This is my first time using this forum, so sorry if this isn't the right place. This is going to be a wall of text, so feel free to skip to the quotes (or ignore me, hah).

I purchased my home a year and a half ago, knowing that the HVAC goodies were on their last legs. They are two 10 SEER 2 ton Rheems original from '96, and I'm not actually sure what my furnaces are (also two, in the attic and a much less important issue for my location). I was able to struggle through the summer in order to hopefully get a slightly better deal in this season.

Just got my most recent quote from a company, and tossed out 4 others. I'm now comparing two (the new one and an older one that I hope to negotiate on since it's not the middle of the summer now). My main problem is that they are two very different quotes and I'm not sure how to compare them or decide what would be best for my situation.

For reference, my attic is a limiting factor because of clearance. I believe a Carrier product would fit, but not something like a standard Trane. I have a two story, 1900 sq ft home that is cooled just fine by what I'm currently working with.

Quote #1 is from the middle of summer and the engineer that came out was the most professional of any of the 6+ I've had take a look at my setup. His quote includes re-engineering my attic furnaces. Quote #2 is from a week ago and more of a one to one replacement, albeit at a higher cost (more equipment). I'd be fine going with option #1 if I could be sure that I'm not losing capability or setting myself up for future headache. Anyway, here are the gists of my quotes:


Quote #1 - "I’m recommending removing both systems in the attic and installing one larger Trane complete two stage machine with Trane zoning. System will need to be designed horizontally for proper engineering."

  • Trane XC 80% afue 80,000 BTU two stage, variable speed gas furnace with a energy saver
  • ECM D/C drive blower and the Trane 3 ton XR17 TWO STAGE high efficiency R410a Puron air conditioner
  • Trane all aluminum cooling coil.
  • Engineer system for horizontal application
  • Secondary drain pan and emergency water solenoid cut-off switch for flood protection
  • Install new custom fabricated externally insulated metal supply and return plenums
  • High Efficiency AprilAire MERV-13 media air cleaner system. I recommend minimum MERV 13 (minimum
  • efficiency reporting value)
  • Integrated Trane (2) zone control system to isolate independently by thermostatic controls: Includes Zone panel, motorized control dampers, freeze protection device, low voltage transformer, 2 WIFI enabled thermostats, Trane's top of the line Comfortlnk series XL950.
  • 48 months interest free financing
  • WARRANTY: 10 YEARS PARTS & LABOR ON ALL COMPONENTS, 10 years on compressor and coils and lifetime on heat exchanger.
  • COST: $12,336 (with financing instead of the possible rebates)


Quote #2 - "Installation of Two new Carrier Performance 16 SEER 2 Ton Complete Systems.Systems include all New High Velocity supply Grills Seal all boots to sheetrock u/s and all new plenums. Extend Drains pass units outside and install cement blocks under units so they are not upstructed by tree roots. Also Merv 13 Aprilaire air cleaners."

  • Carrier 24ACC624A003 Performance Series 16 SEER
  • Carrier CNPVP3014ALA Evaporator Coil
  • Carrier 58CTW045---1--12 Performance Series 80% afue Gas Furnace Two Stage
  • Carrier TP-WEM01 Performance Series Thermostat
  • New duct covers on all ducts
  • Attic hatch seal cover
  • 36 months interest free financing
  • Warranty: Lifetime Workmanship Guarantee
  • 20 Year Heat Exchanger
  • 10 Year Parts
  • 10 Year Compressor
  • 5 Year Parts on Tstat
  • 2 Year Labor
  • COMPLETE ZONE WARRANTY: ZONE HOME SOLUTIONS WILL PROVIDE A 10 YEAR LABOR WARRANTY AS LONG MAINTENANCE AGREEMENT IS ACTIVE AND DOES NOT LAPSE THROUGH ZONE HOME SOLUTIONS HVAC DIVISION. DOES NOT INCLUDE DIAGNOSTIC FEES.
  • COST: $14,199 (with financing instead of the possible rebates)


As I stated, I'm hoping I can shave some off of Quote #1 since it's a different season. If I'm able to do that, it makes my decision a bit more difficult. Any insight would be greatly appreciated. This is the Atlanta/Alpharetta GA area by the way. I'm sure pricing is different all over the country.


Thanks!

Comments (8)

  • 10 years ago

    Brands here are equal so that shouldn't sway the decision. Ask #1 to quote two systems and #2 to quote with new metal ducts and your decision should be easier. I have hunch the cost of maintenance agreement in #2 will more than make up any difference in cost.

  • PRO
    10 years ago

    You need to find out if the zone system being quoted includes a bypass and what type it is.

    If it doesn't include a bypass, not a good thing. Usually they increase the size of the ducts to pull this off. During hot summer days this can cause lack of capacity problems. 'lack of air velocity' when both zones call.

    If it includes a bypass and the bypass is 'barometric bypass'. It's a duct damper with a weighted arm on it, position sensitive and guaranteed not to work very good.

    bypass included and it's a 'modulating bypass'. This is the better of the two, but sizing and design of the zone system is critical.

    Additionally the dampers that control air flow to the zones -- are they 'spring open' or 'spring close'. If they are take a pass. The better of the dampers are 'power open and power close' (no springs)

    The Trane equipment sounds undersized compared to what you originally have in the home. 2 ton + 2 ton = 4 ton not 3.

