We are getting ready to sign a contract to start construction on a new home. This home will have a 2300 sq ft first floor and 2300 sq ft basement with a 500 sq ft bonus room. We are trying to decide which HVAC system/guy to use. I feel comfortable that both installers would do a good job, and that is what I understand is the most important, but I'm not sure which system to pick. We have decided to use natural gas instead of geothermal. Both have done load calculations. Both will have 3 zones (1st floor, basement, bonus room).


Carrier ($17,550):

17 SEER 4 ton, 2 stage A/C 24ACB748A003

97% efficient, 2 stage furnace 59TP5A100E2120 (100,000BTU)

4 ton cooling coil, CNPVP4821ALA


Ruud ($16,282.35):

18 SEER 4 ton, 2 stage A/C UASL048JEC

96% efficient, 2 stage furnace U96VA1152524MSA (115,000BTU)

4 ton cooling coil, RCF4824STAMCA

The Ruud installer says this unit will be 17SEER (I'm guessing due to what it is paired with??)


Which system would you pick and why? Any questions that I should be asking either installer?

Thanks for your help.




Comments (10)

  • 11 years ago

    Did either contractor do a load calculation? Where is the house located?

    One contractor says you need a 100K BTU furnace, while the other says 115K BTU. One of these guys is wrong, and my gut tells me they are both wrong.

    New construction with typical windows and insulation at 2800 sq. ft. should be able to be heated with a 80K BTU furnace. If it is a very cold climate you may need 100K, but I am doubtful.

    It is hard to say if the 4 ton AC is the right size. It sounds like you have a small second floor which means a lot of roof exposure on the first floor.

    New construction must have a load calculation since there is no history of HVAC for the house. No calculation usually means over sized equipment. If these contractors will not do a calculation, then keep looking.

    Your quote should also specify the thermostat and type of filter. I recommend a 4 inch media filter.

  • 11 years ago

    Both said they did a load calculation. The house is located in Southern Indiana (zone 4).

    The entire first floor will have roof exposure since the second floor is all above the garage. We will also have a basement with a walkout along the entire south side of the house.

    Both systems say Honeywell 2 stage digital programmable thermostats.

    Ruud system specifies 5" air filter. Carrier estimate does not specify filter (I'll ask).

  • 11 years ago

    Are you sure you are in zone 4? I thought southern Indiana is in Zone 6. The winter design temperature is 5-9 degrees F depending where you are.

    You should are the load calculation and see if it makes sense to you. Check the indoor and outdoor design temperatures.

    Get the model number of the thermostats. There are many Honeywell models. You want to make sure it is a true 2-stage model. You should get a model that has the cool to dehumidify feature.

    I like the Carrier equipment. I am not very familiar with the Rudd quoted. Perhaps someone else can comment. Do these prices include the duct work? If not the prices seem high.

    I would be concerned about making the bonus room it's own zone. Even on the low stage the heating and cooling may be too much for a 500 sq. foot room. Ask the contractors how they will handle that situation.

  • 11 years ago

    I don't know a lot about climate zones, but from what I've found online, Southern Indiana is in zone 4 when dealing with insulation/energy types of issues, but zone 6 for plant hardiness. I always figured when people talk on the HVAC forum that they are referring to energy zones (not plants).

    I'll have to get a copy of the load calculations from each guy and have them explained to me.

    For the thermostats, neither gave me a model number but both quotes say 2 stage. I'll get the model numbers and check to make sure they include cool to dehumidify.

    Both of these quotes include duct work. This is a new construction home so the units, zoning equipment, duct work, and thermostats are all included in the quotes.

    Like I said, I don't know much about HVAC, but both of these contractors as well as two others all suggested making the bonus room a zone of it's own. I know that the Carrier guy said that the dampers for the zoning will open and close partially when needed, instead of either being all open or closed (maybe all zoning is like this, I just don't know). Would this help with the small size of that zone?


  • 11 years ago

    I would want the 59TN6 or 59TP6 furnace for the var speed blower. Carrier price includes zoning controls and necessary ductwork modifications? What thermostat? Filter cabinet included? New refrigerant lineset? Basement is finished and below grade? Without more info, I can't believe you need a 100 K furnace.

    IMO

  • 11 years ago

    I have a small vegetable garden so my mind is calibrated to hardiness zones. Now I realize there is a second set of zones for HVAC.

    Carrier zoning equipment is supposed to be the best, so I would lean in that direction. Be aware that many contractors are not very good a zoning. It takes some planning and calculations when you have multiple zones. The fact dampers can be partially opened will help relieve the static pressure. This mean quieter operation and less stress on the blower motor.

    Making the bonus room its own zone is a good idea. You just want to make sure it is going to work well.

  • 11 years ago

    tigerdunes,

    What is the difference between the 59TP5 that was in my estimate and the 59TP6? What I'm finding on the Carrier site shows that both are 2 stage, up to 96.7 efficient furnaces. The difference I'm seeing is that the TP5 says multi-speed ECM blower motor while the TP6 shows variable speed ECM blower motor. What is the difference between multi-speed and variable speed? Are there other differences?

    I still have to figure out which thermostat is included (all my estimate says is Honeywell 2 stage programmable thermostats). I also need to figure out what filter is included with the Carrier.

    Cabinet, refrigerant lines, duct work, zoning hardware are all included (this is a new build).

    Basement will not be finished at first, but we hope to be able to finish it within a few years. Basement will be 2300 sq ft also and will be about 2/3 below grade. The south side of the basement will be walkout and the west side will be sloped.

  • 11 years ago

    mike and tiger,

    Thank you both for your help.

    I just talked to the Carrier contractor. He said that he would switch to the 59TP6 for no additional cost. The zoning equipment priced is the Carrier equipment. 5" filter.

    The thermostats are Honeywell 6000 Series. He said that these do not control humidity. He said for an extra $850, we could upgrade all 3 thermostats to the Carrier COR Thermostat, which he said is Wi-Fi enabled and has additional options over the Honeywell. I am not interested in wi-fi options (all I want is a comfortable house). He acted like he wouldn't spend the extra $850 if the only option on that thermostat we wanted was the ability to cool to dehumidify. What other options should I look into?

  • 11 years ago

    What zoning control? Be specific with brand and model. I would want to see load calc in writing. With zoning, I don't want HVAC oversized. Now to thermostats. Does zoning control handle dehumidify on demand or does each thermostat? You need to find out. I would want that feature.

    IMO

  • 11 years ago

    Zoning equipment is Carrier, but I'll have to find out what brand and model controls it. I will ask to see the load calc. The thermostats priced do not handle dehumidify on demand. The upgrade to three Carrier COR thermostats is $850, which I don't really want to spend. I don't wi-fi thermostats. Are there specific thermostats I should ask about?

    Also, anybody have an opinion on the RUUD equipment, or should I only be looking at the Carrier?

0