Software
Houzz Logo Print
nancydrew2007

S.E.E.R. Differences

19 years ago

I am about to replace our heat pump/AC unit with a new Trane system. I'm wondering if updating from a 14 S.E.E.R. to a 16 S.E.E.R. unit is worth it. I am told I am getting a good deal on the price differential. I live in PA, but only plan to be in the house for another 3 years. Can anyone tell me what the expected price difference would be between 2 such systems and how much more "efficiency" I can expect from the 16 S.E.E.R. unit? If, for example, I pay $900 more for the 16 S.E.E.R. will it be worth it all things considered, including heating and cooling comfort?

Comments (26)

  • 19 years ago

    16 SEER uses a dual-stage compressor. The first stage is 75% of the rated capacity. Most systems in use today use 1 single stage compressor.

    Your true operating costs are determined by the Energy Efficiency Ratio (EER), and not SEER.

    Post the model numbers of the heat pump condenser and air handler.

    What are your electric rates ($ per kw-hour)?

    Good luck.

  • 19 years ago

    Thanks for responding so quickly last week. I left a message for the contractor to provide the information you suggested I obtain and all I received was this: "Here are the ratings 15.5 SEER / 11.2 EER / HSPF 9.1"

    I doubt this is helpful without a comparison to the information from the lower SEER model. Is that correct?

  • 19 years ago

    Nancy:

    Posting the model#s of the heat pump condenser (example: 4TWX4036) and air handler (example: 4TEE3F37) would be most helpful. With this info, I can go to the American Refrigeration Institute (ARI) website and verify the info that the salesman has given you. I would not buy anything unless the model#s of both the condenser and air handler are on the quote. This will prevent the "bait and switch" of the air handler. The air handler makes or breaks the system performance.

    11.2 EER is week for such a high SEER system. An HSPF of 9.1 is excellent.

    How many tons - 3,4,5?

    Is $900 the true differential cost between the 16i and 14i?

  • 19 years ago

    TX! I'll go back and ask again. It's a complicated issue as I am replacing Trane equipment that was still under a 10-yr warranty. The original was installed back in Jan. 2002 so now the contractor is trying to get what he can for us from Trane. The previous unit was 4-ton so it was my understanding that the new unit would be 4-ton. I will need to confirm. I'm not sure what HSPF is, so I will need to resarch that. What is more important - EER or HSPF - I mean, if the EER is weak but the HSPF is excellent, which should I go by? I was told that if I wanted to "upgrade" from a 14 SEER to a 16 SEER it would cost me an additional $825 and that would include a new thermostat. However, now I see that the contractor came back with a "15.5" SEER, not 16 - is that really the same? Does the 15.5 have the dual stage compressor?

  • 19 years ago

    One more piece of info to add to the previous message - I was told:
    "the ARI # for the tax rebate is #1106632"

  • 19 years ago

    Nancy:

    Energy Efficiency Ratio (EER) = system cooling ouput / compressor amp draw. It represents the cost to run the a/c at 95 degrees outside air temperature. Higher EER is cheaper to operate. An EER of 12 minimum is the goal.

    Seasonal Energy Efficiency Ratio (SEER) = EER x fudge factor. The fudge factor represents much cooler outside air temps. A high SEER doesn't mean lower a/c operating costs.

    Heating Seasonal Performance Factor (HSPF) represents the cost to run the heat pump in heating mode. An HSPF of 9 is great. Higher is better.

    An XL16i is nominally rated at 16 SEER and does indeed have a 2-stage compressor in the outside condensing unit. However, the system is SEER rated and not just the outside unit. The air handler (inside unit) has an effect on the SEER rating which is why I keep asking for model numbers.

    The ARI# 1106632 shows a condenser model# 4TWX6048B1 condenser paired with a 4TEE3F39B1 air handler. It is indeed 15.5 SEER, 11.5 EER, and 9.1 HSPF. It is rated at 47,500 btu cooling (almost a full 4 tons = 48,000 btu) and 43,000 btu heating at 47 degrees. Note that it is weak on heating btus for a 4-ton system (48,000 btus).

    Note that this system does NOT qualify for the Federal Tax Rebate of $300 (must be 15 SEER minimum, 13 EER, and 9 HSPF - all 3 must be met). See link below and scroll down to "air source heat pumps". There is another air handler for the 16i that gives better numbers and will qualify. I'll check it tomorrow in work where I have a faster computer connection.

    Post model#s of the 14i that was proposed. Maybe a better bang for your buck.