    Additionally a down side to the Trane option is that this system is not a communicating system.

    A two stage communicating system will do a much better job because the thermostat communicates with the indoor and outdoor equipment.

    Amana and Goodman both have these options available with a better warranty to boot.

    The communicating zone system is doable, you can set up the zone system with both communicating stats or just one on the proper zone to control the system via communication protocol. This type of set up is NEW, the communicating zone system just became available this year. So you may have trouble finding exactly what you want in this arena. But this would be the better choice. (better comfort / better warranty protection)

    Cody thanked Austin Air Companie
  • 10 years ago

    Thanks for the input guys. I'll probably try to find any remaining reputable HVAC companies in the area and get another two system quote WITH a load calculation. Does my Quote #2 seem like a fair deal for the equipment provided? At the very least the engineer (owner of the company) seemed to care about providing a quality service. I immediately tossed two or three quotes because they just came in, took a peek and tossed out a number.


    Austin Air Companie,

    There was another portion on the quote that I left off. Here is the full text:

    "Integrated Trane (2) zone control system to isolate independently by thermostatic controls: Includes Zone panel, motorized control dampers, freeze protection device, low voltage transformer, 2 WIFI enabled thermostats, Trane's top of the line Comfortlnk series XL950. OPTION: EWC 2 zoned system with bypass damper and sensor. I DO NOT recommend this option. It requires the use of a bypass damper to bypass airflow back to the return plenum when 1 or more zones are not calling. It's an economical way of zoning. Also, bypassing the cold air can confuse the TXV (thermal expansion valve) resulting in loss of humidity control."

    That second "option" reduces the quoted price by ~$1000.


    Thanks guys!

  • 10 years ago

    Cody,

    Try getting some quotes from bigbox guys. In NJ, they use reputable contractors. Off so many (more than half dozen) HVAC contractors I had for quotation, only one guy did a proper manual J calculation. The folks who ballparked it, were close. Point to be taken- while manual J calculation is something desired, most will not do it.

    Aside that, why you are picking up a 80% AFUE furnace? Cost difference is minimal and on a longer run, I am not seeing energy price to go downhill.

    I don't like combining the two system into one; the installation and upkeep seems too complex. With two independent systems, you can fall back on one while the other one needs attention.

  • 10 years ago
    last modified: 10 years ago

    The zoning and dampering sounds complex to keep it operating correctly for the merged system. The problem is that a system needs a minimum air flow to operate and if it is cut in half it might have issues. Probably better to keep it separate. I believe in good air quality but some of the electronic media filters emit some ozone. Check if they are installing an electronic or a non-electric.

    https://www.arb.ca.gov/research/indoor/cr-12-2007.pdf

    Plenty of non-electric media filters out there.

    https://www.alpinehomeair.com/viewcategory.cfm?categoryID=403

    Otherwise concerning air flow, the large 6" filters are not very restrictive. So you shouldn't be afraid to get those types of filters.

  • 10 years ago

    I agree with Vth. My thinking is try to keep it simple even if you have to spend a little more money. Most HVAC contractors are not good at zoning. The one who proposed zoning may be good, but it is still a compromise over what you have now.

  • PRO
    10 years ago
    last modified: 10 years ago

    @ Cody,

    Motorized control dampers doesn't specify which type, for that reason I would almost suspect a 'spring' open or close type damper. (these are still motorized but one sided 'either power open or power close' but not both. In other words if the damper is 'power open' it would be spring close and vice versa. A power open AND power close damper is a better more efficient motor.

    Bypass takes a lot of heat from contractors that don't know, or care to know what they are doing. A zone system is 'a lot of work' behind the scenes in prep work and then going into structure and actually doing it. If there is a team doing this the challenge is even greater because many times the design may fall on those doing the work. Lack of communication or know how and you're not going to have anything you want. (nothing but problems)

    The problem is that if you omit the bypass, the system is no where near as effective under all scenarios and could reduce efficiency and may even cause problems more so than it attempts to eliminate.

    I have a zone system in my current home and I am in the process of installing a zone system at my new home that I am moving to soon. (I am the one actually doing the work so I have very intimate knowledge of zoning systems.)

    I also did a zone project a year ago for a 3 level home in which there was no 'bypass' installed. How they got around this issue was to 'over size' the duct work. (There has to be some where the air can go when only 1 zone is calling.)

    What happened was that during hot times the upper level (3rd floor) would not get cool enough. The cure was to rip out the existing zone system and add zones for better control and install a 'powered' bypass. (replacing the duct work is not an option in a 3 level home easier to just tear it down and start over.)

    So with this home the problem still exists, but only when all zones are calling at the same time and it's hot outside. Which really isn't a problem because when people sleep the main part of the house that damper closes down and supplies the bedrooms, when people wake up the bedrooms damper down and the supply goes to the main house.

    If you have a properly sized duct system along with correct bypass, the difference is 'night to day'. I know because I feel the comfort and the efficiency of this type of system in my own home.

    The problem is finding someone who 'knows' as opposed to someone who just offers something from a competitive standpoint trying to sell it to you that way.

    'Bypassing air confuses the TXV resulting in a loss of humidity control': This means I have no idea what I am doing. (It's complete nonsense.)