Which Bryant AC for this system?

17 years ago

Hi,

We are replacing a 20 yr. old furnace and AC. Want to qualify for tax credit, naturally, as well as maximize efficiency. This is to cool our upstairs level, approximately 1900 SF. Unit is located in basement, if that matters. We are in the Chicago metropolitan area

Furnace specs:

Bryant 95% efficiency Model 355CAV4060100

BTU 100,000

Output 95,000/75/45

AFUE 95%

Variable speed, 3 stage

AC quoted was Bryant 114ANA042

coil 5.0 ton model CNPVU

BTU cooling 42,000 tons 3.5

SEER 14-16

Puron 410A

Evolution Thermostat

$8918 before rebates or credits

I think from reading this forum, that this model 114 AC unit is low-end. Would we do better with a different model and why?

I asked about other AC units and he said this:

-model 114 has same efficiency and same air handling(?) as model 124

-model 124 is quieter than 114 and costs $400 more

-Both 114 and 124 qualify for tax credit

-Model 126 costs $1000 more than 114

Model 187- Evolution line costs $1400 more than Model 114

Are the 2 stage systems worth the extra cost?

Is this coil ok- don't have any other info except the letters above

Thank you!

Comments (23)

  • 17 years ago

    jkpita

    Bryant is good equipment, especially the Evolution furnace.

    But why have a top of line furnace and a low end AC condenser? I would substitute the Preferred 15 AC mdl(165). It is compatible and fully supported by the Evolution controller.

    and I would insist upon a load calc. I suspect you may be oversized both heating and cooling.

    IMO

  • 17 years ago

    Thanks for the response.

    I will ask if a load calculation was done. How do I know if it was done right? The contractor did take a very quick walk through the house, I assume noting returns and vents.

  • 17 years ago

    get the load calc in writing on the software letterhead.
    a properly performed load calc takes many factors into consideration and normally takes no more than two hours to perform.

    your ductwork should be inspected and now is the time to address any hot/cold spots within your home's second floor.

    IMO

  • 17 years ago

    Rep will do load calc this week.

    Rep says AHRI website gives higher SEER rating to AC models 114 and 124 when combined with the furnace we are choosing (model 355CAV), vs.the 165. Doesn't know why that is, though.

    Recommends if we want to upgrade the AC to choose a 2 stage like model 126, 180 or 187. Says features on 165 make it easier for service rep to deal with unit, but are not features that we, as customers, would necessarily notice. Thoughts?

  • 17 years ago

    jkpita

    165 is first choice(Preferred 15 mdl)

    126 is second choice(Legacy 16 mdl)

    you do want a new and correctly sized refrigerant lineset.

    IMO

  • 17 years ago

    Actually here is a spreadsheet with the numbers.

    Note that $525 was a rebate from Bryant at the time and the remote was "no charge" .... thus the approx $2700 in savings

    KC

    Here is a link that might be useful:

  • 17 years ago

    I am confused!!!! You (JKPITA) have a quote for the Furnace and A/C for $8918 before rebates. I was just quoted as follows:

    Furnace Bryant 355CAV060120 112K BUT
    4 Ton
    17.3 SEER
    95% AFUE
    Model 180 Condenser

    Cooling

    Bryant FE4ANB006 Evolution Fancoil, Bryant 180A048 Condenser
    two speed puron
    4 tons
    17.3 SEER
    13.4 EER

    New Honeywill Pro 4000 Thermostate
    Evolution Interface for A/C unit in attic
    Install of 5 additional registers
    New outdoor unit base
    New media air cleaner
    Direct vent of existing hot water heater

    My price is $22,415 but only $9,800 after $10,000 State of NJ Clean Energy Program, $1000 Bryant Rebate, $1500 Federal Tax Credit and $125 NJ Energy Audit rebate.

    Is the contractor inflating the price because I am entitled to all of the rebates???

    ANY HELP OR INPUT IS APPRECIATED!!!!!!

  • 17 years ago

    Doesn't make sense to quote both a Honeywell and Evolution thermostat. Is this for two separate systems? If so, no reason not to use the Evolution interface for both.