    Take care.

    Here is a link that might be useful: Federal Income Tax Credits

  • 19 years ago

    Nancy:

    ARI# 1106632 is the best performing match-up for the 16i heat pump. I have a typo in the air handler model#. It should be 4TEE3F49B1.

    I looked up an XL14i and found a 4TWX4048 condenser matched with a 4TEE3F48 air handler provides 48,500 btu cooling, 13.75 SEER, 11.3 EER, 9 HSPF, 44,500 btu heating at 47 degrees. This combination provides more cooling and heating capacity (1000 more btu cooling and 1500 more btu heating) than the 16i match-up. This may be a better deal for the price.

    The 16i has a dual stage compressor which runs at 75% rated capacity on the first stage. This is good for high humidity climates with long summers. The 14i has one single stage compressor as do most systems in use today.

    Neither system qualifies for the $300 Tax Credit, but both will get you a $50 credit for the variable speed fan in the air handler.

    Good luck.

  • 19 years ago

    Thanks again. Here is some more info: Our current system:
    Trane XL 1200; Heat Pump Weathertron; Model TWX048D100A0; Serial # Z402LUR1F.

    Message from contractor when I asked about whether we were getting a 16 SEER or a 15.5 SEER model: "XL16i is a 16 SEER unit but depending on the size and how itÂs matched with an indoor unit is the true system ratings are what I gave you. The 14 SEER may not be a 14 SEER system it could get 13.5 or 13.75 or 13.85 and maybe even less than 13.5. When you get into a larger unit like a 4 or 5 ton the efficiency will go down a little and that is why the rating is 15.5. If you take a 2.5 ton or a 3 ton the rating would be 16 SEER. The indoor unit we matched up is the best efficiency rating the unit can get out of a 4 ton 16 seer unit. The $825.00 includes the upgrade thermostat which is a nice thermostat and must go with the 16 SEER. XL16i comes with a 10 year warranty on the compressor, coil and parts and 2 years on labor."

    So is he saying that he is matching the outdoor heat pump unit with our current indoor air handler???? Or no? There may not be anything wrong with our indoor air handler - we have had 2 compressors fail on our system since original installation in Jan 2002. Which is why we now need at least a new compressor. Been told it is probably due to duct work issues.

    If he is matching a new heat pump with our current air handler (which is from 2002), are you saying it is not eligible for the $300 rebate? I must question him on this.

  • 19 years ago

    Nancy:

    The ARI# that he gave you is valid only for the MATCHED SET for the condenser and air handler model numbers stated in my last post. You should be getting a new air handler, Model#4TEE3F49 for your 16i condenser.

    "So is he saying that he is matching the outdoor heat pump unit with our current indoor air handler???? Or no?"

    - This was answered by the installer with "The indoor unit we matched up". Anotherwords, a new air handler unit that he selected, not your old air handler.

    YOU NEED TO GET THE MODEL#S OF BOTH THE AIR HANDLER AND CONDENSER IN WRITING ON THE QUOTE!!!!!(sorry to yell but it is important and your questions indicate that you are confused). If you have the 2 model #s, there is no confusion.

    A failure of 2 compressors in 5 years is indicative of a poor installation (improper system charge, poor brazing procedures, poor refrigerant purge/flush, etc.)

  • 19 years ago

    Dear Gary G. - You are really kind to keep following up on my e-mails. I owe you at least lunch - or maybe even dinner :) I did ask for the model numbers, along with a few other questions, and the text I shared was how the contractor responded. The proposal he already provided is primarily for the installation of the new equipment that Trane is "willing" to give us being that this is the 3rd compressor now for this system - again, a system installed in January 2002. I am with you on the "poor installation" issue - we have not had the original installer back since he replaced the 1st compressor, which was July 2003 - 18 months after the original installation. I assumed there was a real issue with him when the Tx valve failed in July 2005. I wish there was a way to make the original installer pay for all for this but apparently I need more "proof" to do so. I will ask the "model numbers question" again of the current contractor. He is suggesting that I "jump at this offer" from Trane and I really don't want to upset anyone and not get the equipment or pay even more for the labor like I have in the past for the previous problems. We've had a couple of quotes for the labor involved this time and this was the best one. The one quote didn't specify the equipment and it was for $2557.03. Another quote was for Airhandler: 2TEE3F49A; Electric Heat: BAYHTR1419BRKA; Heat Pump: 2TWB2048; 4 tons, S.E.E.R. 13.25; HSPF: 8.0 - that was for $5475 for the labor only!

