Hello All,
I am having a new house buitl in Michigan. I went to the site today and noticed some issues that concern me. Please refere to the photos. The outside wall does not but firmly agaist the joist and you can see the nails exposed. The carpenter told me they pulled it outward so that the outside wall would not have a wave in it. I also noticed that the main supporting beam has quite a few pieces of of metal that are shimming it up. Is this acceptabble. A final note I would appreciate comment on is that the builder omitted two windows without consulting us. When I challanged him on it he said "oh, we don't put those in am=nymore because they look out on the neighbors and there have been complaints'.
Any thoughs are certiainly appreciuated....thank you,
Dave W




Comments (48)
- 7 years ago
Metal shims are fine under the steel girder and it looks like the cavity will be grouted with mortar.
2nd-3d picture the joist is a bit undercut, and it should be resting on the sill plate, if there is no sill plate and there is an opening, this is how we frame this ...we double-up rim joist over the opening and the joist attached with a hanger like this

4th picture they missed a joist when nailing the sub-floor but I'm sure there is a row of nails along side of it...Check to make sure its nailed, if not the sub-floor will be lose in that spot and should be nailed down. - 7 years ago
Looks pretty shoddy. The beam pocket needs to be closed [grouted with mortar], it took them a few shims to level but still ok. Missing nails: it should be re-nailed or re-screwed. But not just nailed... make sure that glue was applied. In the second picture joist looks pretty short.
WRB is a cr@p one ... it looks woven [3rd picture]. These are horrific.
Related Professionals
Bloomington Architects & Building Designers · Frederick Architects & Building Designers · Vicksburg Architects & Building Designers · Fayetteville Architects & Building Designers · Scottsbluff Architects & Building Designers · Palm Bay Design-Build Firms · Manhattan Design-Build Firms · New Haven Design-Build Firms · Aurora Design-Build Firms · Champaign Design-Build Firms · Anchorage Design-Build Firms · DeRidder Home Builders · Westminster Home Builders · Clarksville Home Builders · Eugene Home BuildersHU-262669657
Original Author7 years agoOK, thanks for the the response guys. I suppose it's not as bad as I was imagining. I was mainly concerned with the gap between the joist and the outside wall. But these are not the actual joist just the short spacers beween the joist (not sure what you call those).
BT-Im not sure what you meant when you said 'WRB is a cr@p one ... it looks woven [3rd picture]. These are horrific.' Can you please clarify?
Thanks again
DW- 7 years agolast modified: 7 years ago
Its not possible to be sure what a weather/air barrier is made of from a photo of the edge of it but the dangling threads are not a good sign. Take a photo of the face of the house so we can see the logo. Whatever it is, its a bit late to be questioning it but I've forced a contractor to replace the wrb when it didn't meet the contract spec. A lot depends on the nature of your contract.
The steel beam seems to extend beyond the exterior face of the foundation and sheathing. If that's true, how does it get covered up and protected from moisture? Why does the face of the concrete look as if its been bush hammered? I suspect the wall was not formed ;properly.
A steel beam should be in a foundation pocket and not visible from the exterior. Perhaps the pocket was omitted and a notch had to be cut after the pour. But that still would not explain why the notch is not centered on the beam.
I'm not going to guess where the other framing photos were taken. You need better photos or a description. The fact that they don't show steel joist hangers suggests they're not structural connections.
I don't know if this is shoddy construction but its definitely sloppy.
The matter of missing windows would hinge on your contract. It doesn't sound like you have a contract that you can enforce otherwise the GC wouldn't dare omit a window. I don't know what to tell you because I'm an architect who controls every aspect of a project from beginning to end. If a GC omitted a window he would be cutting an opening in a hurry if he wanted his payment application approved.
Its scary to hear about the risks homeowners take with the largest financial transaction of their lives. Sloppy work seems to go hand in hand with sloppy contracts.

HU-262669657
Original Author7 years agoThe weather barrier says 'Carter' in green lettering (i'll try and post more photos later). I think people like me take these risk because we don't know how else to go about it. I have since been looking into trying to get an independent inspector. But that area seems full of scamers wanting to make a quick buck too. I am not in the building trade so it's hard to know who to trust. Further, people are buying prebuilt houses everyday (with no oppertunity to evalute the construction process at all). That, like everything else in life, also seems to be a gamble.
