venting fireplace possible?

5 years ago

My preference would be to have a vented fireplace however our builder is stating this isn’t possible. I offered to pay for a power vent but they still seem to think it’s impossible whereas I’m tempted to think they just don’t want to be bothered. I’m turned off by several things about a ventless unit- the time restrictions, effects on air quality and the amount of heat produced, particularly in the smaller den as the fireplace is double sided. Any insight as to wether or not venting to an exterior wall based on this image is in fact possible so that I can determine wether or not it’s worth fighting for. Thank you!

Comments (13)

  • 5 years ago

    The location of the fireplace creates several challenges. Most likely you can’t run the vent to the rear wall because of the rear wall offset. There are specific clearances required for the vent location, depending on the unit you choose. Venting in a corner can be difficult. Venting to the left side wall is possible depending on how the ceiling is framed. If there is a second floor above the den, then the direction of the floor joists/floor trusses will determine the difficulty of venting that way. If there is no second floor, then venting straight up through the roof would be easiest. However, I’m guessing this is not an option since it’s the most logical solution and the first one the builder would try. Perhaps an electric fireplace would be the final choice. They are becoming more popular because of venting issues.

  • 5 years ago

    Yes, there’s a second floor, and no wall directly above to carry through to the roof. I hadn’t considered the offset issue... I thought the power vent would compensate. Guess this is why I’m the buyer not the builder.

  • 5 years ago
    last modified: 5 years ago

    A ventless fireplace is simply too dangerous but show the design of the whole house. The vent of a "direct vent" gas fireplace can run horizontally to an exterior wall or vertically to the roof or a combination of the two.

    The information below is for a specific fireplace. For your fireplace you must refer to the manufacturer's installation instructions.





  • 5 years ago

    I agree and I really want to find a way to have a vented unit installed! Here’s the whole floor plan

  • 5 years ago
    last modified: 5 years ago

    Alternatively you could make the windows in the den about 12" narrower so the clearances in the corner near the fireplace meet the required minimum clearances. I would use smaller flanking windows and a larger center window unless you have a view of a ski mountain or the ocean.





    But refer to your manufacturers instructions rather than those above.

  • 5 years ago

    Thank you for that! They’ve already framed and ordered the windows so I don’t think they’d be willing to do that. I did ask wether they could run the duct to the exterior wall and up to the roof. Would a power vent be helpful in this situation or not necessary?

  • PRO
    5 years ago
    last modified: 5 years ago

    You are asking too late to receive a viable response.

  • 5 years ago

    The only thing that’s been done is framing, no walls, electrical or plumbing yet. You don’t think there’s still an opportunity to edit this? I hope that’s not the case.

  • 5 years ago
    last modified: 5 years ago

    As a general rule a fan is not needed if the vent is within the shaded area of the diagram below but you should call the manufacturer to be sure. The slope and shape of the roof will be an important factor.

    It is also possible to locate the termination in the exterior wall of the second floor between the bedroom and bathroom windows.

    In any case there would be a chase in the corner of the bedroom.



  • 5 years ago
    last modified: 5 years ago

    Mark, I never say it's too late to redesign even after the house is built. A client told me that once and I didn't realize it wasn't a compliment until later. But here it's free.

  • 5 years ago

    Thank you for your input! You’ve given me hope that it can be done!

  • 5 years ago
    last modified: 5 years ago

    It seems pretty certain a horizontal soffit to the exterior wall on the first floor and a vertical chase on the second floor would allow you to place the termination box on the exterior wall above the second floor. You just need to be comfortable with the soffit and chase.

    But I haven't seen an elevation drawing or a roof plan and the termination box must fit between the windows and between the roof eave above and the high point of the pent-roof below.

  • PRO
    5 years ago

    I consider the framing to include the walls. Consider this concept with a single door.