steam radiators not getting hot

6 years ago

We heat our second floor with steam radiators in each room. The air vent in the basement was giving off a terrible hissing sound with steam water spurting everywhere. It must’ve been occurring for a very long time because I found mold on the walls and the ceiling. We’ve been in the house for 4 years. My HVAC guy came and agreed that something was wrong with the system. He said that the pressure thermostat on the boiler was broken and was sending too much pressure to my system and that was creating the hissing sound in all of the steam. He replaced the thermostat and cleaned out my steam boiler. He told me that I have to clean my steam boiler every two weeks using a valve and a bucket. He also turned down the pressure on the new thermostat to 1 PSI. That evening we did not have any heat coming out of the steam radiators even though the thermostat was on 70°. The room never got above 63° and the radiators never got hot. I contacted my HVAC guy and he told me to turn up the pressure on the boiler a little bit. I turned it up to 2. A little bit of heat came, but certainly not enough to heat our entire second floor, and only the tops of the radiators got warm while the bottoms stayed ice cold. He came back again this morning and replaced the air vent that had previously been spewing steam and water. He said the system should work fine now, but it has been set to 70° for the last four hours and there is barely any heat coming out of any of the radiators. I am at my wits end and don’t know what to do. The system is clean and so many different parts have been replaced in this past week. Before the thermostat was changed on the boiler it was up to 9 psi and we had lots of heat and liked it. My HVAC guy said that was enough pressure to heat the Empire State Building. The Pilot is on in the boiler.

What else can be wrong???? We’re in the north east with ice and freezing temps!!!!

Comments (4)

  • 6 years ago

    It looks like you have a 2-pipe steam system with a fairly new boiler. I agree with your HVAC guy that 9 PSI is very high for a two story steam system. However I am skeptical the pressuretrol was defective and needed to be replaced. If he has replaced many parts, and leaves without testing the fixes he makes leads me to believe he does not know what he is doing.

    My suspicion is the boiler was changed and the piping was done incorrectly. It is possible the pressure was increased to 9 PSI to compensate for these problems. I think if you have to go 3 PSI then low pressure is not the problem. The higher the pressure, the more gas you are using. How much are you spending on gas to heat the house?

    You need to find a steam heat expert. A good one is hard to find. Where are you located?

    You can post you questions and look for a steam contractor on Strictly Steam. The link to finding a contractor is at the top of the page.

    Keep us posted on what you learn.

  • 6 years ago

    Thanks. The piping is original to 1937.

  • 6 years ago
    last modified: 6 years ago

    The piping right above the boiler needs to be done correctly with cast iron pipes. That’s the first thing that needs to be verified. Many times boilers are replaced by a plumber who does not understand how a steam system works. The rest of the piping is not as critical. It does have to slope back to the boiler.

  • 6 years ago

    The best place e on the internet for steam questions is heatinghelp.com lots of serious steam heat experts over there, They will want to see many more pictures including the piping near the boiler. If the installer did not read the manual for your boiler and install the piping according to the manufacturers directions this likely your problem.