sniffdog

Pre-wire for Generator - Will it Save$

19 years ago

In construction phase now - will have a power generator to run critical circuits in the future. I had a 100 amp sub-panel put in, and all critical ciruits will be fed through this sub-panel. All of the feeds have been home run, but nothing has been tied into the panels yet.

The electrician recommended that I have a transfer switch wired in now - will save me time and money down the road. Cost for the switch is around $600, I am not sure about the labor.

Would like to hear from an electrician if this makes sense. I won't be putting the generator in for 6 months or so, and am in a budget crunch right now. Should I wire the Xfer switch in now? Will it save me money?

Thanks

Comments (11)

  • 19 years ago

    I have a 320 amp service to my home and have 2 Square D 200 amp main panels, one in the basement and one in the garage. Instead of a separate generator panel, I opted for a main breaker interlock between the garage main and the generator backfeed breaker into the garage panel. So my generator has a dedicated outlet wired into the panel with 10/3. All the circuits that would need to be run on the generator were brought to this panel. The generator interlock meets the intent of the code, although many electricians frown on them. Maybe that's because they can't charge 600$ plus labor for them.

  • 19 years ago

    formula

    I don't think your solution is an option for me. The $600 for the transfer switch is not what I am concerned about. I would like to know if there would be any significant savings in labor putting the Xfer switch in now vs after I move in and the sub-panel has been wired.

    I am not familiar with wiring up power gens. But it would seem to me that the part of the circuit that would be switched is the main feed into the sub panel (the 100 amp wire that was extended from my main service panels). If that is the case - as long as they left me enough slack to reach the power generator Xfer switch (which will only be a few feet away from the sub panel) - isn't it as simple as removing the feeder from the sub-panel and running that to the Xfer switch. Then running a new feeder from the Xfer switch to the sub panel?

    If this is the case - then I can't see a big savings putting in the Xfer switch right now. If I can defer some cost now - that would be a good thing.

  • 19 years ago

    Go ahead and put it in now. Wiring with walls open is always cheaper, the electrician is already on site, and the price of copper will be higher later.

  • 19 years ago

    Hi,

    I have a Cummins Onan 20kw generator installed just last year after I built a house. Yes I was also in a cash crunch too.

    One thing to note is that the transfer switch and the generator may come as a set. Check out the Costco web site. I bought mine from there. My transfer switch came in with not only power lines but also (1) control lines to auto start the generator on power failure and (2) Battery Keeper charger wires and (3) power for heating the oil pan and collant system (fast start up engine is always warm). So just putting in "any" transfer switch may not be such a good idea.

    It therefore may depend on the Generator set/equipment you have in mind. Also note that you may need a concrete pad for your generator, propane / gas line (need a trench), propane tank. All infrastructure componets that may be cheaper and easier to get in while you build your house as all tools and workmen etc. are already on site.

    Some gensets you may be able to get away with just a gravel bed instead of a concrete pad. Depends on the size of genset you are thinking about.

    My recomendation is therefore to do something along these lines:

    1) You are cash poor right now
    2) You want a genset later. Not sure which one.
    3) Figure out where you want to place it. Note need an area about 4 feet by eight feet to place with maybe 2-3 feet clearance all the way around. Depends on the genset. Keep away from windows and doors due to Carbon Monoxide poisioning and fire risk reasons. Keep away from bedrooms for noise.
    4) Figure out where you can place your fuel, if LP Propane gas. Do you want to burry your propance tank? You may have town propane gas then this is not an issue.
    5) Ask the electrician to put in place from your main sub panel area a plastic / metal conduit pipe to your generator location.
    6) Place in the conduit pipe with lots of spare lenght of wire to allow for final wiring the following:

    Power delivery:
    Two power cables for each 115V Phase. #10 gauge
    One Neutral cable #10 gauge
    One Earth cable #10 gauge

    Battery charger:
    Two wires for the battery charger to keep you genset starting battery topped up.