- 7 years agolast modified: 7 years ago
If there is no other logo, the house wrap is most likely a "house brand" from a local lumberyard with their logo on it. That usually means its much less expensive than the best brands. You can test a sample of it using Matt Risinger's simplified method.
I suspect there was no brand or standards specified for the house wrap so if you asked for it to be upgraded, you would probably have to pay for it. If you do that, insist on Tyvek HomeWrap. If the windows are already installed, leave a foot of the old stuff showing around the windows and install the new stuff over the window flanges and tape it.
Where I live, Home Inspectors must be trained and licensed so a scammer wouldn't last a week. Where is the project?
If you hire one you will get a list of deficiencies and possibly advice on repairs but no advice on how to correct poor design or enforce a poorly written contract.
I wish you luck. I have to run; I'm inspecting two projects this morning before approving payment applications. It only takes a half hour per project because I know what to look for and the GC knows better than to stray from my contract documents.
- 7 years ago
You definitely can't do that to Tyvek. It was originally designed for mailing envelopes. Try to tear one of those up.
- 7 years agolast modified: 7 years ago
Looks like a house wrap made of woven polyethylene or polypropylene fibers. You not ripping that apart, some you can't even cut it will dull the blade after a few cuts.
- 7 years agolast modified: 7 years ago
Impossible to judge the steel beam installation without the building plans in hand. For instance, some of my builds have required the beams to be penetrated by bolts projecting up in the pockets and then secured with washers and nuts, then all grouted together. Thus in a flood, the house won't simply float off the foundation.
Block wall pilaster.
It's also possible that the formers overlooked a pilaster at that point on the wall.
- 7 years agolast modified: 7 years ago

This is Michigan: rain and snow country. Woven WBR, Menards foam gasket, no bug shield, I expected to see some sort of sheathing [OSB/PLY] over the mudsill. Over the sheathing we typ install some sort of neoprene gasket [flashing] covered by WBR. It is not unusual to seal the space under the mudsill. These details are lousy.
Looks like a long span but I do not see a column, would never use six shims, I can just order a correct size, could tip during q or t. Would never have I beam sticking out. Is this really an 8" stem wall? I hope this is not another case of woven WBR against R13 insulation and nothing in between. - 7 years ago
The beam is nothing less than a comedy of errors. The need for a beam pocket clearly got missed during construction of the cast in place concrete foundation. It looks like it will be unprotected on the end. It's just not right.
While shimming is often required under a beam, your guys have messed that up too. Best practice for shimming is to maintain full bearing under the beam's flange. The shims your contractor used are too small to meet that requirement.
If you have rigorous inspection by code inspectors in your municipality, they'll catch the issues and fail the structural inspection. If not, you'll be well served to hire a structural engineer to prescribe the fix and inspect it afterwards. Send the engineer's invoice to your general contractor. He can record it under the category of "continuing education expense."
- 7 years ago
There should be signs of subfloor adhesive oozing out from the bottom of the floor underlayment. Potential problem for movement and thus a squeaky floor.
- 7 years ago

So the shims simply sit on the concrete??
All the connections between steel beams and the concrete in my house are made with embed plates (as in this picture). These are placed in the forms before the pour so that the beam has a perfectly flat surface (and a controlled interface) to sit on. Then it’s welded to the plate to fuse everything together.
I’m sure there is a reason why the structural engineer designed it that way. Yours looks a lot less sturdy. Who came up with this installation detail?
- 7 years agolast modified: 7 years ago
It will be fine, there is nothing wrong with it and that beam is not going anywhere. But don't take my word for it, call an architect or whoever designed the drawings and ask them if this OK or not and you will get your answer.
- 7 years agolast modified: 7 years ago
The beam may not go anywhere but it might rotate or shift. If there is no anchorage a steel clip angle can be added at the inside of the foundation wall.
I’m curious how the excess beam length will be removed. - 7 years ago
There is no lateral forces to make that beam rotate. The nailed floor joist on top from each side will prevent the beam from shifting. When the pocket will get grouted will additionally secure the beam in place.
If there is a force strong enough to make that beam shift or rotate, the entire structure will fail before that beam does.
