What should be specified above NEC?

19 years ago

We're trying to write the specs for a new house. We'll have a GC. My general thought is that sometimes building codes aren't really all you want: you might want to build above-code. Reading here and there, I still can't figure out in the electricals what to specify that the NEC doesn't require. Any advice?

Comments (17)

  • 19 years ago

    Local or Regional codes sometimes are a bit different, usually a bit more stringent side. Sometimes seem just flat overkill but usually have valid reasons. Or a quirky building codes inspector.

  • 19 years ago

    Some possibilities:
    - Are two 20 amp circuits in the kitchen enough for you? Or do you want a third circuit?
    - Is 12' max. between wall outlets acceptable or do you want more?
    - Do you want an outlet in a halway where the code wouldn't require one?
    - Extra garage circuits for freezer or shop outlets? (Code only requires one circuit.)
    - Extra outside circuits for a future deck?
    - Any specialy circuits for bath floor heat, hot tubs, shop equipment, generators, etc.?
    - Do you want the minimum main panel size by code or upsize it for future loads (hot tub, etc.)?
    -Any prewiring for computers, etc.?

  • 19 years ago

    Non of this would be included in NEC requirements

    -Receptacles under windows inside, in eaves outside(switched) for christmas lights.
    -three wire cables to any ceilng boxes from the switch box to allow for later installtion of a fan with separate light and fan switches.
    -receptacles in locations where TVs, computers etc are expected to be located.
    - high mounted receptacles for wall mounted flat panel TVs
    - Prewire for cable/satellite TV, computer network, phones.

  • 19 years ago

    Also:
    Ceiling fans; landscape and security lighting; switched outlets in the eaves (and front windows?) for Christmas decorations
    All receptacle circuits wired for 20 amps, even if a 15 amp CB is to be initially installed.
    Backup generator and associated switching for power outages;
    Intercom; security system; coax for TVs/satelite
    There have been several threads here on this topic that you could do a search on

  • 19 years ago

    In addition to what all is mentioned above, the NEC and local codes are very limited on lighting. The codes gives you the minimum to see where you are going. Being in the middle of a large scale house design, I can tell you lighting is one of the more involved upgrades from the basic wiring.

  • 19 years ago

    More... if you know where the beds will be located, have double gang boxes (for two duplexes) placed on each side, NOT directly behind.

    Use the same dg box setup for the bathroom receptacles.

    Ask for ultraquiet bath vents placed to remove moisture, not just odors.

    Place the dryer and washer receptacle up where you can reach them.

  • 19 years ago

    I would go with higher quality in general but some of the places to keep an eye on are
    Bath fans-proper sizing and noise factor

    Recessed light fixtures- quality brand like Halo,Juno or equivalent

    All copper wiring including the buss in the main panel.

    spec grade receptacles on kitchen, bath, garage and outside. Maybe everywhere. Definitely spec grade or decora switches.

    whole house surge protection

  • 19 years ago

    If there are any ceiling locations that may not initially have a fan, but could some day you should have them install 'ceiling fan' rated boxes. In fact, I'd probably do that in all ceiling locations even if you didn't think you'd put a fan in there because the next owner might...

    Task and decorative lighting is well above min requirements: undercabinet, bedside, spot lights, art nook/shelves, security...

    Install a quad receptacle where you plan to plug in computer, monitor, printer, speakerphone, etc.

    Charging station for phones, ipods, etc.

    Need any additional smoke detectors besides the min requirements?

    Additional countertop outlets in kitchen? Inside appliance garage?

    Dedicated microwave circuit? Refrigerator?

    Additional outdoor lights and outlets...

    Use spec grade receptacles.

    etc. etc. etc.

  • 19 years ago

    dont forget about outdoor lighting... lights in a deck/porch, flood light, etc.

