Outlet under the kitchen sink

8 years ago
Hello - need some help with this: we have a outlet under the kitchen sink that connects to the garbage disposal and a water purifier that we leave under the sink that connects to the filter that comes from a device we installed where the soap dispenser would be. There’s also a switch to the right of the sink that turns the garbage disposal on/off.

When we first moved in, we were able to install the water disposal with the plug under the sink and have the sink disposal running fine with the on/off switch.

A couple months ago, the fuse blew out along that side of the wall, and ever since then, we haven’t been able to plug in the water purifier to the outlet under the sink without having to turn on the sink disposal switch. So the only way that it’s been able to be on is if we have the sink disposal running at the same time.

We had a technician come by and say that it was impossible that we were able to install the water purifier under the sink using the outlet there without having the sink disposal switch on the entire time.

This doesn’t make sense because we definitely had the water purifier working under the sink without having the sink disposal switched on for months.

It also wouldn’t make sense because why would there be a switch for two outlets and it not being able to work without the sink disposal running the entire time? We had this same setup in our old townhouse, so we know it’s not just something that’s particular to our home.

Does anyone have any thoughts/suggestions/things we can tell the technician?

Comments (8)

  • 8 years ago
    last modified: 8 years ago

    When you say technician who are you talking about?

    You need an electrician to come check the wiring. It is most likely the outlet is running on the switch. Not sure why or how it would have worked before without looking at it.

  • 8 years ago

    There are two ways to use an outlet(duplex) for that use. One is to wire one plugin to the switch and the other hot all the time. That needs to be done during install, the wiring connections are a bit different.

    The other is how I did the same situation(dishwasher and disposer) in our current home.

    I plugged the dishwasher into the bottom socket and an air switch into the top socket. The disposer is plugged into the air switch plug adapter. There is a flexible plastic hose from the air switch adapter to a flush mounted plunge type button mounted in a hole in the sink. (Our sink is stainless and I had to drill another hole on the opposite side of the hand soap dispenser).

    The dishwasher is on all the time(when the controls are used) and the disposer is only on when the plunge button us pushed---once for On and a second time for Off.

    In your case, use the receptacle for the purifier and an air switch in the other socket for the disposer.



  • 8 years ago
    last modified: 8 years ago

    I've wired outlets so that one is hot constantly and the other is switched. If you were running this way before, then yours must be wired the same way.

    Did you by chance unplug the purifier when the fuse blew and then plug it back into the other receptacle?

    Swap the plugs and see if it goes back to the way it was.

    FWIW it's pretty easy (and not uncommon) to wire a dual outlet to have one switched and one hot all the time. For example, I do it for the bedroom light with a clock radio plugged onto the same outlet. (need continuous power to the clock but want to switch the light on/off).

    I'd question your technician's ability.


    FWIW, I was not familiar with an "air switch" so I googled it. Here's a link to one.
    Insinkerator air switch


    Pretty neat but if the OP already has a switch then why bother.

  • 8 years ago
    last modified: 8 years ago

    There is a linkage on the side of the outlets between the screws that if broken you can wire each outlet on a separate circuit. But if she swapped how they were plugged in, then the disposal would be on all the time when she plugged it in. I am not thinking we are dealing with that scenario.

    Still need the wiring and outlet looked at so we know what is actually going on.

  • 8 years ago

    Just confirming it is possible. My dishwasher and disposal use the same outlet.

  • 8 years ago

    Did someone change out the receptacle under the sink? Newer codes require that receptacle to be GFCI protected. If they installed a GFCI receptacle, it can not be split wired like it was before without adding another receptacle down there, or putting the GFCI in the breaker panel.

  • 8 years ago

    If the duplex receptacle had been wired with one position on all the time and the other switched, and the plugs were swapped, I'd expect that now the disposal would run all the time.

    Is it possible that the disposal actually has its own internal switch? That would explain things.

    In any case, I agree with the advice to try swapping the plugs before doing anything else.

    PS - you might want to consider posting this in the Wiring Forum.


  • 8 years ago

    You need an electrician.