I purchased a new GE Profile gas slide-in range. I also bought a new gas line for it. My question is: Do I need to use gas threadding compund, or whatever it's called, on the threads? Or is just screwing it in fine?

Comments (4)

  • 19 years ago

    What kind of connection?
    Tapered pipe thread require thread sealer.
    The fittings for flex line require sealer for the adapters to the pipe, but not on the flex line to adapter connection.

    Purchase a bottle of leak check.

  • 19 years ago

    It's a 4ft. pre-fab yellow flex line. The threaded connections are already installed. All I need to do is screw one end to the hard line and one to the range.

  • 19 years ago

    You need to install the Stainless flare fittings that came with the new flex pipe on the stove and on the gas pipe (or shut off valve). They must be installed with the appropriate sealant -- either yellow Teflon tape or pipe dope made for gas lines (use the dope). Be sure that you have a wrench on the stove fitting to avoid transferring the torque to the stove fitting -- it's usually a regulator or something that doesn't appreciate being twisted.

    You then install the flex line onto the flare fittings without sealant.

    You must test the connections after you are done. I usually use soapy water (look for bubbles).

    It is fairly straightforward, but you do need to do a good job and not cut corners. Gas is safe when you do a good job but it can level your house (and the neigbors')if you don't.

    BTW: Don't count on the gas valve to give you a positive shut off. Cap the pipe if you have it open. I have seen too many leak significant amounts of gas while I was replacing an appliance.

  • 19 years ago

    Check your local code carefully before connecting this cooktop.

    Some codes do not permit flexible gas connectors but rather they require all gas appliances to be plumbed with iron pipe the full distance. For this reason the appliance manufacturers allow a rather large opening through the back of the appliance cabinet and the actual point of connection to the gas regulator in the appliance is in the front 1/3 to 1/2 of the appliance frame. This permits running a gas pipe from the wall and extending out about 12" to a gas cock type shutoff valve. With the large opening the range or cooktop can then be slide in place and the end of the gas line with the shut off will now be inside the appliance cabinet. Once in place the cooktop can be raised allowing access to connect a nipple from the stop cock to a union and a second nipple from the union to the 1/2 female iron pipe thread in the appliance gas regulator thus completing a rigid gas pipe connection.

    When using a flexible connect the codes prohibit a flexible connector from passing through any floor, wall partition, cieling or appliance housing.
    Ref:
    International Residential Code IRC-2422.1.2
    Uniform Plumbing Code UPC-1212.0X2

    Properly when connecting a gas range or cooktop with a flexible connector you must first install a rigid pipe extending from the gas regulator to the exterior of the appliance cabinet and the transition for rigid pipe to flex pipe must occur outside the appliance housing.