- 7 years ago
I’m curious how the excess beam length will be removed.
I've had them cut off by the welder when he comes to weld the beams to the columns.
- 7 years ago
As poorly executed as this installation appears to be, I would not assume that any subsequent steps will be properly executed.
- 7 years ago
@GN Builders, are you sure there is a plate bolted to the top flange of the steel beam and that the joists are fastened to it? I don't see any evidence of it in the photos.
- 7 years agolast modified: 7 years ago
There should be one, it's typical. If it's not, they have bigger issues than the way that beam propped up.
P.S. Just looked at the picture, there is a sill plate goes over the plate with sill sealer under it, so there should be a plate on top of the beam, since the joist bear on top of the sill plates.
- 7 years ago
@GN, I'd feel better if there were a photo clearly showing the plate and the joists attached to it before concluding the beam is braced laterally. I don't see any bolts protruding through the top flange of the beam which would indicate a plate.
I think this beam may have been installed on a retrofit basis to correct for either over-spanned joists or loads that were not properly carried down to the foundation.
- 7 years ago
From the photo, it appears a steel beam was simply plopped in place, to solve some sort of problem, apparently after the fact, and the beam is too long, and apparently not properly anchored or shimmed. The end of the beam we can see in the photo appears to just be sitting on some randomly placed shims.
If this was my house, I would:
1. Call the general contractor to meet me on the site and explain how he would do this to his own house;2. Call the local building department for an immediate structural inspection;
3. Withold progress payments until properly and satisfactorily anchored and resolved.
- 7 years ago
Charles, most of the time they will use Hilti gun and nail the plates on or glue them in.... I never seen a plate being bolted to the beam there is no need for that....The 2x plate is there only to act as a nailer to secure the joists, it's not going anywhere.
When we finishing a basement and there is a metal I-beam and the wall is going under it, we will also nail the top plate to the beam.
That said, I'm sure there is framing inspection and inspector will note if something is not right. I don't think a GC or a contractor on the job will install main structural member the wrong way and compromise structural integrity of the the entire building.
I also don't know why it's sticking out like this, I'm sure they will cut this off somehow but of course it would be much easier if it was recessed more.
Just give them a chance to finish it and worry about it if it's left like this.
Good luck - 7 years ago
@GN, the only time we use powder-actuated fasteners is for bottom plates of basement walls, but we more typically use Tapcons. When we combine steel and wood--whether it's to the flange or web of an I-beam, we always through bolt it with the bolts staggered. That way we know we've got a reliable connection both with respect to shear and uplift forces and it's easy to verify at inspection.
There are too many questions about this beam and how it has been installed to assume the builder will end up doing it correctly. We don't know whether the owner's request for a building inspector to inspect something would be addressed. Indeed, we don't even know if there are code inspections in the area in which the home is being built (in the rural area I grew up in there are still no inspections.)
I think the owner will be well served by hiring an independent professional to review the what, why, and how. Sooner is better than later.
- 7 years ago
Charles, I know what you saying, you have to meet drawing specification details when you're dealing with shear and uplift forces, there is no argument in that.
I'm talking about basic residential construction where an I-beam is used to eliminate a few lolly columns, where you nail the plate on top of it so the joist can be fasten to it.Quick and simple and it's done this way in every house that is going up involving I-Beams...
Unless of course attachment detail calls for something else. - 7 years ago
@GN Drawings and specs? I suspect that's the root cause of the OPs issue. At this point, a prescription requires diagnosis.
- 7 years ago
Charles, I gather that the root of his issue was the blocking having a gap in it and the few plates that they stuck under it which is nothing if this is a typical residential framing and the drawings don't have any specific details in regard to that.
- 7 years ago
"I’m curious how the excess beam length will be removed."
There's a good chance they will leave it and put a little gable roof over it and add a couple miniature fake shutters.
- 7 years ago
@Mark, wouldn't that be something to see LOL... but seeing a few things in my time it wouldn't surprise me a bit and I'm sure there is someone out there who would do something like this.
- 7 years agolast modified: 7 years ago
There shouldn't be any need for grouting the opening; the beam should be cut back 2" shy of the foundation wall face and a 1 5/8" thick CMU soap laid flush with the face of the wall then waterproofing can be added (I suspect its only dampproofing).