  • 17 years ago

    Yes, it is 2 separate systems The quote says "Install 1 new Evolution Interface for unit in attic unit."

    The attic is where the a/c system is.

    In order to qualify legitimately for NJ's $10,000 rebate (50% up to $10K), he will be running a register to my master bedroom (which has a separate electric heating system) up through the attic in order to meet the square footage to required energy efficiency improvement required for the full credit. Could this be a possible reason for the Interface???

  • 17 years ago

    Yes, it is 2 separate systems The quote says "Install 1 new Evolution Interface for unit in attic unit."
    The attic is where the a/c system is.

    In order to qualify legitimately for NJ's $10,000 rebate (50% up to $10K), he will be running a register to my master bedroom (which has a separate electric heating system) up through the attic in order to meet the square footage to required energy efficiency improvement required for the full credit. Could this be a possible reason for the Interface???

  • 17 years ago

    Dan999, Are you getting 2 furnaces and 2 AC units? The prices do seem inflated if for only one furnace and AC. Although the quote for the Model 180 condenser added $1400 or $2500 to the quote we got

    If you search for "bryant" on this forum, you will see many have posted their quotes and model numbers. I can't believe it costs double the Chicago price to do business in NJ.

  • 17 years ago

    I should add that our Bryant dealer is giving the $1000 Bryant rebate up front, so maybe add that to the prices I quoted.

  • 17 years ago

    Tigerdunes,

    We have had a load calculation run and as you suspected, the recommended system was oversized. I do have a copy of the load calc if you would be willing to look at it.

    The quotes include new refrigerant lines and tin plated coil.
    Dealer is also giving Bryant $1000 rebate up front.
    Both quotes include an Aprilaire and Evolution controller ( Evolution only for the applicable AC unit; otherwise it gets a different, but included thermostat)

    Package 1:
    FURNACE: Bryant Model 355CAV042060
    BTU output 60,000 output 57000
    AFUE 95%
    3 stage variable speed

    AC Model 124ANA030
    Coil size 3.5 Model CNPVU-tin
    BTU Cooling 30,000 Tons 2.5
    Puron r410 single stage
    SEER 16

    $7360

    Package 2:

    FURNACE: Bryant Model 355CAV042060
    BTU Output 60,000 Output 57,000
    AFUE 95%
    3 stage variable speed

    AC Model 126ANA036 or Model 165 ( same price)
    Coil size 3.0 Model CVPVU-tin
    BTU Cooling 36,000/18,000 Tons 3/1.5
    2 Stage Puron

    $8260

    Questions:

    We are leaning toward the cheaper AC model 124A. I know you recommended the Model 165 earlier. What would be the benefit of the 165 that would justify the additional $900 in cost? Is a 2 stage AC really better than a single stage? This unit is located in the basement but services the upstairs.

    Will AC model 124A achieve 16 SEER when combined with the 95% furnace?

    Why does the coil and BTU size change when comparing Model 124A to the 126A/165A?

    The original quote was for a 100,000 BTU 95% furnace and the Model 114 AC. Do the new prices seem in line with the change in equipment?

    Thanks for your keen eye and let me know if you wan

  • 17 years ago

    OK, I'm a little confused.

    You say that you have been quoted a system with the Legacy 14.

    Then you say you have been quoted a system with the Legacy 16 OR the Performance 15 at the same price. I can not find an AC model 126 ANA on the Bryant website. They show the 124ANA, which is their Base model (and I think it is also considered a Builder's model, which is fine), but please correct me if I am wrong. And you say the Performance 15 is a 2 stage compressor. The Performance 15 is a single stage compressor, I believe. Someone correct me if I am wrong, because I am looking at these systems as well.

  • 17 years ago

    Sorry, found the 162ANA with the 355AVC042060.......... but it doesn't seem to be a 2 stage compressor? Am I missing something?

