New home zoning help

18 years ago

Ok - I have searched and searched and I can't really tell what is the best to do in this situation.

3 level house with daylight basement in NC triangle - both heat and a/c are issues but winter is mild (think lows rarely below mid 20s). The house will be tight, low-e windows, above code insulation etc. The house will be about 1900 sq feet per floor and the basement will initially not be finished and probably will leave some unfinished (ie workspace/storage).

We are looking to be as green as reasonable (anything with a 10 year payoff for sure). Sounds like heat pump with gas backup. That isn't the issue so much as number of units and zones. The builder is used to using 3 units for similar houses presumably with no zoning (aside from the 3 units). We would definitely like zoning - we like to sleep in the lower 60s - but otherwise heat to the high 60s and cool to the high 70s.

It seems to me that 3 units is overkill and I would like to see if 1 unit with zoning is possible. Certainly it seems like 2 units with zoning would be okay but how does one plan for a future finished basement in this situation?

Priorities are energy savings and ability to keep the master (2nd floor) cold while not changing the rest of the hosue. Also, I would love a way of bringing in outside air when it is reasonable to do so - we often have 80 degree days and 55 degree nights. Running the A/C seems ridiculous in such situations but pulling the fan in and out of the window gets tiresome. I would love a system that checks the outside temp and just brings it in when it makes sense for the desired temp.

Also - does it make sense to skip the gas backup and just use a NG direct vent fireplace on particularly cold times? There are definitely areas around here with no NG that just do HP.

Comments (4)

  • 18 years ago

    is this a retrofit or new home construction?

    2 systems with three zones-zone 1 upstairs;zone 2 main floor and basement

    three stats-one for each zone

    zone 1-high eff HP with var speed air handler either Infinity 16 HP or Performance 15 HP

    zone 2-Infinity 16 HP with either staged backup heat strips or 80% Infinity backup nat gas furnace plus zoning controls

    zoning controls are not for the inexperienced,get references and visit a home with Carrier Infinity with zoning controls. It's the only system I would suggest and you have one vendor responsible for everything with no third parties.

    run the numbers on fuel comparison calculator

    IMO

    Here is a link that might be useful: Fuel Comparison Calculator

  • 18 years ago

    tigerdunes - appreciate the response. It is a new home. On zone 1 is it reasonable to split the master bedroom off of the rest of the upstairs? We like it cold at night but don't want to waste doing more air space then we need and the kids wouldn't like it. I've considered a small window unit for the summer but the wife wouldn't go for it (she hates the fan I bring out for fall and spring). We often open the window a crack in the winter but that is just wasteful.

    Any problems zoning for the basement if it isn't finished?

    Hope my GCs sub has experience. If I want, he will go with another sub but I am picking my battles here (ie - only 1 or possibly 2 subs would I want to pick my own).

  • 18 years ago

    david

    the most important part of a new system(s) with zoning controls is correct sizing of the equipment, correct sizing of ductwork both supply and return, and an HVAC contractor who has demonstrated experience and can provide references that you can visit.

    if you plan on zoning the upstairs, then I would recommend the two stg Infinity 16 HP rather than a sgl stg HP like the Performance 15. Is it reasonable? Of course this can be done but you will have to weigh the costs.

    since this is new construction, you can install zoning controls for all zones using one system. however, I would stick with two systems though. and for the upstairs, if you do elect a high eff HP with backup electric heat strips, the electrical contractor will need to size your electrical supply/breaker box correctly.

    and for the main floor/basement system, the downstairs ductwork can be stubbed now for zoning with completion at a later date.

    and as been said, Bryant offers same equipment with the Evolution system.

    IMO

  • 17 years ago

    have you talked to ac companies about zoning?
    hiring a different contractor for ac instead of using
    the ac co that he uses shouldn't be a problem.
    start interviewing ac companies.
    ask about load calculations to understand why you
    prolly don't NEED 3 units.
    and know that zoning is one unit..different zones w/tstats.
    not 3 different units.

    best of luck.