Main Panel in Utility Closet

19 years ago

All,

I am having my basement refinished as close to code as possible. The main panel sits above the sump pump. The panel meets the 30" width requirement and has about 34.5-35" clearance in front.

We have built a closet around the sump pump and main panel. According to my understanding of the code we come very close (except for being off by about an inch in terms of front clearance.

Does that sound right?

Thanks,

Andrew in DC

Comments (3)

  • 19 years ago

    No, it doesn't.

    In the NEC 2005, I can find where it says that a minimum clear distance of 36" is required in front of the panel (Table 110.26(A)(1). That includes the floor space which, if I understand you correctly, includes a sump pump in your case.

    No offense, but my inspector would laugh at me if I asked him to okay an install such as this. In my opinion, this alone is enough to fail the inspection.

    Another thing - coming "very close" to code is not the same as "in compliance" to code. In my location, a inspector will grant a written variance from the code in very few instances and never because it would be too much work or involve too much expense to bring up to code.

  • 19 years ago

    Doc,
    Thanks for the response. I assumed that people would scoff at my question but I needed the information regardless.

    The problem is that it is hard to get simple code information that I can understand online.

    So, please explain to me the implications of the sump pump. The panel is on the wall, about 3 feet off the ground. The sump sits in front of it and does not produce above the floor. If, by chance, the bottom of the panel is 36 inches or more above the floor, doesn't that work?

    I understand about the "almost"/"very close." The closet abuts a door so I am not sure how I can get the extra inch but will talk with the contractor about this.

    We understood the risks about not pulling a permit but felt that the cost/benefit wasn't worth it as our house is old and has enough issues that our permit could be denied...for instance, the minimum ceiling height is about 1 inch too low. I just want to do the best that we can...and am prepared for the scoffs, as I said.

    Thanks again.

  • 19 years ago

    Imagine a box 30" x 36" by 6'6" sitting on the floor directly in front of the panel. NOTHING can be inside that box area. The sump pump if it has a cover flush with the floor suitable for standing on top of might be OK. Normally it not OK for the sump pump to be in front of the panel.
    The panel does not have to centered on the 30" space. It can be to one side or the other. If the panel happens to be wider than 30" then the space must be the width of the panel.