to use on that either. My mind is kind of burnt out on this for the moment, and i'm sure I'm forgetting to add some details. Thanks for any help

Comments (4)

  • 11 years ago

    Are you in NC? Coastal or Boone? Location makes a difference. As an extreme handyman you need to design "middle of the road" and conservative on choices. Doing so gives you wider latitude when things don't go quite right. I would not exceed 300' with my loops. Your heat loss is very low. That makes it harder for a tankless to do this properly. Most tankless can modulate from say 10k-199k btu. At design condition, the coldest day of the year, you are at 22k btu. You will short cycle the bejeppers out of that tankless and it will never get off low fire, which will cause all kinds of problems. I've been out on hundreds of these to pin the tail on the donkey. If you go ahead with this, with a tankless make sure you buy from a manuf that will warrant that application. Some will not. They learned their lesson.

    If I was in your shoes I would put in a Rinnai EX22 and a Fujitsu Inverter heat pump. That is the combination I heat my home with. Very comfortable and very economical.

  • 11 years ago

    Yes I am in NC, sw of asheville. Within a few degrees of boone's temps, but not quite as cold. Electric rates are high here so I am trying to stay away from that. I will be using the tankless for my dhw. The unit will be located in the garage, and the manifold about 20' away under the house. I was wanting to put a radiator in the garage on the return line to dissipate remaining heat and keep the system from freezing. I'm not sure if I should include that on my calculations. I also know I need ( I think its called) a buffer tank to help my short cycles, and was thinking I could use a 36 gallon pressure tank for dual purpose, buffer/expansion. Although I'm on a very tight budget. I want things done right, so I will get a proper heater rated for this use.

  • 11 years ago

    You are not getting much action here. There are lots of hydronics enthusiasts at heatinghelp.com and terry love's web site.

  • 11 years ago

    Thanks for the info. I am currently reading siggy's text book and will go from there