rprice29507

electric subpanel addition

18 years ago

I have a detached garage used mostly for storage and a work shop. It currenly runs off of a 15amp breaker in my service box and is located about 30 ft from the main service box. I recently purchased a compressor which seems to draw more power than this line is able to provide. I want to add a 100 amp subpanel to the garage to make up this power shortage. I do not need 100 amp but I do want enough power to run my compressor as well as any machinery upgrades or perhaps an appliance. I have already purchased 50 ft. of #8 underground cable to make this upgrade and with the cable being only a 3-wire cable I am aware I will have to add grounding as well. I have been told a 35 or 40 amp breaker feeding the subpanel would be suffficent to run my compressor and then some. Is this accurate?

Roger

Comments (4)

  • 18 years ago

    The grounding has to run with the cable, that means you need an 8/3UF with ground (black, red, white, bare). Is that what you have? You will also need to drive a ground rod, but this has nothing to do with your bond back to the main panel.

    A 40A breaker would be correct in the main panel. You will also need a disconnect in the garage panel.

  • 18 years ago

    There is lots of good information about subpanels and other topics in the FAQ that can be found by clicking on the link at the top of the main forum page.

    Here is a link that might be useful: Subpanels

  • 18 years ago

    How many branch circuits could be added to this subpanel fed with #8 wire?

  • 18 years ago

    You can add branch circuits to the capacity of the subpanel. That means as many slots as there are in the sub, that's how many circuits you can have. Many novices are fooled into thinking that the sum of all the breaker's ampacity must not exceed the ampacity of the feeder from the main panel. That's not true. You will trip the feeder breaker from the main panel if you exceed the sub's capacity, but you won't hurt anything or risk a fire if you overdraw the feeder. Again, that's assuming the feeder breaker is in good operating condition and is installed correctly. That's why you need a qualified person to install this followed by a competent inspection. Sometimes it's difficult to get both. It's not a good choice to have 20 circuits on a sub with only a capacity of 40A (#8 feeder). Whether an inspector passes it is something that is difficult to predict. Usually they'll ask why so many circuits with such a small feeder. Then you tell him that you only operate 2 or 3 cc'ts concurrently, and then he just gives you the look and shakes his head.