  • 17 years ago

    We were originally quoted on AC Model 114, which is the builder's-grade unit. We didn't want the lowest end AC. The 124 is a step up from that. Costs $400 more than the Model 114A

    The 126A is not shown on the Bryant website, but we do have a brochure on it. It is Legacy line, 2 stage and Puron refrigerant; states up to 16.5 SEER. Don't know why it isn't on the website. Model 165A is Preferred Series, 2 stage, up to 15 SEER

    The new quotes reflect the smaller furnace, now that a load calculation has been done, and more choices in the air conditioning line.

  • 17 years ago

    jkpita

    what size is existing AC and how did it perform?

    did it ever run continuously and/or fail to keep your upstairs cooled to your comfort thermostat setting?

    I will post back about condenser mdl recommendation.

    IMO

  • 17 years ago

    Old unit ( 20 yrs old) did not run continuously and did cool to proper setting on thermostat. The back of the house faces west and has no shade. These rooms ( 2) would be warmer than the rest of the upstairs until the sun moved lower. Then they would cool fine. Load calculation did take this into account

    Not sure of the coil size- compressor was 3.5 tons. We have only been in the house for a year.

  • 17 years ago

    jkpita

    what were your results of cooling load calculation and at what design temperature was used for both outside temp and inside temp?

    I am not certain I would drop from a 3 1/2 ton condenser down to a 2 1/2 ton condenser.

    post back. I will address your options.

    IMO

  • 17 years ago

    Tigerdunes,
    I read the notes with the load calc. The rep changed the coil size to 4.0 if we go with the 126A, in order to achieve higher SEER to qualify for tax credit.

    He also specified no window treatments and stretched the load parameters quite a bit beyond what would be expected for the Chicago area ( his words).

    Summer temp: outdoor dry bulb=95; indoor dry bulb 75. Indoor Relative humidity 50

    Under cooling system summary it says: Net required- cooling tons 2.0; BTU 24,020/ Recommended 2.32 tons; BTU 27,805

    Thanks

  • 17 years ago

    Tigerdunes -any further input?

    Bryant 126A or 124? Or 165, and if so, what is the justification for the extra cost over the 124?

    Thanks- trying to make a decision this week.

  • 17 years ago

    jkpita

    first off let's put pricing aside for the moment and assume that 2 1/2 ton condenser is correct size.

    I am a numbers guy. here are the AHRI matching performance/eff numbers for four configurations.

    Legacy 14
    3047932 Active Systems LEGACY 14 PURON AC BRYANT HEATING AND COOLING SYSTEMS 124ANA024-D CNPV*3017A** 355(A,C)AV042060 23200 13.00 16.00 1 RCU-A-CB

    Legacy 16
    3471819 Active Systems LEGACY 16 PURON AC BRYANT HEATING AND COOLING SYSTEMS 126ANA024-A CNPV*3017A** 355(A,C)AV042060 25000 13.30 16.00 1 RCU-A-CB

    Preferred 15
    1389897 Active Systems PREFERRED 15 PURON AC BRYANT HEATING AND COOLING SYSTEMS 165ANA024-B CNPV*3017A** 355(A,C)AV042060 23400 13.00 15.50 1 RCU-A-CB

    Preferred 17
    3484878 Active Systems PREFERRED 17 PURON AC BRYANT HEATING AND COOLING SYSTEMS 167ANA024-A CNPV*3017A**+UI 355(A,C)AV042060 25000 13.30 16.50

    as you can see, these four AC condensers have very close numbers. I personally like the Legacy 16 and Preferred 17 the best-more cooling BTUs.

    these are the major differences between the Legacy series and the Preferred series.

    1.the Preferred series is much quieter
    2.the Preferred series has a nicer condenser cabinet
    3.the Preferred series is compatible with the Evolution control-ie the Legacy is not which means you lose diagnostic capabilities

    now to pricing. dealers tend to stick it to customers on upgrades. I would tell your dealer to price the upgrade on his cost difference against the 124 plus $100 which is fair to both him and yourself.

    I would ask you to doublecheck the size of your existing AC condenser. if 3 1/2 ton, I question the advisability of dropping down to a 2 1/2 ton.

    IMO

  • 17 years ago

    Tigerdunes, Thank you so much for the information and your opinion. You have been most helpful!