griz4

Should i get a 5 Ton over a 4 ton?

17 years ago

received my 5th quote for new HVAC system in 19 year old home. Replacing a Lennox Pulse system (model #G14Q4/5-100-7) Looking at American Standard 95% VS 2 stage system and 14 SEER Condensor with matching coil. This 5th quote was only bid that did heat loss calculation (though i dont have results) The following was written in the quote and wonder to the pros out there is it worth it to go to the 5 ton MDL#AUH2D120A9V5VAA(is only $120 more than the 4 ton system). I have read alot about not getting too big a system as it then works too hard and then becomes not as efficient. As you can see i have a 3rd floor finished attic. my home is 2800 sq foot colonial. Winter is not issue, stays warm up there but in summer need to use window AC to keep comfortable. So would the 5 ton blower asst in moving that air up to 3rd floor with the VS blower on this type of furnace? or should i just get the 4 ton MDL# AUH2C100A9V4VAA(100k BTU) furnace.

'WE HAVE QUOTED THE 120,000 BTUH FURNACE TO GIVE YOU THE 5 TON DRIVE AS THE COOLING COIL HAS A CAPACITY OF 54,000 BTUH AND WE ALSO WANT TO ACCOUNT FOR THE FINISHED ATTIC. THE HEAT LOSS CALCULATION ONLY REQUIRES A 100,000 BTUH FURNACE BUT IT IS ONLY AVAILABLE WITH A 4 TON DRIVE. THE 100,000 BTUH FURNACE WILL HEAT AND COOL

BUT THE 5 TON DRIVE IN THE 120,000 WILL BE MORE EFFECTIVE'

Comments (11)

  • 17 years ago

    Did the other contractors take into consideration the finished attic? Is the roof adequately insulated?

    If the heat calculation is correct, and you are presented with a copy, then it would be correct to have a 5 ton air conditioner.

    Most homes built around 20 years ago had oversized furnaces and undersized ductwork. If your current furnace is on the loud side, then a larger a/c will cause your indoor unit to be much louder.

    Also, under such a situation, the furnace unit would work harder due to increased static pressure and would probably enjoy a shorter life. For the sake of your attic, the rest of your house may be muggy due to running short a/c cycles (poor humidity removal), which could also negative affect the lifespan of the outdoor unit.

    Did the contractor discuss the status of your duct system, and any modifications?

    Also, an oversized furnace such as proposed would probably run almost exclusively in first stage. If you do go this route, insist on a 2 stage thermostat.

    V

  • 17 years ago

    It would be a 5 ton furnace but just 4 ton condensor per the quote (model #'s are listed in original post)
    Only 1 other contractor considered the attic space and he was thinking i only needed a 3.5 ton furnace, but when i told him about the attic space that is finished, he said would need at least a 4 ton. I am also have the panel replaced for the 2 zones i have and getting American standard thermostats- 600 family programable ones.

    I think the ductwork is in good shape. home was custombuilt and all top of the line equipment insulation was put into the home.

  • 17 years ago

    What A/C are you getting (size)? Model #?

    I don't see how having a 5 ton blower would necessarily help since it's still going to be set up for 4 tons of airflow/approx. 1600 cfm. The 5 ton furnace has a 1 H.P. motor;, the 4 ton has a 3/4 H.P.

    Even the 4 ton furnace set up for 1600 cfm (your A/C) still won't be running at its max setting. Ask the dealer what his reasoning is exactly.

  • 17 years ago

    This is the condensor in the quote:

    american Standard 4 TON, 14 SEER CONDENSER WITH THE R410A
    REFRIGERANT MDL# 4A7A4048A1000A

  • 17 years ago

    First, if the duct system isn't set up for 2000 CFM, getting the bigger blower won't help. Also, unless you are in a very dry climate, moving 2000 CFM through a 4 ton system can make for higher humidity.

    Personally I'd plan on staying with the window shaker. I don't think anything you can do will keep the attic as comfy as a lower floor since heat rises and the cool air falls. Also if furnace is in the basement, hard to push enough air up 3 floors.

    I'd get the properly sized furnace. Make sure you get a nice 2 stage thermostat.

  • 17 years ago

    Agree with baldloonie, and also the 120k furnace will probably have to move more air yet, and if your ductwork can't handle it, it's a no go.

  • 17 years ago

    I really dont know what my ductwork is set up for and have no idea how to check. There are a bunch of numbers on the ducts i can see in the basement, but dont know if that means anything.

    My goal is not to get the 3rd floor as comfy as rest of house, just did not want it to be an oven.

    so it seems i should just request the 4 ton furnace if i go with this quote. am also going to make sure the thermostat is set for 2 stages.

  • 17 years ago

    Other posts here provided good advice.

    Viewing the charts I put on the linked page below might be helpful.

    Lower Air Infiltration & do what is essential for optimal ductwork & Airflow performance. - udarrell

    Here is a link that might be useful: Ductwork Sizing & More

  • 17 years ago

    Update
    Well i decided to go with the 5 ton blower on the furnace hoping it would help in cooling my 3rd floor space.

    As far as the heat of my new system, could not be happier. This system is QUIET compared to what i had. Never hear it come on from the first or 2nd floor of house like i used to with the Pulse furnace we had. The house does not get overheated when system comes on, the heat is very evenly moved throughout the house. The old system would just blast max heat and would get so hot in the house.

    Just started turning the AC on more the last few days and it is also working great. The condensor outside is super quiet, do not even hear it go on; used to be able to hear the old condensor all the time from inside the house. Also the cold air is getting to the 3rd floor and keeping it cool! It also seems i dont have to set the thermostat as low. the house is very comfortable set to 73-74 degrees. Last summer had to keep it on 70 to get comfortable in summer. Have not hit any 90 degree days yet so that may change. But right now, very glad with my decision to go with the AS 95% VS unit i noted in my first post. I also got the 10 year P&L warranty for that piece of mind coverage.

  • PRO
    3 years ago

    it’s been a while, but wondering how your system is doing today?

  • 3 years ago

    13 years later? It could be time to replace the replacement.

    Let old threads rest in peace.