Help with wiring for under cabinet light

11 years ago

I will be putting a new under cabinet light in. It is a hard
wired LED light. If I place the light under the cabinet and up against the
wall, can I use the metal base of the light as the junction box? If I mount it away from the wall, do I need
to run the romax thru flex conduit for the 6 inches or so exposed part of the
wire? If so, one end of the conduit would be attached to the light, what about
the other end? Can it just go into the wall cavity (this is remodel work), or
does it need to be attached to the sourcing junction box which I assume would
have to be metal? Any other thought appreciated. I am in unincorporated
Snohomish County Wa.

Comment (1)

  • 11 years ago
    last modified: 11 years ago

    "can I use the metal base of the light as the junction box? "

    Only if the fixture is listed and labeled for such use/ installation.

    "do I need to run the romax thru flex conduit for the 6 inches or so exposed part of the wire?"

    ARTICLE 334 Nonmetallic-Sheathed Cable:

    334.15 Exposed Work. In exposed work, except as provided in 300.11(A), cable shall be installed as specified in 334.15(A) through (C).

    (A) To Follow Surface. Cable shall closely follow the surface of the building finish or of running boards.

    (B) Protection from Physical Damage. Cable shall be protected from physical damage where necessary by rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, or other approved means. Where passing through a floor, the cable shall be enclosed in rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, or other approved means extending at least 150 mm (6 in.) above the floor.

    IMO, the 6" space under the upper cabinet is not an area subject to physical damage, as it is more than 6" off the floor and the cabinets the cable is attached to are usually the equivalent of fine furniture that isn't allowed the slightest scratch, but you should verify with the inspector.

    "one end of the conduit would be attached to the light, what about the other end?"

    300.10 Electrical Continuity of Metal Raceways and Enclosures. Metal raceways, cable armor, and other metal enclosures for conductors shall be metallically joined together into a continuous electrical conductor and shall be connected to all boxes, fittings, and cabinets so as to provide effective electrical continuity. Unless specifically permitted elsewhere in this Code, raceways and cable assemblies shall be mechanically secured to boxes, fittings, cabinets, and other enclosures.

    Exception No. 1: Short sections of raceways used to provide support or protection of cable assemblies from physical damage shall not be required to be made electrically continuous.

    HOWEVER, a bushing or other connector would need to be used on the free end of the conduit in the wall to protect the cable from abrasions where it enters the conduit if it doesn't extend all the way to the next junction box.