Mini-split system for a restaurant?

9 years ago

Here is what we have: we bought a pizza restaurant and found that it is missing the central air units from the roof. What we were told by the contractor who found it is that he thinks we require (2) 5 ton units. I would like confirmation if this would be suitable or not. We are in the Atlanta metro area, the overall square footage of the restaurant is about 1300 square feet, the kitchen takes about 1/3 of that with (2) ovens operating at 500*. The hood fan was replaced and working properly, but temps in the kitchen on a 60* day generally remain around 80*-85*, occasionally higher. I am no HVAC professional, so I have been researching the 'net the best I can to find as much info as possible and what I find is for the size space we have would require about a 3 ton unit. Here is where my question comes in. I have been searching different options as we don't have a lot of money left to replace the AC and come across this mini-split. Would this be a feasible alternative, or should I look elsewhere? In my head, I think the "big" unit could go in the kitchen and the 2 "small" units could go in the dining area. Thanks for any help!!

http://www.thermospace.com/ductless_split/acd9918-tri-zone-36000-btu-9k+9k+18k.php


We have had a number of different quotes ranging from $17k-$30k+ for replacement and unfortunately we are not in a position to afford these numbers.

Comments (6)

  • 9 years ago

    A 3 ton condenser would be the right size for a 1300 sq foot house in Atlanta. It is undersized for restaurant with a commercial kitchen.

    You need to find a contractor who knows how to do a load calculation. This requires specialized software which calculates how many BTUs are produced in your restaurant on a typical summer day when the restaurant is full of people and the stove and ovens are going full blast. Don't waste your time and money on a contractor who guesses on the AC sizes. You want a copy of the report and have it explained to you. You may have to pay for this service but it will be worth the money.

    Once you figure out what is needed then you can decide how much money you are going to invest. If it were my restaurant I would spend the money first on keeping the customers cool and comfortable.

    vitos_marietta thanked mike_home
  • 9 years ago

    Thank you both and I/we agree wholeheartedly with keeping customers comfortable and happy. The problem we ran into was multi-layered here, but long story short it is draining us financially. We learned too late that the AC just wasn't there. So many pieces of equipment failed as a result of working against the heavy load of the hot kitchen that they needed to be replaced just to pass health inspection. We are fortunate enough to be located within a mile of the new Suntrust Park, so we are hopeful that delivery orders will get us through for the time being. And thank you for the suggestion of leasing the HVAC equipment, I hadn't thought of it that way yet. I will start researching this option to see what can be done.

  • PRO
    9 years ago
    last modified: 9 years ago

    The delivery orders is a smart move... another idea: print up a flyer and attach it to every delivery order with a statement about your situation set up a 'go fund me' page --- people love a good 'true' story. Ask your customers if they 'love' the pizza to help you with the cooling needs of your restaurant.

    Then concentrate on making the best pie you can make and best delivery service, no matter how hot it gets in that kitchen this summer.

  • 9 years ago
    last modified: 9 years ago

    You can cut the AC size with ERV (eg: Renewaire) for makeup air. Also see if you can separate the kitchen so they are at a higher temperature zone compare to the customer zone. You need to deal with commercial contractors that specialize in restaurants.

  • PRO
    9 years ago
    last modified: 9 years ago

    No I would not cut AC sizing for a restaurant with a hot kitchen and varying people loads throughout the year. You are asking for trouble if you do this.

    If a HVAC contractor offers anything like this to cut AC sizing, find a new HVAC contractor.

    In order for the Return temperature of 75 degrees (in the picture) to be what it is, the AC must be properly sized. Realize a hot kitchen is how hot? Take a temperature reading... this is your 'ACTUAL' return temperature.