Oh NO! Thermador range hood installed and it's SOOO loud.

17 years ago

I posted about this on Kitchens but hoping for some input here from the appliance pros! We're really crushed as we're nearing the end of a grueling kitchen reno, and getting our hood installed was supposed to be a celebration. Instead it is a big disppointment!

We just installed a Thermador H30HQS hood with integral VTN600Q motor (600 CFM). The installation is very clean, with just one 90 elbow and then 5 feet of rigid ducting to roof cap. Well-secured.

The noise is atrocious!!! I know we will never turn it on for normal cooking as it is now.

We did some more research and we think there's clearly a problem.

On this forum we found a great vent blower overview that states that the majority of the sound from the hood should be airflow, and the secondary component of the sound is the motor.

In our case the majority of the sound seems to be from the motor.

1) The ducting installation is good, shouldn't be an issue.

2) We turned the blower on BEFORE any ducting was installed or filters in place. The sound was atrocious. After ducting hooked up and filters in place, sound was exactly the same. It seems in a normal situation, the increased airflow resistance of ducting and filters should have INCREASED the noise level. On this case it did not. Is it possible the sound is simply airflow over the ventilator motor's blades? (It is a dual-blower model.)

3) Even on the lowest setting, you can feel the floor and cabinetry around the range vibrating slightly. On high the vibrations are easy to feel. That doesn't seem right.

4) I cannot find noise level specs for our model (discontinued model). But other hood manufacturers and even other Thermador models have specs such as 2.0 sones to 6.5 sones, low-high. Where one sone is roughly the equivalent of a refrigerator, 4 is normal conversation, 8 is city traffic. Although of course it's subjective without a meter of some sort, I would say we've got about 6+ at low and likely well over 8 at high. At lowest speed, you have to significantly raise your voice to speak to someone. I cannot hear what people are saying (in normal voices) 6 feet away. At high speed, it's like being on a subway platform when a train goes by!

It seems like maybe it's actually a problem with the motor itself....????? What do you think?

I am going to call Thermador tomorrow. I really hope they will honor the warranty and send someone out to look at it!

The hood was purchased from a local appliance store but the motor was ordered on line. As noted both are discontinued but should still be under warranty, no?

If all else fails, we might consider cutting our losses on the motor and getting a remote blower to use with the existing hood. Perhaps that would help. ???

Comments (5)

  • 17 years ago

    If the fan is bent or otherwise unbalanced, there will be a vibration. My fan is balanced with clips attached around the circumference. I have a thermador with the 1000 CFM fan, and believe me, I know when it's on, but it's 25% motor, 75% air rushing.
    Casey

  • 17 years ago

    Thanks-
    It's definitely mostly motor noise. Weirdly, the motor had two brackets (one at each open end of the dual blower motors) and my DH -who is a mechanic and marine systems tech- didn't believe me when I told him that the instructions said to remove them. He assumed they were to balance the fan blades. But the instructions and attached tags clearly stated that they were shipping brackets, so they were removed.

    Anyway- A repair guy is coming to look at it tomorrow, so we'll see what he says. I just can't believe this amount of noise is normal.

  • 10 years ago

    I have the same issue with a Thermador fan. What was your solution?

  • 9 years ago

    I know this thread is old, but Stacey Collins or stephschwab - any updates? Thanks!

  • 9 years ago

    Ideally, the loudest noise should be the blade tip turbulence from the blower fan blades. This can be reduced at the cook station where space permits by using a remote blower and in-line silencer.

    The second loudest noise should be hiss from turbulence around the baffles. This cannot be helped, but may vary with baffle design.

    Unfortunately, in some cases the loudest noise is from an unbalanced motor-fan assembly, and/or insufficient isolation of motor vibration from the house and from the ducting. This type of noise can be easily carried via the ducts. (Of course, a blower in the hood is not isolated at all except by its mounts, and needs to be well balanced.

    Duct noise proper due to turbulence in the ducts (and here I will include interior hood turbulence at all sectional area transitions), when the duct is properly sized for air speeds in the 1000 - 2000 ft/min range, can compete with, but shouldn't dominate the baffle noise unless the duct path is particularly tortuous.

    Where one is stuck with a particular motor-fan assembly that appears unbalanced, use of an industrial balancing shop to correct the problem may be appropriate.