Greenspeed, is this setup ideal/ worth it?

11 years ago

I am building up on my house (cape style) in Long Island New York, will be approx 2200 sq ft, new upstairs to code, R30 attic, R15 walls. Downstairs is not being touched, except for new windows, and opening up of (old) bedrooms to make dining room / open floor plan. I currently have an old oil boiler with hydronic / radiator heat (under one window in each room) I need a new AC to support the house and was leaning towards and quote for a 4ton greenspeed. This would cool both floors, and heat both floors, I am not planning on running the radiant heat to the second floor only using the greenspeed. The first floor will retain most of the radiators (the rooms being opened will have theirs removed) Oil boiler will continue to exist for those radiators, but may thermostat may stay off if greenspeed works well, it also does DHW for now. I am also having a hot water coil run up to the handler to be "backup" to the greenspeed.


So browsing the forum it looks as though the greenspeed by itself should sufficiently heat my house, and I am under the impression that if it gets really cold (which it has been this february) the hot water coil will provide all necessary heat.


I guess I am looking for confirmation that this is a good setup, and that I do not need to run baseboard to the new second floor. Also the air handler is going in the new attic, which is not part of the building envelope.


Also I am a little concerned with the noise, has this been tamed, or should i ask / check for anything specific that will help quiet the unit?

Comments (15)

  • 11 years ago

    R30 in attic and R15 in walls not enough.

    If hot water coil fuel is oil, you should do a fuel comparison between cost of oil versus electric strip backup. I will assume boiler is 80% efficiency or perhaps lower. Do you know for certain?

    Where is ductwork going to be located for downstairs and upstairs zone.

    Yes you should ask about the condenser noise in heating mode at low temps.

    IMO

  • 11 years ago

    This is a good set up if you don't have access to natural gas. Electric rates on Long Island are among the highest in the country so it makes sense to spend the extra money on a Greenspeed heat pump. You will save a good amount of money on oil. The heat pump should take care of most the heating needs.

    You should have a load calculation done. The heat pump needs to be sized for the cooling load. An over sized AC in the summer will waste energy and not do a good job of lowering humidity.

    The contractor can install a muffler which will help lower the noise of the outside unit. This has to be done correctly on site.

    Are you going to run the duct work from the attic down to the first floor ceiling? It is not ideal for heating. Running the duct work in the attic is not ideal either. The duct work should be insulated as much as possible and well sealed. R30 in the attic is OK, but more would be better. R15 for the wall is the best you are going to achieve with 2X4 construction. The 2X6 construction would be nice but it is a significant extra expense. It may be difficult given the construction of the first floor.

  • 11 years ago
    last modified: 11 years ago

    Where in Long Island are you located? I'm in Northeastern Queens
    right near the Nassau border. Last May, I replaced the 1st, 2nd and attic
    windows and also installed a Greenspeed 4-ton with the 005 air-handler for my 2100sqft
    home. The Greenspeed has been slightly better than my greatest
    expectations.

    Not to say the experience has been perfect, but the few snags are
    more related to forced air vs. radiated heat and poor 1st floor insulation. This
    May I will be redoing the downstairs insulation and adding two more returns,
    which should solve the remaining distribution problem.

    My recommendation is
    to read the installation manual and quiz your contractor. I only found two
    contractors truly experienced enough with these heatpumps to pass with flying
    colors. My installer was absolutely 110% great. He wasn't the overall cheapest
    quote, but the extra money was well worth the attention to detail.

    You definitely want
    to follow specs: ensure your ductwork is drum-tight, capable of 1400cfm and have the muffler installed. They also installed the Diversitech
    heatpump pad. It may seem like overkill, but my unit only tends to get loudish
    at temps below 12F running 100% and 6500-7000rpm. This has happened only around
    5 nights during this unusually cold winter. Adjusting the compressor fanspeed
    down to 5700-6000rpm pretty much eliminates the noise.

    http://www.diversitech.com/Product-Line?id=a0jC0000005QcwxIAC

    And for adequate heating capacity, you want to size for the heating
    load and then upsize a ton. Otherwise, the miniscule summer savings will be way offset by the winter cold. Even with a few 0-7F nightly lows, I have yet to need my gas boiler backup.

    I have ConEdison with current pricing at .25
    a kwh. During the weekdays, I have the temperature set running for 12 hours at
    60F and the remainder at 70F. I’m only running this high to ensure my pipes
    don’t freeze during this unusually cold snap.... my usual setpoint is 57F at night and 67F during the day.

    To give an example of operational costs,
    which are well below last year's numbers...

    ____________high/low
    temp__mean temp__cost in $

    Saturday 21st____32F/14F_______23F______$6.51

    Sunday 22nd____42F/31F_______37F______$9.87

    Monday 23rd____38F/5F_______20F______$14.55

    So far, the highest daily cost to run it was $18.10 for a 10F mean temperature day. I'd approximate the winter savings have been around 40-45% with gas prices hovering around $3.50 a therm.

  • 11 years ago
    Boiler is from 1987. Well maintained, probably not efficient. R15 is all I can do in 2x4, cost of 2x6 and thicker insulation is tough to justify, and brings me over budget, would need to cut something then. I understand r30 isn't the best for attic floor, but I figure it will probably be cheaper add more bats myself if needed I the future.

    Blower in attic, ducts in attic and other ducts should be between the 1st and second floor, all ceiling vents. What's worse floor vents for cool air or ceiling hot vents?.Again out of budget to spray foam attic sealing and do air tight second floor. Running unit in basement up is probably more in labor and will take away space for returns, trunk.