    Thanks again.
    Nancy D.
    P.S. Just let me know where to "send your lunch or dinner." :)

  • 19 years ago

    Nancy:

    Have you answered your original question of "Is it worth an extra $900 for the 16i over the 14i?"

    Whichever you choose, I would consider a Parts and Labor warranty for your piece of mind. I read that you will be in the house for another 3 years, and they will give you 2 year labor warranty (that's 1 year without a labor warranty). How about 3 years or 5 years labor warranty, just in case?

    Best to you.

  • 19 years ago

    Have I answered my original question....not specifically, no. But perhaps I can't as there may be "indirect savings" - I don't know. It doesn't sound like I am going to recoup $825 worth of savings over the next 3 or 3 1/2 years in my PECO (electric) bill by going with the 16i vs. 14i. I don't know exactly what warranty Trane would give me on the 14i system - I just know the 16i "comes with a 10 year warranty on the compressor, coil and parts and 2 years on labor." The proposal/cost for labor from the current company is more reasonable than the $5475 quoted by another - even if I do add an additional $825. I am disappointed about the tax credit but will get over it since neither the 14i or 16i seems to qualify for the $300. Now what worries me more is the integrity of the contractor. i.e., If the 16i system is not really going to provide better heating and/or cooling capabilites than the 14i - but I am being told to "jump at it." Also, is the price difference between these 2 systems really $825 - doesn't seem like it should be based on the btu, etc. info you provided. I'll tell you what I do know...this HVAC business is complicated and everyone tells you something different. I am not sure if that is because even some contractors don't really understand the issues or if it is based on some trying to get more of your money than others. Also, I sure wish I would have gone with a different installer to begin with in 2002. The one I used was recommended by a friend!!!

  • 19 years ago

    Nancy:

    The 14i comes with the same parts warranty as the 16i and is supplied by Trane. Not sure about the labor warranty. When I was quoted a 14i last May it included a 2 year labor warraanty.

    You will not re-coup $825 savings over the next 3 years going from the 14i to 16i (heck, you won't re-coup it over 10 years), but at least you know that ahead of making your decision. There are really no indirect savings.

    Did the contractor who offerred you the great deal on the 16i also offer you the 14i, or is that another contractor? Maybe you are being told to "jump on it" because he makes more money from Trane? The price difference has nothing to do with system btus, but with a dual-stage compressor versus a single stage compressor.

    The reason why I keep torturing you for model#s is so I can provide you facts and info to help in your decision. I have read many posts where someone bought a system without doing any digging only to find out that their high SEER system wasn't what they were lead to believe.

    I understand your frustration but don't get bogged down with it. In the end, you will be HVAC-educated and should feel comfortable with your decision whichever way you decide to go.

    Additionally, you will be ready for this again when you sell your house in a few years and do it all over again.

  • 19 years ago

    I totally understand your request for the model numbers. I did ask and when I did so I said I wanted to know for tax rebate purposes. That is when I got the response: "the ARI # for the tax rebate is #1106632." The 16i vs 14i are both from the current contractor - let's call him "Nate." Is there any possibiity that "Nate" doesn't know the model numbers and was told 14i vs. 16i only from Trane? Again, we are getting the equipment from Trane. So the 16i has a dual-stage compressor and the 14i doesn't. Per your note, the dual stage compressor runs at 75% rated capacity on the first stage, which is good for high humidity climates with long summers. The 14i has one single stage compressor as do most systems in use today." We live outside of Philadelphia - not as humid as South Carolina, but it can get a little sticky for several weeks at a time in the summer (like this past one). I will ask again for all model numbers and see what response I get. Tx! It's not torture at all.

  • 19 years ago

    Nancy:

    I am from South Philly but I have been living in Baltimore for the past 17 years. Humidity can be high but nothing like Florida or the Gulf Coast.

    "Nate" must know model numbers because he has to order the heat pump condenser and air handler from the Trane distributer and he needs the model numbers for the order.

    Because we live on the East Coast and can get some nasty winters to go with hot and humid summers, the heating portion of the heat pump is very important. This is why getting the most heating btus from the system is a necessity. Below freezing, the typical house needs supplimentary heat as the house loses heat faster than the heat pump can supply it. This is where the back-up resistance strips in the air handler come into play. The better insulated the home and the more heating btus available from the heat pump, the less the back-up heat is needed (up to a point). Electric resistance heat can be several times more expensive than heat from a heat pump.

