New Build - One or Two HVAC Systems?

12 years ago

We are getting close to starting a custom build and trying to decide if we want one HVAC system or two.

Background info:
We are on the north side of zone 4. First floor master with 3150 sq ft on the first floor, 1300 sq ft on the second plus a 500 sq ft bonus room over the garage. 1500 sq ft of finished basement. We will use blown cellulose in 2x6 walls with an inch of XPS sheathing on top of the OSB sheathing. An inch of Foam on the attic floor with blown cellulose on top to ~r50.

Original spec was for a 4 ton (in basement) for the first floor and basement with a 2 ton (on second floor with ducts in the attic) unit for the second floor. In talking with the HVAC contractor his load calc says a single 5 ton system would be enough for the house. We would put the unit in the basement. Make zones for basement, first floor, master, second floor. The issue is running the ducts. We would need to use open web trusses for the second floor and make three runs up from the basement due to the placement of beams (not many options to move the beams). The single system would be carrier infinity or potentially geothermal.

The HVAC contractor thinks it can be done, his major issue is getting the runs up from the basement. The builder is concerned the single system won�t adequately cool the second floor and hasn't used open trusses in the past.

Any opinions on using one system? Are there specific pitfalls we may run into? I tend to favor this as the duct work would not be in the attic and I would only have one system to maintain. Additionally the cost is ~25% percent less.

Comments (14)

  • 12 years ago

    I am going to second the idea of two systems with both in the basement. I would avoid installing any HVAC equipment and duct work in the attic if it is possible.

    The north side of zone 4 is near the Canadian border. You need to get a heating and cooling calculation to verify the furnace and AC sizes. In your in a cold climate, but you have above average insulation. There should be no rules of thumb used in the sizing.

    Do you access to natural gas? What are the electric rates? A two system geothermal is going to be expensive. You may not see a return on investment if you are using gas or your electric rates are lower than the national average.

  • 12 years ago

    Thanks for the feedback.
    hvtech24 - the contractor certainly feels he would have no problem with the zoning. Guess I'm not sure how to confirm he is an expert? If we did one system it would be modulating equipment.

    mike_home - my issue with both systems in the basement is I add the costs of the open truss floor, soffits/chases/ductwork and still have the cost of two systems. Not sure if I would get the return on investment there, is the duct lost to the attic that much? I'm in southern Ohio, we have natural gas and electric rates are average. I pretty much ruled out Geo if we go the two system route.

  • 12 years ago

    There is more loss with duct work the attic. The other issue is some contractors don't like to install a high efficiency condensing furnace in an attic. They are afraid the condensate will freeze. A proper installation with heat tape solves the problem.

    Have you spoken to the HVAC contractor and see if it possible to run the duct work for the second floor so that is is parallel with the floor joists? This is how it was done in my house.

  • 12 years ago

    6500sq ft over 3 floors is going to be tough for a single system and complex for zoning, especially if the system is on the bottom floor (basement). 5 tons is 1300sq ft.ton - did he do a detailed heat loss calculation to come up with that figure?

  • 12 years ago

    2 systems with zoning controls. If you go this route, then you have to take a hard look at the best integrated zoning system, Carrier Infinity or sister company Bryant Evolution.

    And your builder/HVAC company must pay close attention to insulation and ductwork size/design for your FROG which are notorious for heating and cooling.

    IMO

  • 12 years ago

    the frog was what I though of also.
    use the foam (1" on attic floor) to encapsulate
    the walls, ceiling & between floors of frog area.
    then it will be easy to condition.

    btw...if you use foam on the roofline, you'd keep
    second floor equipment in a semi conditioned
    unvented attic.

    you could then skip walls & sealing of between
    floors of frog & the 1" on attic floor.

    I'm a big fan of zoning (one system, multiple zones)
    but everything would have to be just right for
    it to work in the house you describe.
    too much room for error IMO, I'd opt for
    2 systems & possibly minisplit for frog.

    kudos for the foam sheating on exterior of
    walls. follow up with air tight drywall approach
    on interior of walls.

    start thinking about fresh air provisions.

    best of luck.

  • 12 years ago

    You would be disappointed with one system using zoning controls. Your expectations are way too high.

    IMO

  • 12 years ago

    Thanks again.

    don't think we can run the ducts through the second floor joists because of lvl beam placement.

    Contractor said he did a manual J and 5 tons would cover it, I didn't go into detail on the calc. I'll give him a call to get more detail.

    for the FROG we are planning on 1" closed cell foam all the way around with cellulose or batts over the foam. Thought about making a semi-conditioned attic but it's a pretty tall roof line so figured costs would add up. Maybe it's worth getting a quote on that. I did consider a minisplit for the FROG if needed, but hoping the system can be designed to handle it with foam. Expecting to put in an HRV/ERV.

    Based on responses I'm a bit worried about the risks of one system, seems like the most efficient route but if I end up with a second floor that is always hot I won't be happy.

  • 12 years ago

    Your last post has me confused. How come running the duct work for the second floor with a single 5 ton unit in the basement is not a problem, but is a problem if you two systems?

  • 12 years ago

    the joists run north-south and there are two lvl beams running east-west which the joists attach to with joist hangers. If you put the unit on the second floor you can't get to the other sides of the lvl beams. I guess you could if you dropped soffits but it wouldn't look good on the first floor.

    if the unit is in the basement we could make three supply/return runs up from the basement to the second floor, one on north side of the north lvl beam, one in-between the lvl beams and one on the south side of the south beam, using open web trusses you could then run the ducts as needed for each room,

    Guess maybe there is another way but I haven't found one without major changes to the layout. In my area nearly all the homes put the second unit on the second floor and run the ducts in the attic.

    This post was edited by wynnejt on Wed, Nov 12, 14 at 20:33

  • 12 years ago

    >If you put the unit on the second floor you can't get to the other sides of the lvl beams

    I believe what Mike was getting at (and what I was saying earlier as well) is why can't you put both units in the basement?

  • 12 years ago

    If you can service the whole house from one system from the basement then you should be able to have install two systems. In my house there is a common return shared by both furnaces. It is not ideal but it works. There are dampers in the return to prevent back flow of air when only one furnace is running.

    I get the feeling the builder and the HVAC contractor are more motivated in keeping costs at a minimum rather than working with you in trying to design a good system. It is unfortunate but this is very typical in new construction when it comes to HVAC.

  • 7 years ago

    Hi OP, can you share the approach you took and is it working well?