American Standard Quote Input

16 years ago

I got another quote for two American Standard heat pumps. These are four ton units. The size determination was done with a manual J load calculation. It will be replacing a 10 SEER, 3 ton Payne which is not that old but purchased by the penny pinching previous home owners.

One is an American Standard 4A6H5048E1 with a 4TEE3F65B1 for approximately $7100. 10 years parts, 1 year labor warranty.

The other is an American Standard 4A6H6048C1000B (I assume it will be a replacement for 4A6H5048E1) for approximately $8600. 12 years parts, 1 year labor warranty.

Both include a Honeywell media air cleaner and a Pro-8000 thermostat. Both systems are quoted with a 10 KW heat strip.

Thoughts on the quoted systems and price? I'm in Tennessee where electricity is 8.3 cent per kilowatt hour.

Thanks for any input!

Comments (5)

  • 16 years ago

    You will likely never recover your investment in energy savings,even if you were jumping from 10 seer to 20 seer, because the seer ratings are horribly unrealistic.

    In my case, jumping from an "8" seer to an "18" seer saves about 20% in energy costs under real-world conditions, and power in my area is variable-pricing depending on time of day, 22 cents/kw is the top rate. You may save a higher percentage but a lower dollar amount per month - even if you save $100 a month(highly unlikely), that's alot of months before you break-even.

    I'd be very concerned with the "upsizing" if your current unit can maintain acceptable temps - you could negate ANY energy savings if the replacement is too large.

    Here is a link that might be useful: old post about seer ratings, scroll down..

  • 16 years ago

    The 4A6H6 isn't a replacement for the 4A6H5 (the E1 model is pretty new) -- it's a '16 SEER' 2-stage heat pump. The upgrade price seems a bit steep, although it is slightly more efficient and has the capability to run at a lower capacity (not much lower, 75-80%) for more comfort/humidity removal.

    The ductwork for a 3 ton unit will do no good with a 4 ton unit -- may even worsen some matters such as noise and efficiency. I hope those estimates include some ductwork modification.

  • 16 years ago

    Verify the warranty on the 4A6H6. I'm pretty sure, after registration,it carries a 12 yr compressor and 10 yrs on the rest. Like Ryan said, verify return and supply ability to handle the extra airflow. Use Am Std's ACONT900 if you choose the 4A6H6 model and make sure the indoor section is also communicating. The 4A6H6 will be going to non-communicating on the next gen. Part of the gov't interference w/ tax credits driving the market.

  • 16 years ago

    A huge thanks to everyone that responded with info.

    As far as the duct work question, there is an additional 14x14 return that will be added to the basement (which currently does not have one) when the new system is installed. I recently added a heated and cooled 240 square foot addition to the house which is which has added a branch off the original duct work to support two additional registers. The entire house is about 2800 square feet.

    The input duct work to the air handler is 21x12 inches, output is 19x9 inches. Two of the three people giving me estimates said the duct work could support a four ton system. The third seemed intent on replacing my three ton with another three ton system. Based on the info above, does my duct system sound like it could support a four ton unit?

    Thanks again for any info - I am really happy to get it and want to make the right decision.

  • 16 years ago

    Any thoughts tigerdunes?