Goodman unit

10 years ago

I need some guidance desperately. I had a new 3 ton Goodman AC/heat pump installed a few months ago. This was replacing a unit that I believe was the same specs. The unit has 5kw heat strip kit which is exactly the same as my previous unit.
I recently had an electrician over to repair a switch. I've had knee surgery and I'm currently out of work. He offered to take a look at my panel while he was here to ensure everything was above board. Suddenly (although I've had no problems) I need an overhaul of my panel.

Please advise: House is about 1250 sq ft. Appliance load includes electric stove/oven, electric washer/dryer, 3 ton AC/heat pump with 5kw aux heat, electric water heater, refrigerator, chest freezer, microwave....
Circuit panel includes main breaker, double 50, 2 double 30s, and multiple single 20s.
As far as I know, the range is wired to the 50, dryer on 30, and AC unit is on 30. The water heater is very small and is 120v which allows it to be wired on single 20.
This electrician insists there is no way a three ton unit and heat strips can be covered under a 30amp breaker.

Advice? I'm not working right now and I don't have money to waste on getting people out here when it's really not necessary. I've been here 8 years and never even tripped a breaker. That said, I also don't have money to replace everything I own if my house goes up in flames. Honesty appreciated. Many thanks.

Comments (7)

  • 10 years ago

    It is preferred that outside HP condenser , air handler, and heat strips are on separate circuits. What size are the circuits each of these components are connected and what is the electric draw?

    5 KW heat strip is small. What is your location?

    IMO

  • 10 years ago

    I'm in South Carolina. We rarely get below freezing--even in the dead of winter. I don't know anything about the electric draw or the wiring. I just know the installers didn't ask any questions regarding the wiring. I'm assuming this is because it was replacing an identical unit and there were no issues,

    I assume everything is connected to the double pole 30 amp breaker simply because the single pole 20 amp breakers would only be suitable for 120V, correct?

  • 10 years ago

    Obviously a 5 KW heat strip will not temper the air on a defrost call much less handle heat demand on emergency heat...

    Can not help you on your concerns without your help on answering my questions...

    Good Luck!

    IMO

  • 10 years ago

    I can't see the box for my self so there's no way I can say anything for certain but here's facts that should set your mind at ease. Fires don't start from under size breakers. Fires are caused by breakers that are over sized for wire. If your hvac is served by #10 or larger wire,the 30 amp breaker will trip when and if load exceed's circuit capacity. Under those conditions,the breaker can trip,be reset only to trip again two weeks later without presenting a fire hazard.. Any time an electrician inspect's a breaker panel,it's incumbent he make certain no wire is under size. Now my opinion. Sound's like he needed to find some work. I wouldn't give it another thought.

  • 10 years ago
    last modified: 10 years ago

    What the electrician probably is noting is that the heat strips and heat pump need their own separate double pole breakers and I would have to guess your panel is out of space and it is also probably over crowded. You could look at tandem breakers for the single 20s as an option. Considering the heat strips are rarely used, not likely you would need to increase service main.

    It is overall a better option to replace the panel (don't know how old it is) and get one with more spaces, but that may not be totally necessary. Your current panel will be on the crowded side with tandem breakers and being totally full on top of it, which is another reason to replace with a larger panel.

    An even more fun idea is a tandem double pole breaker, that confuses the heck out of a lot of people what the heck it is when they see it lol. (Either a double pole in the middle and two separate tandems on the outsides Example, or two double poles Example)

  • 10 years ago

    Thank you all. I went outside today to try and do a little recon. The sticker on the unit showed min amp 20.6, max amp 30. I also noticed a disconnect box and decided to open it. I always assumed the box would just include a switch and was surprised to see two breakers inside (a double pole 60 and a double pole 40). Does that change anything?

  • 10 years ago

    "Does that change anything?"

    Not really but if you intend to keep chaseing this rabbit I suggest hireing an electrician.