need help!!! high limit switch indicator

17 years ago

backgroud- I have a 1993 model Comfortmaker furance model#GU100a016ain that runs for about 15-30 miuntes then goes out and furnace indicator light signals that the high limit switch is opened and then system locks itself out from trying to restart, all while never reaching the set temperature. Sometimes it works for serveal days then as soon as the outside temp. gets cold, the problem returns. I have had a HVAC techican look at it several times and all seem to come up with a different reason why it keeps going off and on, but none can fix the problem. I have replaced the control module board,flame ignitor,high limit switch,sereval thermostats=now using reg. mercury stat.,checked and cleaned coils, & replaced the low voltage wiring, in which the first problem came from,were the system was saying not calling for heat, when it really was showing calling for heat.

Comments (5)

  • 17 years ago

    High limit switches are usually very reliable. Dollars to donuts the furnace is overheating and shutting off for a reason.

    That's not unusual when furnaces run for lengthy periods of time in cold weather, since that lengthy run gives the furnace time to overheat. The usual cause of that is reduced airflow through the furnace, caused by a dirty air filter, covered up air return grate, too many warm air vents closed, fan speed set too low, overfired furnace, duct work undersized or other causes.

    Usually such problems are pretty easy to diagnose and correct --- the problem is diagnosed by putting a thermometer in the warm air ductwork coming from the furnace and vrifying that the furnace shuts off at the temperature specified by the limit switch (which is calibrated in degrees).

    Replacing all those parts was probably a waste.

    You need to verify that the limit switch is opening because the furnace is overheating and then determine the cause of that problem.

  • 17 years ago

    Wow, I just opened 8 of the 18 warm air vents in my house which is a 3 level home and I usually close all the basement vents all the time. do I need to still check the warm air ductwork temperature, and if so, just where is that? Close by the furnace or will any of the 18 vents due? and how many degrees should a normal system be, and how do you adjust it?

  • 17 years ago

    I was told that there were some heat exchanger problems with that vintage ICP for the Confortmaker models made 1992-1995?

  • 17 years ago

    Did opening the warm air vents allow the house to heat up properly?

    Measure the warm air temperature as close to the furnace as convenient. But to know the temperatire the limit switch shut off at, you would have to locate that switch in the furnace. It would specify the temperature at which it opens up.

    As to heat exchanger, going on probabilities does you no good. You need to find an honest and competent repair service to inspect it. Unfortunately, too many repairmen can see a couple of hundred dollars in your heat exchanger if they find a crack in it, which can influence what they find.

  • 17 years ago

    I believe that model has a condenstate sensor that would fail. Being that it is wired in series with the limits and rollouts and trips the limit circuit, many techs didn't check them.

    There was a upgrade but at this time may not be available. many were just bypassed. Look for a switch with wires in the lower bottom right hand corner.