johnnybees

Fresh Air for Boiler Room Combustion

5 years ago

My house is a new build and is very tight. We recently had a CO scare. The hot water tank was heating and we had the kitchen vent on. My CO alarms went off and when i went into the Boiler Room i noticed it was warm, which is normal, but also very humid which told me either the Boiler or Hot Water tank were not exhausting properly. I was able to diagnose that it was the Hot Water tank that ends up dumping most of its exhaust into the room when the kitchen vent is running. The vent ,even at low speeds, runs at 300-400 cfm so it quickly removes the air from the house and since its tight it doesnt get replaced fast enough and causes negative pressure which then allowed the Hot Water tank exhaust to come out the side instead of going up into the duct.


I know they make dampers that open and close when wired to a boiler, but do they make ones that open and close when wired to both a boiler and hot water tank. The easy answer would be to wire only the hot water tank to the damper since it seemed like it was the culprit but i'd rather not take a chance and would want the damper opened when either or both are running. Is this possible?

Comments (10)

  • 5 years ago

    Does the boiler room have a window? If so, have you tried opening it (maybe just a little)?

  • 5 years ago

    No windows.

  • 5 years ago

    If you have tight construction you should be using gas appliances with outside air intake. An atmospheric vent gas water heater is a bad idea.

    Your furnace / boiler should have an outside air intake and an atmospheric vent water heater shouldn't be a thing in your situation.


    That said, install a damper that opens on negative pressure to avoid the back draft situation that you just had. If this is a NEW house, get the builder to fix it.


  • 5 years ago

    There is a lot of information missing, like the total BTUs, the size of room, HRV/ERV, louvered door, perimtting, etc. But if this is a new build and the mechanical room does not meet volume of air, and there is no additional outside combustion, ventilation, and dilution air then it has not been built to code. You should go back to the builder immediately. Also, if you have replaced a <400cfm range hood with one >400cfm, that introduces make-up air requirements beyond the gas-fired appliance requirements.

  • 5 years ago

    Jake The Wonderdog

    The issue is the boiler and hot water heater were already existing and where fine because the house was old and not tight. I did a complete reno but left that room as is but now the house is tight. We havent had issues until we finally had a scenario where we were cooking and using the kitchen vent at the same time the Hot Water Tank was heating.

    What negative pressure damper would you recommend?


    3onthetree

    Room is 11'x6'.

    Boiler input = 105k BTU

    Hot Water Tank input = 40k BTU

    Door isnt louvered.

    We have an ERV buts its not running yet.

  • 5 years ago

    So this is a remodel, not a new build. Were there openings in the mechanical room, like into the attic or crawlspace, that you covered up during your reno? Gas appliances require combustion air whether the house is old and leaky or not. And did you install a range hood exhausting more than 400cfm or not?

    Be clear that there are 3 separate issues here: 1) It sounds like you have no combustion air for the boiler or water heater; 2) the range hood is interfering with the operation of those gas appliances; 3) you have a "tight" house.

    All need to be solved:

    3.) ERV is for the "tight" construction, requiring fresh air just for occupancy (IRC 303.4/M1505.4.3)

    2.) Your range hood, if under 400cfm, is creating a backdraft either because placement near the mech room or whatever, requires makeup air (IRC G2407.4). If it is over 400cfm, it requires makeup air (IRC M1503.6). So either way a damper to operate when range hood exhausts.

    1.) Your mech room provides ~528cuft of indoor air and gas appliances require ~7250cuft. If you cannot provide permanent openings for indoor/outdoor air, then a mechanical damper must be interlocked to both boiler and water heater to provide >51cfm of outdoor air (IRC G2407.9)



  • 5 years ago

    The building code requires a make up air system must be installed for range hoods that operate about 400 CFM. This will solve the negative pressure problem.

  • 5 years ago

    3onthetree

    Mechanical room didnt have openings prior.

    Yes, we installed the range hood.


    Can all dampers be wired to both the hot water tank and the boiler?

    If i have a damper that opens when either or both are running then i dont need any make up for the range hood right?

  • 5 years ago

    First, if the hood is >400cfm makeup air is required with any fuel burning appliance in the house anywhere, period. I don't see anything in IRC that exempts requirements for makeup air if even one is locked from operating while another is being used. IRC just pulls verbatim from IMC, but I doubt IMC would have anything additional like that.

    I have seen the combustion air damper and fail-safe wired to multiple appliances, however the nuts and bolts of how to do it are beyond my pay grade.

  • 5 years ago

    I either want one that operates when either one is operating or one that operates when there's a pressure drop. You know if the pressure ones work well?