2 inch ABS to basement

16 years ago

Hi There,

I'm redoing the old drain pipe in my bathroom. The shower and tub used to go through notched joists via 2" galvanized pipe to the main stack. The joists are only 2*8's! So I had to sister all the existing joists. Due to code and logic I can't drill the joists for 2" PVC. My question is, can I run 1.5", tie it together in a joist bay and drop that down to the basement through a wall cavity? What's the proper method for changing direction from horizontal to vertical, two 1/4 turns(45) or one 1/2 turn(90)?

Once down there it will be tied into the existing 4" stack. I'm hoping to avoid demolishing 100 year old plaster walls. The above assumes I'll be sloping the pipe at 1/4" per foot until I get to the wall.

Thanks so much,

Gil

Comments (6)

  • 16 years ago

    Why can't you drill 2x8s? Doesn't sound like a problem to me.

  • 16 years ago

    Code doesn't allow it. 2" is about 2.37" outside diameter that means you'd have to drill at least a 2.5" hole if not bigger. Seeing as I replaced two broken joists due to large holes I'd rather not deal with that again.

  • 16 years ago

    There are far more important considerations than the holes in the joists.

    First off, code will allow a maximum hole diameter of 2-/8" in a 2x8 joist providing the hole is no closer than 2" from the edge of the joist top or bottom.

    The tub drain is 1-1/2" but code requires the shower arm to be 2".

    Both the tub and shower are rated at 2dfu's therefore the combined load is 4dfu'. Both of those could discharge into a 2" vertical drain line because under the IRC a 2" is rated for up to 10dfu's vertical and under the UPC the maximum is 16dfu's vertical, but you would be required to have a cleanout at the point where the lines transition from horizontal to vertical. Even more important, you would be required to install a vertical vent riser.

    Under the IRC the vent must be within 8ft of the shower trap weir and within 6ft of the tub trap weir.

    Under the UPC the vent must be within 3'6" of the tub trap weir and within 5' of the shower trap weir.

  • 16 years ago

    Lazypup,

    Thanks for sharing your expertise. It's a combined tub/shower unit, so the max would be 2 DFUs right? The vertical vent riser would need to come off the 2" pipe going down to the basement, sort of like a mini stack? Is a cleanout required where the main stack goes from horizontal to vertical? Such as where a toilet is?

    That bathroom is only 96" long by 72 wide, so venting won't be an issue, everything can go up to the attic. Here's a rough sketch of the layout. Tub is the pink square on the left, toilet is on the far right corner. the toilet is standard distance from the walls.

    Thanks again for the feedback,
    Gil

  • 16 years ago

    What's the best way to connect to the 4" cast iron with 3" PVC? There was a fernco coupling there, the type with two hose clamps. I was wondering if it would be better to remove the stub of pipe sticking out and put a fernco donut in? The stub of pipe seems to be in okay shape, just wondering which is better.

    Thanks,
    Gil

  • 16 years ago

    Removing that stub can prove to be very labor intensive and either method are fully code compliant. If the stub is in good shape I would continue to use it.