If the beam is not connected to the wall, that should be corrected as well. I would add a steel clip angle at the interior face of the wall under the beam. Beams should always be connected to their supports and before someone contradicts me, here's the recommendation of the Manual of Steel Construction.

- 7 years ago
Res nobody is contradicting you, I'm sure this rules from this book apply to some heavy structural design, as you can see the word " recommended" is in almost every sentence in that book.
This is a case of conventional framing, you not dealing here with heavy loads, shear loading, uplift loading, wind loading, etc If you take and calculate the the load for the tributary area, at 40LL and 10 DL you probably be 400-500 LB per foot on that beam which is nothing.
That said, we don't even know what they have there, if this is completed, what the design calls for, what the specs are, what the requirement is... I don't think the residential code book even covers the subjects related to I-beam girders, in every case there is a an I-Beam, the beam design is per engineering specs and 90% of the time the beam is dropped into the pocket and the only detail on the plan is the needed min bearing... Not to mention inspectors always pay attention and check all the structural details.
If you ask me, the drawings for a street lamp have more engineering details and attachment detail specifications than an I-Beam girder in a residential construction.
Frankly speaking...I think the reason this is done the way it is,that I-Beam was slipped in there after the fact and it looks like they screw up with the length and after they got it in as far as they could, there was no way out and this is why it's sticking out. Because if this beam was installed without framing in place, it was a snap to cut to size, and if they didn't do that, now they have to do it with a grinder or what ever they can fit in there to make that cut. - 7 years ago
@GN, for the record, I'm a licensed professional engineer and contractor. There are too many unknowns to pronounce the beam as adequate or inadequate for the intended purpose. It may have been retrofit to address over-spanned joists or it may be in lieu of
a load bearing wall in the basement or it may be required to address a point load that was not accounted for in the original design or any number of other conditions. We don't know.
Accordingly, the beam's design and installation should be evaluated by an appropriately credentialed professional with access to all the required information.
I don't know what type of homes you build, but our home designs frequently need to address shear, uplift, large magnitude point loads, cantilevers and wind loading. The Manual of Steel Construction is a helpful reference. We have a copy in our office. We use it and follow the "recommendations."
Homeowner interests are rarely served by someone making a structural engineering prescription from a distance without the benefit of appropriate credentials or proper engineering analysis. I suggest you review the limitations of your NJ contractor's license and the requirements for consulting as a structural engineer in the state of Michigan. If you don't have a P.E. license in Michigan you may be subject to disciplinary action. - 7 years agolast modified: 7 years ago
Charles I'm happy for you and congrats on getting your P.E and contractor license and the last thing you need to worry about is what the limitations on my license are. I know exactly what they're and what they do in Michigan is the least of my concerns :-)
Now lets get back to reality... The original poster has a builder who has an engineer or an architect with a license hanging in his office just like you have yours hanging someplace, who designed this house and everything in it and I can bet anything that they all will say there is nothing wrong with the way its done and it will pass the inspection...If not the issues will have to be addressed and corrected simple as that.
That said I'm building same homes everyone else is building and we also address shear, uplift, cantilevers and wind loading and all that other stuff when they need to be addressed.
I don't work with large magnitude point loads, I'm not building bridges or tall buildings, and I don't deal with earthquake or hurricane regions, etc and this is why I don't go looking for steel manuals with attachment details for mega structures and heavy steel construction and try to apply the same requirements to conventional residential construction.
I looked at the guys picture and everything looks OK what he is showing. My OK or your manuals and how it should be or would be is meaningless in here.
I will say this again, everything will come down to what the inspector says and if he red tag the job, the issue/s will need to be addressed and corrected simple as that.
- 7 years ago
I do not understand how this got to this point. The original author showed aftercut beam pocket with the beam sticking out and what appears to be 6 shims under the beam, woven WBR right next to a sill plate with no sign of structural sheathing and no gasket between WBR and the sill ... asking IF this is a "shoddyy construction".
Why are we discussing that I (H) beam or load? The inspectors are clueless about the design and loads as long as engineer signoff so it probably is ok. This builder is cheap [savings on WBR].. He would not be installing a steel if he could avoid it.