  • 19 years ago

    I didn't know if it was possible that Trane merely said to "Nate," "We can give her a 14i totally covered under warranty, or a 16i for an additional $825, if she wants to pay for the "upgrade." Again, I'll ask for the model numbers because if understand your message above, we may be able to get more heating btus from a certain combo of the 14i system vs. the 16i system. Which seems counter-intuitive to me, but what the heck do I know. One would think that if you pay more for the 16i it would "work" better. I guess I still don't understand the benefit of the dual-stage compressor.

  • 19 years ago

    The dual stage compressor is supposedly better for comfort in the summer as it can run at 75% capacity which reduces humidity without over-cooling the house. Thus the house can be at a warmer temperature but feel cooler because of the reduced humidity. This is what you're paying for with the 16i. The 19i has 2 compressors with the idea of summer comfort being the same. The dual-stage or dual compressor set-up really isn't for the Northeast where heating is required since the heat pump will be running on 2 stages most of the time.

    "Nate" = North American Technician Excellence. Time for Nate to step up to the plate.

  • 19 years ago

    I sent "Nate" an e-mail on 11/13 asking again for model numbers. Still no response. Not a good sign.

  • 19 years ago

    Sounds like "Nate" is only interested in selling the 16i. He can't BS you now because you are HVAC educated.

    How about another Trane installer? Trane already knows your situation - the service would be done thru another certified Trane installer.

  • 19 years ago

    "Nate" response:
    "The model # for the XL14i 4TWX4048A1000A outdoor unit and the indoor unit is 4TEE3F49A1000A and the XL16i outdoor is 4TWX6048A1000A and indoor is the same 4TEE3F49A1000A. Just a reminder that the XL14i is being phased out and they are holding one for us. We need to get back to them before long so we donÂt lose that unit. They are running out of them and they are a fast selling unit."

    I'll go to the ARI web site shortly and check it out.
    Comments?

  • 19 years ago

    I don't think the 14i is being phased out.

    Here are the performance numbers with model# of condenser and air handler provided:

    14i
    50,500 btu cooling, 11.4 EER, 14 SEER, 45,000 btu heating at 47 degrees, 8.45 HSPF, 28,000 btu at 17 degrees

    ARI# 5487720 is discontinued for air handler ending in A1, ARI# 1106614 is active for air handler ending in B1. Minor revision to air handler, same performance numbers.

    16i
    47,500 btu cooling, 11.5 EER, 15.5 SEER, 43,000 btu heating at 47 degrees, 9.1 HSPF, 27,600 btu heating at 17 degrees.

    ARI# 1106632.

    Comparison
    The 14i puts out 3000 more btu cooling at almost the same EER (operating cost). The 14i puts out 2000 more btu in heating at 47 degrees outside air temp but costs a little more to run (HSPF of 8.45 vs 9.1). Heating btus are similar for 17 degrees outside air temp.

    I would choose the 14i and bank the $900 savings.

    Best to you.

  • 19 years ago

    I searched the ARI web site also and I didnÂt get any results when I searched for just the XL14i outdoor unit 4TWX4048A1. I did find matches when I searched just the indoor unit 4TEE3F49A1. As you said, it looks like it is to be matched with "B1" outdoor units.

    For the XL16i I found the outdoor unit 4TWX6048A1 but it is only matched with a 4TEE3F40A.

    Also, when I searched by the ARI reference number given previously (1106632) I get the "B1" models. I also called Trane customer service in Texas directly. They couldn't find the "A1" match ups either. I'm wondering if they (both installer & local Trane person handling my problem) are offering me "old" (i.e., discontinued) equipment because this is a replacement for equipment that failed under warranty.

  • 19 years ago

    Nancy.

    The ARI search function can be a pain. Type in the outdoor unit model# and the indoor unit model# only - leave out the XL16i or XL14i. End the input with "48" for the outside unit and "49" with the air handler. All numbers after these will be displayed when the search returns valid matches.

    The A1 and B1 are typically minor revisions.

  • 19 years ago

    So does that mean that if an indoor unit with an "A1" at the end supposedly matches with an outdoor unit with a "B1" at the end (per the web site search) it may still be okay to use this "A1 indoor" with an "A1 outdoor" unit?
    I just want to make sure that the indoor & outdoor units "match" or are the most compatible with each other.

  • 19 years ago

    Yes, they are a match.

    If you go with the 14i, will you be getting the same 2 year labor warranty that was offerred with the 16i?

  • 19 years ago

    Good question. Will ask.