frozen pipe to backflow preventer, again!

19 years ago

For the third year in a row I've noticed the supply pipe going into my outside backflow preventer has frozen and split. This year I thought I had figured it out. Inside my basement, there is a pipe for the sprinkler that comes off the main water. It has a ball valve, several inches of pipe, then a spigot, several feet of pipe, then it goes thru the foundation outside.

Like every year, last fall the sprinkler was blown out and the ball valve inside closed to prevent water from going outside. Over the winter I left the spigot open and sure enough, a small amount of water seemed to be making it's way past the valve. (I just let it drain into a bucket). Somehow the pipe outside still froze and split, I'm not sure why.

I want to replace the ball valve but is there a better valve to use to prevent this from happening?

Any advice would be appreciated.

Bill

Comments (6)

  • 19 years ago

    i have a similar set up, but don't have a check valve. It sounds like when the system is being blown out that some water is remaining between the check valve and the house. It can't freeze and break if it's empty of water. Somehow the water is still in that section.

  • 19 years ago

    Thanks for replying.
    You may be right. I can't remember where the compressor was connected to the system. Should it be inside at the spigot or outside near the back flow preveter?

  • 19 years ago

    If you put the compressor inside, it won't blow air/water out because of the back flow preventer (that only allows water/air to come in).
    I would blow out the whole system as has been done in the past and then open the bleed screw on the ball valve inside and then blow a little more (all the blowing should be from the outside). This last step should clear any water that is between the back flow preventer and the ball valve.
    If you don't have a bleed screw on the ball valve, you are going to have to install a vale that has one or you will have to somehow disconnect the pipe in the cellar each year. It all comes down to finding some method of getting that last bit of water out that is between the BFP and valve in the cellar.

  • 19 years ago

    thanks, i'm going to try the repair myslef, including a new backflow preventer which looks like it has developed a leak. I haven't seen these at home depot. Would a plumbing supply carry them?

  • 19 years ago

    HD should at least have the simple, single flapper type. A cheap single backflow in brass should be less than $10. If you get into some fancy preventers with dual flaps and screens and cleanouts you can get into $150+. If it's a simple one, ask at HD they should have it. If not, a pluming supply place for sure will.

  • 19 years ago

    Ask for a vacuum breaker, that's what the cheap one are labeled...