cables entering panel

19 years ago

I wish to bring 6 new NM cables into a panel using the side knockouts, since all knockouts on top have been used. The panel is on a concrete basement wall, fastened to a piece of plywood which is hardly an inch wider than the panel.

My question is regarding NEC requirements for bringing the NM cables into the panel. Do the cables need to be in conduit since they extend down the wall (as for an outlet)?

Also since there is so little plywood extending beyond the sides of the panel, I would have to stack the cables at least three deep. (There will be two 12/2 and four 14/2 cables.)

What's the code compliant way to route these cables?

Comments (6)

  • 19 years ago

    Is it possible to add more plywood of the same thickness to extend the available surface?

  • 19 years ago

    You can generally put two "2-wire" cables in a single typical metallic NM connector.
    Perhaps you can double up on a few in the top?

  • 19 years ago

    I can add plywood, though I was hoping not too since I've already returned the hammer drill I borrowed for use elsewhere in this basement remodel. I can probably manage using a regular drill for just a few tapcons.

    I've seen that conduit is required in unfinished basement areas with outlets. Is conduit required by code when running cables down to the sides of a panel?

  • 19 years ago

    Stapling or otherwise fastening the NM directly to the surface of the masonry wall would be frowned upon by most inspectors, although I have not found a specific mention of this in the code. The conduit offers some protection and is a convenient way that is about as attractive as any low cost method available. Conduit would certainly be permissible for the cables to your panel. If conduit is used, a bushing must be installed at the other end of the conduit to protect the cable from the edges of the conduit. On the surface of plywood surrounding the panel has been accepted by every inspector I have encountered.

  • 19 years ago

    Thank you so much. I will add plywood and secure the cables directly to it.

    I've looked in electrical how-to books, even tried to interpret the 2005 NEC, but couldn't resolve this issue. Ulimately the inspector will decide, but at least I will not do something unheard of.

    I'm really glad to have found this forum.

  • 19 years ago

    As a longtime DIY, one of the shortcuts I've found for determining what's allowed by code - and getting good ideas - is to check out friends' recently built houses. That's where I first saw the use of conduit stubs for bringing several runs of NM into panels, for example. I'd never heard of it until then.

    Careful though - once in a while you'll find some violations in new construction.