Networking closet Wire guage

9 years ago

So I'm in the middle of turning a spare closet in my house partially into a networking closet. At the moment I currently have a 14" enclosure that will house my router, switch and small patch panel. I would like to make sure I run the correct gauge and breaker to the room.

Now, it seems like no big deal, but I also plan on running some heavy-duty Cisco networking equipment in the closet for a lab environment, which will work off of the same patch panel. This is why I was thinking of running a dedicated 20A for #12.

Here are the things I plan on running in the room.

Cisco 2911

http://www.cisco.com/c/en/us/products/routers/2911-integrated-services-router-isr/index.html

Cisco Catalyst 3650 48 POE

https://www.cdw.com/shop/products/Cisco-Catalyst-3650-48PD-S-switch-48-ports-managed-desktop-rack-mo/3227945.aspx?pfm=srh&expand=TS

Cisco ASA 5505

http://www.cisco.com/c/en/us/support/security/asa-5505-adaptive-security-appliance/model.html

Along with a back-up power unit... which I'm not sure about yet. Probably a 1200W...


I ask because I've done a lot of low-voltage, but I have NEVER done high voltage wiring and didn't want to do anything stupid. The equipment that I have is extremely expensive and I would kick myself if I were to fry them. I couldn't care less about my 150 router and switch for normal use.

Comments (4)

  • 9 years ago

    The basic process is to add up the power requirements of the devices that will be on the circuit and then size the circuit appropriately. Typically you don't want to exceed 80% of the circuit's capacity, which for a 20 amp circuit would be 16 amps or 1920 watts (watts = amps x voltage) because I think this would be considered a "continuous load" because these devices would be on 24/7. Just very quickly looking through Cisco's site I didn't see anything about the power requirements but I'm sure it's there.

    The only real difference in running a 20 amp circuit vs. a 15 amp is the cost of the wire. Around here 12/2 NM-B (aka Romex) is about 60% more expensive than 14/2. Assuming a 50 ft. run, that would be about $11.

  • 9 years ago

    Routers and hubs are pretty low power consumers these days (this is a far cry from 25 years ago when the initial Cisco routers we had used a few amps just to run the giant blower they had that kept the thing from melting down). 15A probably would suffice, but as Mike alludes, the cabling price difference is going to be minimal in the scope of things. I'd run 12-2 and put in a 20A circuit.

  • 9 years ago

    I think from a power standpoint, you're talking about 2-4 amps for each unit, and maybe a bit less depending on load.

    I think, since you're talking about a closet, your main issue will be ventilation. You'll need to keep the temperature below 90F, preferably around 75F.

  • 9 years ago

    Yes, I agree. The ventilation is def. going to be the main concern with an enclosed area, but I have worked with TC closets before, so no real advise needed in that category. The power I'm just not sure about because I've never done it. So General consensus is my original plan of 20A breaker on 12 gauge wire?