27" hood mandatory or not?

11 years ago
last modified: 11 years ago

There is a lot of great information on GW and also some conflicting.

We will have a 6 burner rangetop (capital cgrt366).

I've spoken to capital and they suggest their 36" hood. But from what I've read here it's advised to go to 42". Capital does not have a 42".

So, I've called vent a hood to determine what they suggest. They feel a 3 blower unit is the right option. And because it must be 30" higher than the range they do not suggest it be deeper than 24". Again, what I've read here suggests a 27" would be a better option.

I've been through the btu to cfm requirements - now I need advice on the dimensions.

Is 27" deep a must have?

Comments (14)

  • 11 years ago
    last modified: 11 years ago

    I guess what VAH meant was no less than 24". They have the 27" version at the same price. Some people may avoid 27 only because of the bumping into head issue. In my case, 27" deep @ 29" (it could not go higher due to duct clearance, but VAH told me the height was ok) just clears my head, so no problem at all. Just go for 27".

  • 11 years ago

    So, if I'm not too high (30") does 24" cut it or should I get 27" deep?


    The VAH rep was very concerned with us bumping our heads. She commented that the front 2-3 inches of the range are a lip before the element starts - so a 24" deep would be over the elements.


  • 11 years ago

    I have the same range top. It is pretty much 27" deep itself. Just do a simple math and/or drawing to see where your head will be to the hood and if you are gonna bump your head or not. When you cook, you stand couples of inch away from the front edge of the range top. So when you lean over to the range top (i.e. when bumping may happen), your actual height will be lower. Select one with round front edge (e.g. NEPTH18) may help even if your head does bump to the hood.


    If you are not high (but you said 30", can't be), e.g. your height is about at, or even slight higher than where the hood is mount (lower edge, ~ 66 inch), I would say there is no bumping issue.

  • 11 years ago

    I'm going to be buying the same rangetop. what cfm range are you planning on?



  • 11 years ago

    Eshmh - which fan do you have? How tall are the users in your kitchen?


    Golf - we are looking at a 3 blower system. Anything above 2 blowers you've got to go to at least 42" (with VAH). We looked at Broan but noise was a concern. Another option is Wolf - not sure what they $$ but I think it will be more than VAH.

  • 11 years ago

    I have the NEPTH18 series mentioned above. 42" x 27", 900 CFM. All heads are around at the lower edge of the hood, give or take.

  • 11 years ago
    last modified: 11 years ago

    I've got the two blower VAH, 36"W, 24"D, 30"H. It's the bare minimum. I have a 36" BS range top. While I would have preferred to go with the bigger arrangement, it will work for me. I don't think I can remember ever using all six burners at the same time. I don't plan to in the future. It was already installed and I didn't want to replace it.

    If I were building from scratch, I would select the 42", 24"D, 30"H with the three blowers. The 30"H arrangement with any hood will bother anyone taller than 5'5". My husband is always hitting his head on it and cussing. I really don't think you need a 27"D hood.

    BTW, I love the VAH. It works. There are videos on line that show you how to clean it. Easy after the first time.

  • 11 years ago
    last modified: 11 years ago

    Huh, since bumping head also happens on 24D, why not just go with 27D? It would not make much difference in this category anyway. :-) The fume does not go straight vertically up, 27D captures the part of fume that would roll over 24D's front better, same idea as 42W over 36W. I would not say 27D is a must have. I think 27D @ 30 is good for a chef is either not so tall (< 5' 7" with round profile) or too tall (probably if can see the hood front straight ahead). :-D

  • 11 years ago

    You should be able to put a 27 x 42 with 900 cfm at whatever reasonable height you need for head clearance, such as, say, 33 inches up. If the duct cover intersects the ceiling, either cut the cover or embed it into the ceiling and patch the sheet rock around it, or use a molding.

    kas


  • 11 years ago

    eshmh - what MUA set up do you have? did you get it locally?


  • 11 years ago
    last modified: 11 years ago

    Builder put it in. It is one of these http://www.thermolec.com/en/productView.aspx?type=product&id=77 + a damper controlled by the current going through the hood. When hood is turned on, damper opens, then if the heater senses the air flow, it is activated and tries to heat the incoming air to 15C. I believe the heater is 4 - 5KW. Not sure if it is powerful enough to do the job to the setting, but I don't want a 10,000KW+ unit in the house. :-) I believe there is dedicated MUA models on the market.

  • 11 years ago
    last modified: 11 years ago

    eshmh, did you add on or build new? I thought that because new homes are "sealed" that a MUA is required. Particularly for high cfm hoods.


  • 11 years ago
    last modified: 11 years ago

    It is a new home. It is supposed to be pretty air tight if the builder didn't mess it up. :-) It is required by the builder if the hood is anything higher than 300 CFM. Otherwise, they won't do any work related to hood.