AC will not cool below 80 degrees

6 years ago

Hello I am new to this and could use some guidance. I apologize in advance if this post is too long, but just want to provide as much information as possible.


Current system, dwelling and location

Location: Louisville, KY

Dwelling: Condominium around 1,500 SQ FT (2nd floor - top floor so my duct work is in the attic)

System: Split system

- Outside AC part is a York (model # H1DB024S06A) it original form when these condo were built (so over 20 years old)

- Inside unit is an Aqua Therm (model # 24VAQ3) it also is original. This is a heating system that draws water form my hot water heater through coils with a blower to heat

my home.


Situation:

I have been in my condo for 4 years. I have had AC unit serviced every year. All has been good by the company that has done this yearly service with the exception of these last 2 years they have had to add about 2 lbs of Freon each year. So I know I do have leak and probably not much time lift with this unit. That being said the last time the serviced my unit was in May of this year. As I mentioned previously at that time the system checked out good, but they added 2 lbs of Freon. The temperature has been increasing here in Louisville, KY, but even on days to where the high temperature outside would only maybe get to like 88 I could not get my AC system to cool my home below 80 degrees. It would just run for hours. I never recall that being the case in past years.


I have a second company come out to look at my unit just 2 weeks ago. They checked Freon levels and he stated it read 40 and the Freon is fine. I explained situation to where it would run for hours and not get below 80. A comment was made stating "yeah it is going to run all day unit eventually at night it will coll done enough to where it will shut off". To me that is not a sufficient answer. I know I have a 20 year old plus unit that is probably not that efficient, but if it only the in mid 80's I believe I should be able to coll my place below 80 degrees without the unit having to run all day. They told me to check and make sure the fan is blowing and the there is condensation on the coil coming out of the unit and that it is not freezing up. I have checked both of these. The fan is running fine and there is no freezing.


Again I know I have a 20+ year old unit and I am probably in need a a new unit, but I still can't help to think that something is not right that it will not cool below 80 when I previous years I know it has been able to. Also I was just not happy with the last response of "run all day and eventually it will get to temperature at night" That is not how an AC system is supposed to work.


Any thoughts questions or suggestions?


Thank you,

Comments (4)

  • PRO
    6 years ago

    You have a twenty year old unit in the south with the ducts run in the attic. And it’s the hottest part of the summer (almost). You have literally everything going against you. First thing- how hot is the attic that the ducts run in? If that is the typical uninsulated attic it could be 130 degrees. I would attempt to fix that ASAP. Otherwise you are probably due for a new unit, and you probably want to replace all the ducting you can access because most 20 year old ducting isn’t sealed well and the boots aren’t insulated.

  • 6 years ago

    also a possible leak and being undersized...I would want to know what supply temperature are you getting on several locations upstairs. The aqua therm unit serves as an air handler as well? Be thinking about a new system and upgrading attic insulation, sounds like it’s time.


    TD

  • 6 years ago

    Reading your history it seems you still have a leak and it is getting worse. The last tech is either incompetent or does not want or cannot provide you additional R22 refrigerant. You are right his response not correct and the system is not operating properly. R22 refrigerant is no longer being manufactured in the US and is becoming very expensive. You have to make a decision whether you continue to invest in a 20+ year old system or cut your losses and replace it.

  • 6 years ago

    Assuming the system has worked fine in the past, it should be capable of cooling your house now. Global warming notwithstanding, this year hasn't been that much hotter than the preceding 4 years, so there's something wrong with your system. I'd contact the service manager or owner of the company you've been using and let them know you didn't understand the last tech's response to your question and that the system still isn't working correctly. You will likely need a new system soon but you should be able to get this one up and running to, minimally, the performance of previous years, even if its only for a few months.