Cracked beam in framing

8 years ago

I am concerned about a cracked beam. The contractor says he spoke with the structural engineer and is going to laminate it. The crack stretches the entire length. Should I be concerned? The roof should go on this week. Thank you!!!








Comments (42)

  • 8 years ago

    If I were you, I'd speak to your own structural engineer.

    rockybird thanked cpartist
  • 8 years ago
    last modified: 8 years ago

    Thanks cpartist. I think I will ask him to get it in writing from the structural engineer.

  • 8 years ago
    last modified: 8 years ago

    It effectively reduces the width of that piece below what's necessary. So you'll need to laminate and have the proper fastener spacing to beef it back up. Brace it while doing that.

    rockybird thanked dan1888
  • PRO
    8 years ago

    The framing looks botched up and done by a bunch of amateurs, not to mention it will not pass framing inspection.

    When joist hangers being used, floor joist should be attached to a double girder, not a single joist like you have it there.

    "When the header joist span exceeds 4 feet (1219 mm), the trimmer joists and the header joist shall be doubled and of sufficient cross section to support the floor joists framing into the header. Approved hangers shall be used for the header joist to trimmer joist connections when the header joist span exceeds 6 feet (1829 mm)."

    I guess they used pieces of OSB to repair cracked joist but this sort of repair is not doing anything.

    I would call an independent structural engineer and have him evaluate everything, because if they don't know basic framing methods, who knows what they did when it comes to structural components.

    Good luck.


    rockybird thanked GN Builders L.L.C
  • 8 years ago
    last modified: 8 years ago

    It might be OK since the crack is close to the center of the beam and the load is only on one side. The design engineer of record should be who determines that. If its not adequate for the load and/or if it needs to be stabilized, that might be possible from the back side involving thru-bolting. That might be what is meant by "laminate it."

    This problem is usually avoided by using more stable Laminated Veneer Lumber (LVL) beams. Notice that the crack occurs at the top of the joist hangers. I suspect the crack was caused by the lack of blocking on the back side of the beam to resist twisting from the imbalanced load. Check the drawings to see if blocking was required but omitted.

    rockybird thanked User
  • 8 years ago
    last modified: 8 years ago

    This is all new construction I’m looking at? If so, I wouldn’t be satisfied with what appears to be the “cobbled-togetherness” of it. I’d be asking TONS of questions, but I’d really want to know about the 2 x 4s on top of the 2 x 10s (reason for, attachment method, etc.) and if it’s okay that the joist hangers aren’t tall enough to accommodate both pieces. It could be perfectly normal/acceptable, but I’d just need to understand the hows and whys of it.

    ETA: I didn’t see the comments made by GN Builders and JDS until after I hit “Submit.”

    rockybird thanked Sammy
  • 8 years ago
    last modified: 8 years ago

    Thank you everyone! I know nothing about framing...what is a double header?

    The framing passed inspection. The architect had no issues with it. He was out here a week ago. Also, I had two independent contractors look at it. I dont think they thought it was the best job, but they didnt point out glaring issues, but I am concerned reading your comments!

    Sammy, it is all new construction.

    But I am really concerned reading your comments.

    Here is the framing diagram:

    Adding: THe roof is being sprayed on Wed.

  • PRO
    8 years ago

    but I’d really want to know about the 2 x 4s on top of the 2 x 10s (reason for, attachment method, etc.

    I guess they used pieces of OSB to repair cracked joist but this sort of repair is not doing anything.

    The top 2x is tapered forming the slope for the roof deck.

    rockybird thanked PPF.
  • 8 years ago
    last modified: 8 years ago

    I assume the sleepers on top of the roof joists provide the necessary slope for the "flat roof". Perhaps the OSB squares secure the sleepers to the joists saving the cost of nailing plates.

    Oops, I need to type faster.

    rockybird thanked User
  • 8 years ago

    I sent an email asking if he could replace the beam or provide written documentation from structural engineer. Do you think that sounds okay? I am also worried about termites getting in the wood.

  • 8 years ago
    last modified: 8 years ago

    Double header would be two of what you have at this point. The one you have is cracked.

    rockybird thanked dan1888
  • 8 years ago

    The contractor is going to have the structural engineer come out and write a report ascertaining that laminating it to OSB should be fine. I think I'm okay with that. What do you all think?

  • PRO
    8 years ago

    It looks like every joist along the floor pan has a crack in it and some areas along the crack show signs of being displacement. I don't know what caused this or the lumber they used is a utility grade lumber...

    If this is going to be fixed, I would sister-up all the joist along the span and if they decide to laminate, whatever they use should be glued and bolted through on both sides of each joist since you have to meet a certain design load for the entire floor. I would bring your own engineer to make sure he will look out for your interest because if these repairs are done the wrong way, you will end up with squeaky floors or worst.