- 7 years ago
BT, I'll tell you how it got to this point, just like everything else get to similar points in here...
I made a small example that this is probably residential construction and this beam is supporting a fairly light loading and the only reason it's there to eliminate a few lolly columns, everyone is doing this lately and it's done the same way, except its not sticking out pass the foundation... Maybe they plan to attach hammock to it... who knows!The next thing you got this the forms filled with concrete and embedded plates into concrete and all sorts of attachment methods and before you know it got to "shear, uplift, cantilevers and wind loading and all that other stuff" that should be addressed followed by examples from books for heavy steel construction and various methods which being used when building "mega structures"... nothing more but typical engineering over-reach.
I'm still trying to figure out what force will uplift that beam in the basement, or my next suggestion was gonna be is to hang a sign off the beam not to use a ceiling fan to prevent wind loading etc.
It is pretty common practice what they did there with a few plates to shim that up where it needs to be... there is no need to try and make an elephant out of a fly over nothing. I'm sure after all done and over with, the beam will be cut back, the foundation void will be grouted and parged over on the outside and everything will look nice :-)If they leave this way tell the builder to fill that hole in and make it all nice before you write a check.
- 7 years ago
I would not rely on the judgement of a building inspector. An inspector, if there is one, will most likely ask for a compliance affidavit or letter from the engineer of record. Whether the engineer called for the beam to be anchored to the wall or not, its good practice to connect any beam, of any size, under any loading to its support. In this case, since the joists appear to be parallel to the wall, the beam would brace the top of the wall. Now that's something the building inspector might ask for.
- 7 years ago
I'm amazed that any knowledgeable person, especially a builder, would think its OK to leave an unanchored wide flange beam in wood frame construction, particularly when the beam is resting on a half dozen poorly placed metal shims. And if the photo is correct, the beam isn't level.
If it's OK to leave the beam unanchored and put one's trust in gravity, why put hold downs or anchor bolts in foundation sill plates? Why fasten second floor joists and roof rafters to sill plates? Why don't we just trust gravity for everything?
And of course we don't have to worry about settlement, shrinkage, wind, lateral and other sorts of forces over the live of the house do we?
Just cut the end of the beam off, fill the opening and forget all about it. On to the next job. - 7 years ago
The question was if it is “shoddy”, not if it “works”. While the beam shoved into the cutout on a few sloppy metal shims will likely work in the sense that the house won’t collapse, I’d consider it shoddy to plop a few metal shims under a steel beam that’s off-center in an apparently non-preplanned cutout in the concrete wall.
I’d rather have embed plates (that cost $20 each - wow, what an enormous extra expense) and a welded beam connection than a sloppy shimstravaganza.
Because it’s clean and neat.
This example here is simply shoddy - doesn’t matter if you do this all the time for residences.
- 7 years ago
Virgil, so the house will not slide off the foundation when you turn your family room fan on.
If you need to ask this question you shouldn't be in this conversation :-).
That said, look in the code requirements and the schedule how the sill plate should be bolted to foundation.When did the last time you saw a triple girder or paralam being bolted to foundation. They will nail a brace at the top to keep it in place while the joist being installed to prevent from moving... other than that tell me about a force that will move that beam after the joist nailed on top of it... and if you come up with that force, I think the entire house be gone before that beam moves :-).
- 7 years ago
Galore, if you grout that joint right now the plates will be embedded into concrete and it will cost you $5 to do that.
- 7 years ago
Res, I don't know what picture you looking at, but the picture I see the joists run perpendicular to the beam as they should be.

If the joist run parallel to the beam, you don't need that beam at all. - 7 years agolast modified: 7 years ago
Here is a typical I-Beam girder installation in any residential construction, unless the project location is in an earthquake region you would have a engineering detail how the beam should be connected.

Top View
The temporary cross brace is to keep from moving while setting the floor joist.If this was a wooden beam, the ends be wrapped in flashing with allowable air space to prevent moisture build up.
There is nothing complicated here and its the same what the OP showed, except the beam sticks out for what ever reason it wasn't cut back, and like I said earlier, it looks the beam was put in there after the fact, because of the foundation cut-out and it looks like they cut the rim joist for the same reason to have more wiggle room.