    For control of engine on power fail:
    Four #14 guage wires for engine control

    For heater of oil pan and coolant:
    One live #12 gauge
    One neutral # 12 guage
    One ground #12 guage

    That way you can mostly delay your final generator installation until later. Note you cannot pour your concrete pad now without knowing your genset. This is because there are bolts that are set in the concrete and then are used to bolt down the generator. The position of bolts depends on your genset.

    Hope this helps.

    Warmest regards, Mike.

    Good luck with your house. Mine took about 2x long an about 40% over budget.

  • 19 years ago

    Mike

    I have most of your list already done. The sub panel and propane tank will be installed with the house and are currently set in the right place. The gas lines are very close. I will have to drill a hole through the wall to run the wires in conduit. I know about the slab - a location has already been picked so that it is downwind and away from bedroom and other windows. It was originally going to be completely done with the house until we ran into budget issues.

    I narrowed down my genset selection between the Cummins 12 kw and the Guardian 16kw generators. If I buy the Cummins - I will get it through Costco. If I get the Guardian, the electrician will supply. If I installed the Xfer switch now - I would select one of these 2 gensets so that the switch I put in was matched to the genset I will buy.

    I am still looking for the answer: will I save money (I mean a substantial savings) by putting in just the transfer switch in now (assuming I match it to the genset I will buy later) All of the wiring from the inside to the generator that you mention has to be done whether I do it now or later. However, if I wait until later to do everything, I will have to re-route the 100 Amp input to the sub-panel so that it is fed through the Xfer switch. That doesn't appear to me to be a big savings. I could ask the electricians to leave enough slack for the 100 Amp feed so that I can cut it (after power is off!) and re-route it to the Xfer switch without undoing any of the main feed connections inside the sub-panel.

    I don't think I would be saving that much by having the Xfer switch put in now, and by not doing it now I would give myself some flexibility to pick whatever system I want when I am ready to have the genset put in and hooked up. Am I missing something?

    The house is behind schedule and over budget. Seems to be a common theme on the forum.

    Thanks for the info.

  • 19 years ago

    sniff,

    If you have decided on a 100 amp transfer switch to pickup an entire sub panel then for now you can install a big J box that the feeders pass through. Later you use this J box to make your connection to the transfer switch. Big J box means really big like a 14x14x6. The connections can be made with NSI type insulated connectors.

  • 19 years ago

    dim4

    What exactly is connected inside the J box? Is it just to provide a splice point for the 100 Amp cable that runs from the main service panel and then into the sub-panel? I presume that when I install the Xfer switch, I remove the J box and replace it with the box provided with the switch? This would make sense - and would be a resonable cost.

    Thanks

  • 19 years ago

    You leave the J box and make your splices there. With NSI connectors it is quick and easy to make the connections. The transfer switch can mount adjacent to the J box.

  • 19 years ago

    Hi,

    I think that you should be O.K. I also installed my generator later after I finished my house. If you have the wiring set with a sub panel, have decided which circuits you want to power and have those wired ready for the generator, the conduit, gas pipe and tank installed I think you are in pretty good shape.

    The biggest hassle in getting my genset in was the gas line, needed to did a big trench and putting on the genset itself.

    I noticed that you are going for a Onan 12kw and Gardian 16kw. This should be fine. Note that these are relatively light in weight and can be installed / lifted by four workmen. The Onan 20kw is about 1,250 lbs and requires a small digger / back hoe for the lift and install. So if you are going for something larger, then perhaps you may want to go for it now because you have heavy lift capability on site.

    Warmest regards, Mike.

  • 19 years ago

    Sorry forgot to add one last thing. You may want to have a whole house surge surpressor / arrestor installed at your main panel. A few power outages are cause by lightning strikes. You do not want one taking the power out and damaging your generator in one go. Cost should be a few hundred bucks and installation should be cheap now since you have an alectrician on site.

    Best, Mike.

  • 19 years ago

    Thanks dim4 and tiger.

    I think i have enough info. I will use the J box approach and that will make the addition of the Xfer switch much easier later.

    I did opt to go with a smaller generator, and only back up things that are absolutley essential.

    Your inputs have been of great help.

    Thanks