  • 19 years ago

    Wow! You guys (& gals?) are the best!

    mikie: I'm in the city of Roswell,GA a suburb of Atlanta. Hoping our codes are on the more stringent side because I'd rather err in that direction.

    formula1: we've thought of a couple of those already. But we definitely want closer spacing than code all around the house. Didn't know about the kitchen spec. and yes, we'll want another 20amp there for sure.

    joed: Okay. And never would have thought about the higher up receptacle for the TV.

    randy: Why wire all receptacle circuits for 20amps? I had just settled on only using 15amp receptacles (and I assumed wiring also) on the advice of itsunclebill on another thread here.

    normel: I think I had read your advice about the bedroom receptacles somewhere before, because it's already on my list. Other good ideas, esp. raising the W/D receptacles up--bad backs, bad knees around here already and getting worse!

    sbrn: Already got the copper wiring. I also know they use something else to bring the service in. But what the heck is the "buss" and why should it be copper? (Doing the spec. grade receptacles, too.)

    buzzsaw: Adding to my list from yours. Glad you mentioned the smoke detector--I think there oughtta be one in the Laundry Room, too.

    radioguy4ever: DH is working up a plan for that. I want a panic switch from the master BR, too, that controls all the outdoor floods.

    Thanks, mucho, ALL.

  • 19 years ago

    Would anybody care to comment on these specs I got regarding circuit design?

    Each circuit from its panelboard shall include 1 energized conductor, or hot leg; 1 grounding conductor (equipment bonding conductor); and 1 grounded conductor (neutral, common). The grounded conductor shall run throughout that circuit exclusively, that is, with respect to any other circuit, it:
    (1) shall not be crossed-over to
    (2) shall not be interconnected with
    (3) shall not otherwise shared
    (4) shall not be split into multiwire circuits
    ii) including no interconnection whatsoever between a grounded conductor and a grounding conductor in a panelboard, subpanel, junction box, device, etc.
    iii) including no interconnection whatsoever between grounded conductors.
    iv) without regard to or distinction between types of cable.

    2) Each circuit load
    a) shall be judged as to whether it is continuous, i.e., could reasonably operate continuously for 3 hours or more and
    b) if judged continuous, then it shall be derated by 20% (, or the peak load multiplied by 1.25) subsequent to all other deratings.

    3) One circuit at a time shall be distinguished
    a) as dedicated to lighting loads, which loads shall be connected only to that circuit
    b) as dedicated to non-lighting loads, which loads shall be connected only to that circuit and
    c) a lighting circuit and a non-lighting circuit shall not be interconnected, including as to grounded neutrals

    Is this NEC code, above NEC code, or just totally unnecessary?

  • 19 years ago

    My vote would be totally unnecessary. If you use an electrical contractor who is fully licensed, none of this will be an issue. And don't eliminate the possibility of using a multiwire circuit... properly done, it can be a wire/money saver.
    One other thing... unless local codes prevent it, use 14ga wire/15A circuits for the lighting and 12ga/20A circuits for the receptacles. The receptacles themselves can be 15A. And don't be fooled by the higher price of Decora devices at the box stores...they are just overpriced $0.39 junk.

  • 19 years ago

    normel: I thought those specs might be just too much.

    We do need the rocker style switches for easier use with arthritic hands. I was gonna use the Pass & Seymour spec grade. I don't think P/S has the rocker in spec grade in the 3-ways, so we'd have to go to their residential/builder's grade on those.

    Do you think that P/S's residential grade would be better than the Decora's residential? Decora apparently has a commercial/spec grade available now too, but if I go to that, I'm using Pass & Seymour.

  • 19 years ago

    Stick with the P&S. They have single pole, 3-way, 4-way all available in spec grade "decorator" style. You may have to go to 20A switches for colors others than white, ivory, or almond.

    Here is a link that might be useful: See page 2

  • 19 years ago

    normel: thanks so much. Don't know why I couldn't find the P&S 3-ways. Got it now.

  • 19 years ago

    On the thread of bad backs and height of receptacles. The most common I've seen are 16" on center off the floor. I find that I'm installing them more and more at 24" off the floor. At that height they are still hidden by most pieces of furniture and a just little easier to reach. If I know for sure that there will be a kitchen table against a wall, I like to put one there at 48".
    As far as double duplex receptacles, I've found them most handy in the living rooms near the electronic equipment. In my son's house we put 2 of these about 5' apart and he currently has something plugged into 7 of the 8 available spaces. I also like them on the kitchen counter.

  • 19 years ago

    coolvt: We're raising our receptacles to 30" o.c. off floor. And specifying the placement of some of them so they will be at the ends of couches and big furniture rather than behind it. It's unusual, but the one thing our house has going for it is wheelchair-accessibility and we figure there will be an increasing market for that in the future. Should we ever have to move.

    DH puts all electronics on those big black surge protector boxes that sit out and collect dust and look ugly. That's ok, we all have our bad habits!