    Hot water coil will be separate zone controlled by infinity system. Gas is in street, but that's around 10k to switch. I can switch in the future and run a small combo boiler, to keep the water could use full. And if the radiators prove to be not needed I can cut them out of the other rooms as I renovate and update in the future.

    I will have load calc done once plans are signed off on. I am wondering what would everyone do for their own home, given I can't spend much more on construction, but have around 15-17k for hvac.
  • 11 years ago
    last modified: 11 years ago

    Bsmith, what is loudish? If the unit is on side of the house, and bedrooms are upstairs, is it bad for bedrooms on that side, and not really noticeable on the other side? That diversitech pad looks neat. I am curious why would it cost more to run on Sunday, when the mean temp was warmer than Saturday?

    I used to have an in wall A/C (2009) that if left to cycle on and off to keep temperature would wake me at night (it was in my room) I had a 3 ton infinity to cool my house before, when the blower went to full speed it wasn't really bothersome, but the outdoor was always silent.

    South nassau, electric bill is about $.20 /kwh.

    The thought process that go me here was, I needed new AC, and its probably 2k extra to make it a greenspeed HP (vs infinty A/C only) and it would cost me around 5k to extend a new zone and run all new baseboard upstairs. So cheaper upfront cost. Although Oil is cheaper now (its still higher than it was 5 years ago) I dont think it will stay this low, and reducing the amount of oil I use would, hopefully, save money vs the increased electric. Then in future I can switch to gas, and just use an on demand unit, for the hot water coil, assuming i no longer need the left over radiant on the first floor, which is quiet drafty currently, hopefully most of the draft will be alleviated with the construction (new siding, windows). I will have an Energy Audit after everything is done as well. Again I am trying to use foresight, and ask what others would do, so next year I'm not regretting my decision :)

    Everyone - Thanks for the help and advice.

  • 11 years ago

    Out of curiosity, did you have any air purifier or humidifier or any other accessory installed?

  • 11 years ago
    last modified: 11 years ago

    I don't have a humidifier, but am considering one. The humidity has hovered around 23-30% all winter. Otherwise forced air without any additional humidification is actually manageable compared to at times brutal radiated heat.

    I do have an air purifier. I wanted an Aprilaire 5000, but the contractor convinced me to get the Carrier Infinity so it would be seamlessly integrated into the system both digitally and positionally. The Carrier is virtually equivalent to the Aprilaire with overall slightly diminished filtering capacity. So far it's been excellent.

  • 11 years ago

    Think again about the insulation issue. Insulation is cheaper than a heat pump.


  • 11 years ago
    last modified: 11 years ago

    True. Although adding insulation isn't always easy or cost effective. My house is double bricked but with a layer of mesh, wood slats and plaster on the first floor. The temp differential in the winter can sometimes run 7-10F from the second floor. Although I do highly recommend DIY blown-in cellulose for efficiency, cost, ease of insulation and safety.

  • 11 years ago

    How much difference would insulation make? First floor isn't being gutted, so 2x4 existing with what ever insulation had been there, except for 2 walls that are coming down and we'll be getting r15. Upstairs is new construction, planned 2*4 and r15.. I could do 2*6 with r21 for about 2 grand more, but that is batts. Other than ny energy code there will be no spray foam or crazy air sealing. Attic is 2*8 so r30 doesn't even fit . assuming I can always lay my attic insulation but can't change to 2*6 upstairs is that 2k worth it, how much would I save over r15 energy wise.


    The heat pump comes in because I need central air for entire house. I also need heating for second floor, so the nominal price to change to the hp from the infinity a.c seems better then running baseboard to second floor. It is cheaper, and would cut down on oil use as explained above. It also allows for a whole house humidifier and air purifier of desired. House is very dry.


    Does anyone have approx cost for other insulation choices?

  • 11 years ago

    Huge difference. For a real world example, think of a basic plastic or Styrofoam cup vs. a thermos. And it's not just the cold, but also the amount of draft from the outside. The more you can keep draft and temp from the outside the better.

    DIY radiant barrier is another great heat saver on the cheap, although proper installation is the key. https://www.youtube.com/user/AtticFoil

  • 11 years ago

    David,

    You are asking the questions I always ask. Adding more insulation is a good thing. How much money will it save during the time you live is this house is difficult to answer.

    If I had to guess I would say it is less than 5% of your energy costs. So if you spend $1000 a year on energy costs, the savings would be $50 per year. It would take 40 years to recover the $2000. Even at a 10% savings it would take 20 years. If the cost were $2000 per year (this seems high for a Greenspeed with your size house) you would be down to 10 years.

    You could come up with an estimate of how much your new heating and cooling system will cost to run each year, then you could plug in various insulation values into the load calculation to determine the change in losses. From there you could calculate the change in costs at today's energy prices. It would be an interesting calculation if you are up for it.

    I would invest the $2000 into either better windows or an SP500 index fund. :)


  • 11 years ago

    For what its worth, the windows i am getting will be Anderson 400 series, going above that seemed to be much more expensive and goes back with will I see a ROI in my life. +1 to index funds!

  • 11 years ago

    I'm in southern Nassau county as well. Had geothermal installed October 2013, then got schooled on the importance of airsealing/insulating. Last summer I replaced the interior masonite door to attached garage with a steel exterior door, used a dozen cans of spray foam all over the place, airsealed my rim joists and replaced the mussed up insulation (some original stuff was only 1" thick!) in HALF my attic with R49 batts total. Just ran electric consumption comparison last night - I'm $1K ahead of last year. Still have the other half of the attic to go, as well as the attic access door.

    The windows should be a big help, but I would want to make sure they're sealed up well all around,