    Good luck.

    rockybird thanked GN Builders L.L.C
  • 8 years ago

    Thank GN builders. This is the roof. There is no upstairs, just a one story building. Does that make a difference?

  • 8 years ago

    The roof joists are fine; they have tapered sleepers on top to allow the roof sheathing to slope.

    rockybird thanked User
  • 8 years ago

    If this was new construction, I would ask for a redo, and maybe add blocking to the joists. The third photo looks to have a split joist.

    rockybird thanked strategery
  • 8 years ago
    last modified: 8 years ago

    The third photo shows a tapered sleeper on top of each roof joist. There are no split joists in the photos. the pieces of OSB secure the sleepers to the joists.

  • 8 years ago

    Look at the joist on the other side of the support.

  • 8 years ago
    last modified: 8 years ago

    That looks like damage in handling or installation and not a structural issue.

  • PRO
    8 years ago

    When the lumber was delivered did they dropped the entire load from a helicopter? I have never seen so many damaged pieces of lumber in over 30 yrs being in the construction industry and the majority of that time I spent around framing. You get a "checked" piece here and there and the guys wouldn't use it, they would use what they can for blocking.

    Around here this would never pass framing inspection, not with so many damaged pieces.


    rockybird thanked GN Builders L.L.C
  • 8 years ago
    last modified: 8 years ago

    I'm believe the split in the beam didn't occur until it was in place and is easily repaired or replaced at the direction of the engineer. One damaged joist edge doesn't warrant such alarmist comments. Rockybird needs to concentrate on more important issues.

    rockybird thanked User
  • PRO
    8 years ago

    It sounds like from what the general contractor says, you should not worry. If the general contractor gives you hard hats to wear while in the house, you should worry.

    rockybird thanked Mark Bischak, Architect
  • 8 years ago

    Sleepers! Thanks for teaching me something new today, guys!

    rockybird thanked Sammy
  • 8 years ago

    You guys are all great!! Thank you for all the comments!!! :)

  • PRO
    8 years ago

    I predict the drywall finish on that ceiling will be delightful. Not.

    Casey

  • 8 years ago

    Good point. Rocky, be sure to use leveled strapping to support the ceiling finish. Its standard in my area but I have heard rumors that drywall is attached directly to joist in some parts of the world.

  • PRO
    8 years ago

    I worked as an architect at a large hospital years ago. One of the buildings we constructed had a myriad of random mechanical penetrations (HVAC grills, speakers, sprinkler heads, access panels, etc.) in the ceiling of the main entry. The Associate Hospital Director (AHD) gave an architect coworker of mine the task of making the ceiling look good without moving any of the penetrations. She came up with a brilliant solution that was influenced by a Pieter Cornelis "Piet" Mondriaan painting. When seeing the design implemented, the AHD said, "This is great, unfortunately nobody will probably notice it."

  • 8 years ago
    last modified: 8 years ago

    rockybird- In your contract with your builder, did you agree to pay for new materials, or "like new"? I'd be concerned about all the damaged boards, cracked beams, laminating for a quick fix.

    If he's willing to give you "rigged up" beams, stay with damaged boards that will never show (unless they become a problem), what do you think the rest of the build will be like?

    I realize you passed inspections. In some areas, it's a fairly low bar. I see that your architect and structural engineer also say "no problem". I'd be very concerned about these sorts of pros signing off on cracked beams and all that damage. Especially the architect, who presumably designed it all, even to specs of this sort of material, in consultation with your GC.

    Bottom line is back to the beginning: What, exactly are you contracted out for? Did you set out to have damaged materials in your structure? I'd hit the brakes, until and unless you get what you've asked for/agreed to pay. Make your mark, now- before you're given other "not so great but we can rig it".

  • 8 years ago

    @JDS - "I have heard rumors that drywall is attached directly to joist in some parts of the world".

    For sure. Common in Ontario and BC.


  • 8 years ago
    last modified: 8 years ago

    There is no reason to assume the structure is deficient or needs to be replaced just from the photos rocky posted and if it passed the engineer's inspection, it is fine.

    The split beam is the same size as the beam at the other end of the joists it supports but the split beam is only loaded on one side by shorter joists so it carries about 1/3 of the load of the other same size beam. Even if the split reduced the depth of the beam by 1/4, it should still be adequate to carry the load.

    As for damage to the joists, I can only see one place where a piece of a bottom edge is damaged. Here again, all of the joists are the same size but the span of the damaged joist is about 40% shorter than that of the longest joist. The damaged joist could be 2" shorter and still be structurally adequate.

    The only complaint I have is the lack of blocking but it may be added later. Rocky, you should ask about it.

  • PRO
    8 years ago

    Get paper from the Engineer who approved this in writing with Engineering stamp on it and keep it for your records.

