was wondering if i could get some advice. lights in my house have been dimming occasionally. i took a look in my breaker box (am not an electrician) but i noticed that the top 4 breakers on each side (total 8)are very rusted where the wiring screws into. the remaining 4 breakers (towards the bottom of box are like brand new. i have never replaced any breakers (been here 30 years). what would cause this and can i just have the bad ones replaced?

Comments (22)

  • 18 years ago

    Rust is caused by water. It could be coming from the main wire feed conduit from the meter. It could be from some other water leak.
    If the breakers are rusty then the panel itself is probably in the same condition. Without seeing it I would estimate that a panel change could be in order.

  • 18 years ago

    thank you for the help. any idea how much something like that would cost? have a 100 amp panel and i'm in illinois

  • 18 years ago

    have seen this twice, I took the eclectricians advise and put clear caulk around the main feed off the meter, nothing scaryer then seeing water dripping into your main fuse panel.

  • 18 years ago

    100 amp panel I would guess cost about $1000 - $1500. Just a guess.

  • 18 years ago

    thank you much!!

  • 18 years ago

    Yeah, seen this kinda' water damage before. Thing is, rust you see is more'n likely the tip'a the proverbial you-know-what, and damage to the guts'a the panel, the hot buses, probably lurks beneath. Could be wrong, but I'd bet a pension they're in dreadful condition, and you'll be needin' a new main panel. Cost? Yea, joed's guess is in the 'hood.

  • 18 years ago

    I've found this situation twice. Once, the rusty breaker would not set. The second occasion, the rusty breaker would not turn off or trip!! Both times it was a Square D, Type QO, so normal reliability was not a question. Both times, also, the outside meter was higher the inside panel and there was no dew loop inbetween, so rain and snow melt on the servive entry cable (with deteriorating jacket) was being piped into the back of the CB panel. My remedy was to spiral-wrap the cable with a couple layers of a water and UV resistant tape.

  • 18 years ago

    If a panel replacement is needed and this is not a very small house, you should pay the small increment to put in a bigger service than 100 amps.

  • 18 years ago

    just went thru this at my dads house...randy is probably right...the water is entering from the service cable somehow...it is very bad to have water entering the box.would really suggest that if you can ,remove all breakers that are getting wet,and getting service entrance cable,meter socket,and breaker box replace as soon as possible...

  • 18 years ago

    thank you for all the help. i will be getting estimates. it does appear that there is water/condensation coming from top of breaker box where the wires come in from outside. probably why top breakers are worse than others

  • 18 years ago

    Either the OP did not say or I missed it about where the service entrance comes in. When a service entrance is properly installed above the roof, there is a weather head placed on top of the conduit that will prevent water or moisture coming down. Also, the meter is always placed above the service panel if the panel is outside. Tape and calking is not the answer to an improperly constructed service entrance.

  • 18 years ago

    OK, I gotta ask. How can the contacts on a breaker rust? Rust is caused from iron corrosion, but breaker contacts are copper or aluminum, right? I suppose it is semantics as there is likely aluminum or copper corrosion going on here, but it is not rust - unless it is coming from your steel panel.

    Also, the corrosion is very likely from moisture, but it may be in the form of vapor rather than liquid. The heat in the panel would likely keep the humidity (water vapor) slightly higher in the top portion of the panel.

  • 18 years ago

    upon taking another look at breakers: the screw that holds the wire is rusted and also the part that grabs the wire is corroded to the point that if you tried to back out the screw i'm sure something would break off. tips of wire are white/grey discolor

    service:
    where service comes in (under roof) there is a weather head and service enters the meter box at the top. conduit leaves bottom of meter box and enters basement after a junction box. as it enters basement another junction box
    aims it down to breaker panel (ITE)

    if rain water is coming in it really is traveling far to get there. meter box is old but looks water tight

  • 18 years ago

    in the case of my sisters house, the rain water was coming in at the top of the meter box, would follow inside the sheathing coming out of the bottom of the meter, down into the main panel, where it was dripping down onto the breakers, called an electrician, he said to put clear silicon caulk around the cable on top of the meter box, that was about 3 years ago, no problems sinse. Another electrician/fireman told me this happens quite a bit.

  • 18 years ago

    just like ctbosox sez...the water can get into the slightest crevice,crack,imperfection...I would disagree with buzz that it is just minimal moisture,and heat will evaporate it.....and just like bosox said...ask any electrician..it happens....it took me a while to figure out how it was getting in my dads,but it is a real hazard.........it might seem like a long way for the water to travel,but it is vertical...and it will travel

  • 18 years ago

    Have a qualified person check it out and if it needs changing I believe the minimum code will allow is a 125 amp entrance panel. If you up it to 200 or 225 it will not add much to the cost but will help the resale of your home and allow you to grow your electrical system for many more years.

  • 18 years ago

    thank you everyone for the help

  • 18 years ago

    Cappoll, do you by any chance have aluminum wiring? What you are describing sounds a little like electrolisis. However, that does not explain only part of the breakers being corrided. Just a thought.

  • 18 years ago

    the wires attached to the breakers are copper and corroded.
    the large wires coming from meter box to breaker box are aluminum and clean

  • 18 years ago

    This continues to be a bit of a mystery why some breakers appear corroded and others not. My suggestion would be to replace the bad breakers and steel wool the wire ends. This would be the least costly thing to do. In the mean time you need to do some dectetive work to see where the moisture is coming from.

    If I understand correctly, there is a conduit of some type that comes from the bottom of the meter and into the panel in the basement through two junction boxes. It sounds very much like moisture is following this track as it comes through the foundation. Have you ever noticed any condesation on the inside conduit? These are the only factors I can consieve.

  • 18 years ago

    thank you for the response. I have had an electrician look and will take his suggestion that i replace panel. he believes that cold air is coming in at top of panel and vaporizing as suggested by buzzsaw. this would account for bad condition of top breakers. he says he will seal incoming wires but doesnt think it is a leak

  • 18 years ago

    Well cappoll, how does this electrician propose to eliminate this "vaporizing" by replacing the panel? If he doesn't think there is a leak, why does he propose to seal incoming wires? Sorry, but I don't think replacing the panel is going to solve the problem. IMO, you have a temperation inversion between inside and outside and it is probably causing condensation.