what could be wrong

19 years ago

We've had an electrician do most of our big renovation but we are slowly finishing up our basement bathroom on our own. We are doing as he suggested using the first outlet which was existing before the reno.

{{!gwi}}

Today we hooked up all the wiring and nothing worked except for the first existing outlet which we have changed out to a gfi....I finally got the second outlet to work when I switched the first gfi outlet to a regular outlet. I have one of those plug-in testers and both show up wired as "correct".

Now I have two working outlets but it seems there is no power going to the 3gangbox. Last week my electrician quickly had a look at the 3 gangbox and said it was all wired correctly.

Am I doing something wrong? I know I have to put a gfi back in that first outlet....so any idea why did not continue the power?

Comments (7)

  • 19 years ago

    To state the obvious, you have a problem with your wiring. You should have black to black, white to white, etc. You need to give more details on what you have done before any suggestions can be offered here.

  • 19 years ago

    Sounds like line-load reversal on the GFCI receptacle.
    The new ones are desined to prevent operation if fed power from the load screws.

    The power coming into the GFCI MUST be conencted to the LINE screws.
    The power to the rest of the circuit is connected to the LOAD screws.

  • 19 years ago

    Thanks guys, we did alot of basement wiring and I thought this would be pretty straight forward.... I really don't want to call my electrician back in cause he's a bit of an idiot.

    Here is a more detailed picture...I hope it's not too confusing and that I got it all correct (my brain is about to explode)...for the sake of it showing up I made the white wire the pink line (yes I am a girl).

    {{!gwi}}

    brickeyee the gfci was working. It was the second outlet that didn't seem to be getting power until I switched the gfci to a regular outlet. I tried switching the wires to the top screws, then bottom screws. The switches are well marked... one side "Hot" and the other "white"...which I followed.

  • 19 years ago

    I think what Brickeyee was trying to point out is that the GFCI has "power in" connectors for the black and white wires, and "power out" connectors for the black and white wires. "Power in" is marked "line" on the GFCI, and connects to the power box. "Power out" is marked "load" on the GFCI and connects to downstream devices. If you reverse the load and line, the device won't work. Your wiring diagrams look just fine.

  • 19 years ago

    Check all connections on the receptacles (don't use any backstab connectors, only screws) and your wirenutted connection, and check to make sure the tab between the screws (both sides) on the receptacles is intact. If someone had broken the tab to make a split receptacle, you would not have power available for any downstream wiring.

  • 19 years ago

    The new GFCIs will not feed power back to the line screws from the load screws.
    Many got installed backwards like this and only the GFCI receptacle itself was protected. None of the donwstream outlets had GFCI protection.
    To prevent this error, the design of the GFCI receptacles was modified to prevent them from being wired inciorectly.
    If you connect power to the load terminals, and other downstream devices to the line terminals, there will not be any power donwstream.
    This sounds exaclty like the symptoms you described.
    Power to the GFCI and nothing downstream.

  • 19 years ago

    Thankyou everyone...well...we took apart the 3 gang box and started anew and now everything works! Something must have not been connected properly.

    I will enjoy my lights and fan for tonight and tomorrow will try to change the first receptacle back to the gfci with what brickeyee said in mind.

    It's also nice to know that we wired it correctly.