    If you end up selling the house in the future this will be picked during the home inspection and inspector will note that a structural engineer should evaluate this... You will have to pay to have this evaluated and this time it will come out of your pocket, having that stamped paper in writing will save you some money and grief.

    Good luck

  • 8 years ago

    If I'm house shopping and the seller says "Oh, don't worry about that massive crack in the beam, here's a piece of paper which says an engineer ok-ed it", I'm going elsewhere.

  • PRO
    8 years ago

    Some engineers will say anything to help someone out, but when asked for a sealed letter saying nothing to worry and that the current condition of "whatever is in question", 95% will not attach their name to it until their suggested repair is completed.

  • 8 years ago

    I've never seen a home inspector remove sheet rock to inspect the framing. You learn something new everyday, or do you...?

  • 8 years ago
    last modified: 8 years ago

    Cracks in solid wood floor joists and beams are not uncommon. Some do not even matter much.

    This is especially true of ones that are the result of the natural drying process of the wood. These “checks” as they are called, are especially common in larger timbers---like the 6x6 support posts you might see in your basement or at other support locations. This solid wood 4x10 beam has a large check right in the center over the length of the picture.

    These checks are rarely an issue structurally, in fact they are quite impossible to eliminate entirely. Checks like this are rarely very deep. They are as “to be expected” as shrinkage cracking of concrete floors.

    Source: Charles Buell Inspections Inc.

  • 8 years ago
    last modified: 8 years ago

    Cracks in Large Timbers: What Can You Do To Prevent Them? Pt 1

    NOVEMBER 17, 2015 BY SOZO STAFF

    First, the bad news: Cracks in large timbers can’t completely be prevented. Ready for some good news? You may think you want to prevent them, but you really don’t. While factors such as direct sunlight and highly fluctuating moisture levels may increase incidence and severity of checking and cracking, they will occur regardless of exposure to the elements. Basically, they’re just part of the deal when it comes to large pieces of wood.

    Why is that? In 4/4 to 10/4 lumber, drying occurs easily and fairly homogeneously. However, thicker boards such as 12/4 or timbers that are 6×6 or even 12×12 comprise a cross section of the original log, causing it to act more like a log than a typical board.

    Because the center of the timber is surrounded by such a significant amount of insulation, it retains moisture longer than the outer layers do. As those outer layers dry, they naturally begin to shrink, only to be stopped by the inner layer, which is still quite moist. The only response they can have is to crack. This checking is actually a healthy response to pressure. If you see a large timber with no such cracks, then you should begin to worry: a rotten core may be the cause.

    While a large timber of any species will check, the way they check will vary based on species. For instance, a dense, heavy wood such as Ipe lacks the empty space between wood fibers, so it will typically check more readily than, say, one made from Douglas Fir. Because of the stability of Ipe, the checks will be numerous but will also be relatively small and fairly shallow.

    By contrast, Firs often have far fewer checks, but they are deep and wide, appearing similar to an explosive crack. What happens with such a species is that the timber shrinks and compresses into the empty space. The pressure continues to build up until the fibers finally have no other recourse but to give way.

    End grain of beams

    Source: MARKETINA

  • 8 years ago
    last modified: 8 years ago

    I have seen this often in existing structures but heavy timber is expensive and hard to find in New England so for new structures I use LVL (laminated veneer lumber).

  • PRO
    8 years ago
    last modified: 8 years ago

    The split in the ridge that the original poster provided cannot be compared to lumber used in post and beam construction or log homes that you show images of.

    The images you show cut from a different part of the tree and have a different grain pattern and most of the time these splits or cracks found in the wooden posts or logs are due to shrinkage as the wood dries and in most situations, it's not a structural concern.

    You dealing with conventional lumber and the grain pattern is different, when a joist has a split along the entire span the structural integrity of that joist is reduced by half and no framer will use a joist which is cracked/checked (or call it what you want ) along the entire span, especially when you dealing with girders or roof ridges.

  • PRO
    8 years ago

    I'd like to know what beam "B-2" is called out to be on the drawings. In the photo, it appears to simply be another 2X member, slightly larger that the 2X joists with the flat 2X on top for the roof slope.

    I always thought headers, trimmers and "beams" using 2X stock were to be doubled, which this "beam" is not...

  • 8 years ago
    last modified: 8 years ago

    The beam in question is not a joist; its a 4x10

    The width of the 2x4 top plate beyond makes that clear.

    rockybird thanked User
  • 8 years ago
    last modified: 8 years ago

    I wanted to post an update on the framing. I had a structural engineer look at all the framing this AM. He stated there are no issues. The framing looks great. The blocking is more than adequate. The cracked beam is not an issue. It is not cracked completely through. The crack probably occurred from exposure. He said laminating it to OSB is fine. He is not worried about it at all. The contractor is having another structural eng. review it next week (he doesnt know about the one that was out today). I feel much better now!