NJ New Home Building Permit (Electrical Sub-Section)

10 years ago

Hello everyone.

My husband and I are currently building a new home (owner-builder
and own general contractor) in New Jersey and although my building (footing/framing)
permit was approved and construction is finally underway, my electrical permit
application was returned and construction will halt once we reach the
electrical stage unless I get this electrical subsection approved soon.

The problem with the electrical application is due to having
filled out the voltage in volts
rather than KW of the appliances and
receptacles for which the permit asked information.

The NJ electrical subcode application asks to provide the
following technical site data for
the listed appliances

Qty Size Item

__ ___ KW Electric Range/Receptacle

__ ___ KW Electric Water
Heater (Using Gas)

__ ___ KW Electric
Dryer/Receptacle

__ ___ KW Dishwasher

__ ___ KW Central A/C Unit

I understand that the Qty will be 1 (or 0 in the case of
the electric water heater as I will be using a gas heater) but the other item
(size) I have no idea what how to fill out. I assume they are asking for the KW
number but even researching the appliances I will be using didn’t provide any
info on KW to help me complete the application.

For example, the technical specification for the dishwasher I
will be purchasing states:

Estimated Annual
Electricity Use:
269 kilowatt hours

Amperage: 10 amperes

Voltage: 120
volts


For the Central Air unit 2.5 Ton 30,000 BTU:

Full Load Amperage Requirement (Amps)

30

Full Load Voltage Requirement (Volts)

220

For the Range:

Element Wattage: 3300


If anyone with any previous experience with the electrical permit process has
any idea how these numbers translate to the Size KW as required for the permit,
I would be infinitely grateful for the help.

I am using 200 amp
service, 120/240V and will be using regular appliances.

Comments (5)

  • 10 years ago
    last modified: 10 years ago

    Watts = volts x amps. A 30 amp / 240 central air would be 7,200 watts (30 * 240).

    Watts / Amps calculator

  • 10 years ago
    last modified: 10 years ago

    Well, strictly speaking, Watts = Volts x Amps x Power Factor (which is in a sense the efficiency of the thing being powered). Typically, mechanical loads have a power factor much closer to .8 or lower, whereas consumer electronics come closer to a PF of 1.

    Bottom line, contact your equipment vendor/manufacturer. Do not do the math on this on your own unless you have a realistic way to assess the power factor.

  • 10 years ago

    I wasn't required to do all of these calculations, but I believe that they want to know what the potential total load is on all of these appliances. If you put in appropriate wiring, outlet, and breaker for 30A at 240 volts, then it would be 7200 watts, or 7.2 Kw. (1 Kw = 1000 watts) They have no control over what you plug into it, so they need to know what the circuit is designed to handle.

    Usually, they want to know all of this so that they can be sure that you aren't going to use more power than the system can handle. They don't add up ALL of the breakers, as it is usually way over the capacity of the panel. It's assumed that you won't turn everything on full blast all at once.

    Find out what size circuit these various appliances recommend. Most ranges, for example, are either 40 or 50 amps at 240 volts, or 9.6 or 12 Kw. Most 'normal' sized appliances fall into a fairly standard circuit size. If you're putting in a 12 burner triple oven super range, that's a different story.

  • 10 years ago

    Are you not subcontracting the electrical work to an electrician?

  • 10 years ago
    last modified: 10 years ago

    There is a big difference between total KWH draw and annual usage. Are they trying to ensure that you are not using energy hogs? Don't mix these up. This has nothing to do with current draw. (suppose to). I think they are asking for avg annual usage:

    Like waterheater http://pdf.lowes.com/energyguides/035505156730.pdf

    (find your appliances and supply (total lies) from the manufactures)

    I remember decade ago looking at double oven: draw was 8.4kW/h. Manufacture claimed annual usage 45kwh. Ok - so they really expecting you to use oven 5hours per year, coincidentally - it also took 30min to warm up. Right.