Air Intake Vent Size

13 years ago

I have a 3 ton central AC/Heating unit which uses a 20x24x1 filter. We recently put an addition, approx. 500 sq ft, on the house for a total of approx. 1500 sq ft.

We were told the existing unit was enough to support the addition. Should we make the intake vent a bit larger around 20x25x1 at least?

Comments (7)

  • 13 years ago

    The filter size is determined by the amount of air flow which must pass through it. You have to determine when the air flow is the highest between the furnace and AC. The formula I use is for a filter rated for a velocity of 300FPM:

    air flow (CFM) / 2.08 CFM/sq. in. = filter area (sq. inches)

    Let's assume you have a 3 ton AC which would normally be using 1200CFM of air. The filter area calculation would be:

    1200CFM /2.08 CFM/sq. in.= 577 sq. in.

    A 20 X 24 filter (480 sq. in.) would be too small. You would need a 24 X 25 filter. The fact you added 500 sq. ft. of area does not change the filter requirements. If you are going to change the filter then see if you can fit a 4 inch media filter. They are less restrictive and last longer than the one inch.

  • 13 years ago

    Thanks Mike.

    Would the CFM info be listed somewhere on the unit?

  • 13 years ago

    It is probably not listed on the unit. It may be in your furnace manual. An air flow of 350-400 CFM is what is required per ton of cooling. Usually the air flow for the air conditioning is higher unless you have an a very big furnace.

  • 13 years ago

    Thanks again Mike.

  • 13 years ago

    Chances are if they only installed one return on a 3 ton unit they also shortchanged the return ductwork. Adding a 2nd return will allow you to get the full 3 tons you paid for. Right now it is probably like most systems that only deliver 2/3's of their rated capacity.

    FWIW my house is 100sqft bigger and cools with a 2 ton AC. It will keep it 75 indoors on a 100degree day.

  • last year
    last modified: last year

    If I are installing a 4 ton AC unit which we prevoulsy had a 3 ton unit do I need to increase the size of the vent to accommodate a larger filter? Say going to a 20x20x1 to a 20x25x4? The house when we purchased already have 2 AC units at 5 ton each.

  • last year

    The house has 2 AC units at 5 ton each and you want to increase an exiting 3 ton unit to 4 tons? Do you have a very big house in a very hot climate with many south facing windows.

    My first suggestion is to verify through a load calculation if increasing the size of existing unit is necessary. If it is then you should increase the filer size and the return to accommodate the increase air flow. For 4 tons a 20 X 25 inch filter could work, but bigger would be better.